Can I utilize one outdoor temp sensor for 2 controls

yourefreeyourefree Member Posts: 4
Hi. I have a navien combi boiler and I am going to add the outdoor reset sensor to improve efficiency of the radiant floor heating system which warms the basement slab. My question is I already have a 10k ohm sensor that works with a carrier furnace to control the humidifier during the winter, can I tie the Navien boiler wire into that same sensor - it is the correct spec but I haven't been able to find out if it will cause an issue with the Navien or the Humidifier control. Wondering if anyone has tried this. Trying to avoid having to install a second sensor system which would involve more holes in the wall. Thanks

Comments

  • HVACNUTHVACNUT Member Posts: 3,707
    No. The sensor is like a thermistor and works off resistance. If you splice two controls in parallel to one sensor, the humidifier probably wouldn't work, and the boiler would read, sensor error. It'll be anarchy.
    yourefree
  • KVieiraKVieira Member Posts: 5
    HBX Controls has a wireless outdoor sensor that allows up to 5 devices to one outdoor sensor. You would need two base units and one sensor.
    http://www.hbxcontrols.com/wav-0110.php
    ratioHVACNUT
  • Harvey RamerHarvey Ramer Member Posts: 2,215
    > @KVieira said:
    > HBX Controls has a wireless outdoor sensor that allows up to 5 devices to one outdoor sensor. You would need two base units and one sensor.
    > http://www.hbxcontrols.com/wav-0110.php

    That's neat! I've been wanting access to a product like this for years.
    Ramer Mechanical
    ramermechanical.com
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • EzzyTEzzyT Member Posts: 1,096
    That is a really nice product much needed on a bunch of projects I have going on.
    Creative Solutions Plumbing & Heating LLC
    Lic #12683
    Co-Owners: Fred Drescher, Jr & Eliezer "Ezzy" Travis
    Marketing & Operations: Dawn Drescher
    201.499.0223
    Follow us on Facebook.
    Check us out on Instagram: creative_solutions519
  • yourefreeyourefree Member Posts: 4
    Thanks for the advice I will buy a new sensor system for the Navien, Up until now I have had it set at a constant 117 degrees per the engineer who designed the system. I'd like to make use of the outdoor temp feature so it adjusts the water temp accordingly.