suggestions for B&G replacement
ratio
ratio Member Posts: 4,247
Well, the PD-35 serving the radiant floor at my church finally failed. (Impeller bound up, & the motor ground the other half of the spider to dust. Seriously. No pieces left. ****?) Anyway, I'm looking to upgrade the pump to something newer. It's a PD-35S, on 3" flanges bushed down to 2½, CI w/ODR, manually balanced bypass on the radiant loop
A plan of mine is to convert this to constant circulation with injection. Like most of my plans, I doubt it'll come to fruition, but one never knows.
To add insult to injury, the 2" B&G pump that serves the convectors just picked up a squeak as well. :(
So, is there anything in particular I should look at? I'm more concerned with longevity than efficiency, but I expect anything I can get nowadays well be cheaper to operate.
daveamir
  • JUGHNE
    JUGHNE Member Posts: 11,562
    I replaced the same pump in a school with Taco Viridian 15.
    Amp draw went from 5.85 down to 3.85.
    For the school it has constant circulation when below 45.
    Boiler has old school reset control.
    Do a search on this site for the Taco Viridian, it has some reviews, so to speak.
    But many would recommend a mag strainer for any ECM/wet rotor motor you would use. I see you have some iron pipe there.
  • Ironman
    Ironman Member Posts: 7,904
    Take a look a the Wilo Stratos. It does literally save 80% on energy. Not much more in cost than the circ you now have.
    I will second the caution about using a dirt separator with any ECM pump.
    http://www.supplyhouse.com/Wilo-2163592-Stratos-1-5-x-3-40-1-Phase-High-Efficiency-Circulator-1-2-HP
    Taco Varidian and Grundfos Magna are other options.
    I'd also recommend that you investigate how many btus, gpm that you actually need. The current pump may be over-sized.
    Bob Boan
  • delta T
    delta T Member Posts: 884
    I love the Stratos, it has a lot of features, a very versatile pump.
    I will third the dirt and especially a mag separator if you want to use one though. Learned that lesson the hard way.....
  • ratio
    Thanks for the input. I've seen first-hand what comes out the bottom of a mag separator, wouldn't consider an ECM pump without one.
    Unfortunately, I can't afford the rework to install one along with the new pump, looks like we'll be staying with a PD35. I can get the whole pump for the same cost as the bearing assy and motor, and I know I'll get at least a few decades out of it.