Indirect circulator pump sizing, too much a bad thing?
cwilliams2000
Member Posts: 140
I have a 110k Peerless boiler. It has a superstor indirect maybe 10 feet away. The pipe only goes up about 5 feet at most. I am installing a new circulator and the original was just grabbed from the installers box. If you were doing this new what would you use. The current one is a 3 speed and I was going to get a Taco ECM 007 pump but I am thinking this is too much flow and maybe is bad for the system but not quite sue if that's the case.
I am wondering what you would put in for this basic install if you were doing it.
Thank you kindly
I am wondering what you would put in for this basic install if you were doing it.
Thank you kindly
0
Comments
-
What is the rating on the indirect? The boiler can't support anything over 10 gpm. What size tappings on the indirect?
Without any information to go on I would run 1" copper for the boiler side of the indirect and 8gpm for the circulator. You will probably get better heat transfer if you don't over pump the indirect0 -
Hi thank you. The piping in place is 1"0
-
What model is the boiler? What Model Superstore? Is the Indirect piped direct or primary/secondary?
One question is the flow, the other is the resistance. That will depend on the models."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
The boiler is a WBV04 and the superstor is a SSU60. I have two circulators. One is for the house baseboard heat and the other is just for the Superstor. Hopefully I was able to answer what you asked. Thank you0
-
It sounds like you have a grundfos 15-58 on it now?
Either the grundfos on speed 2 or the taco 007 ECM would be appropriate.
Pay attention to the boiler return temps as the call for DHW is finishing. You want the temp to be above 140 to prevent boiler condensation."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
that pump will be fine on your indirect, its a very good pump"The bitter taste of a poor install lasts far longer than the JOY of the lowest price"0
-
SSU 60 can go to 10GPM at 7.9 Ft head.0
-
Sounds like on my 3 speed I should definitely have been on low speed then. The head is really like 4-5 feet and the distance is only like 20 feet of total piping.0
-
Your DHW circuit has a flow check or is it in the circulator?0
-
Yes, I believe its called IFC in the circulator0
-
Speed 2 on the 15-58 would give you the best preferment at 5' head, you get 10 gpm, about what the boiler can keep up with.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thanks Bob. Thats funny I was just watching one of your videos on the caleffi auto fill valves and back flow preventers. Thanks for that too!0
-
@cwilliams2000 The SSU60 tank requires 10 gpm and has a pressure drop of 7.9' of head. Add the piping pressure drop and you are more around 9' of head.
So your circ spec needed is 10 gpm at 9'. If using a three speed you will want it at HI speed. The 007e falls just a bit under what you need.
However one other thing in regards to that 60 gallon tank, in order to get everything you want out of it, you would need a 174,000 BTU boiler!
Consider using a mixing valve to boost performance of the tank, store at 145F, deliver 115F.
Dave H.Dave Holdorf
Technical Training Manager - East
Taco Comfort Solutions
1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 920 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements