Taco sr503 relay question

Leon82
Leon82 Member Posts: 684
I'm only using zone 1 and 2 and the tt contact goes to the first tt input on the boiler.

I want to move the 2nd zone to the priority zone 3 and use the priority tt to the second tt input on the boiler to run a separate odr/temp curve. But I want the priority function inactive

I read the directions a few times and am a little confused. Do both end switch close when the priority zone calls for heat? If so it is going to kill my plan

Thanks

Comments

  • Dave H_2
    Dave H_2 Member Posts: 550
    It sounds like you have a SR503-EXP? Am i correct?

    The -EXP controllers have two separate end switches (XX). The "Main End Switch" only closes upon a heat call from any heating zone, in your case Zone 1 and Zone 2.

    The "Priority End Switch" only closes when Zone 3, the priority zone, is calling for heat as long as the priority switch is on.

    Dave H.
    Dave H
    Leon82
  • Leon82
    Leon82 Member Posts: 684
    Yes , exp.
    Thanks
  • Leon82
    Leon82 Member Posts: 684
    edited November 2017
    It looks like it won't work like I had hoped.

    I'm getting 7 volts across rw on a the zones NOT calling for heat. Is this normal?

    It is a battery thermostat with only 2 wires
  • HVACNUT
    HVACNUT Member Posts: 5,804
    When the thermostat is open, it should read 24v across TT for that zone because it's kind of a false reading as it's picking up voltage through the relay coil.
    When the thermostat is closed, it should read 0v across TT
    Leon82Zman
  • Leon82
    Leon82 Member Posts: 684
    Ok, thanks. The one that's closed is at zero currently