Old system - NO air separator
Dale_3
Member Posts: 58
All - We have a few buildings we work on that were built in an era where air separators were not installed, water was pushed through the HX's, the compression tanks are seemingly always water logged and it would appear we have "gotten by." I feel like we should be installing separators on these systems but once again I'm seemingly in the minority. Does anyone have any good thoughts I can possibly add to mine to help convince the powers that be that this should or should not be done?
Thanks in advance. Dale
Thanks in advance. Dale
0
Comments
-
There are two different ways to address air in a hydronic system:
One is the old technology of air MANAGEMENT. This involves air being taken from off of the top of the boiler or its supply riser and directed to a compression tank like you have.
The other is air ELIMINATION. This involves an air removal device like a Spirovent (a micro buble resorber) that removes air from the system. This type of system REQUIRES a bladder expansion tank because air is being REMOVED instead of being directed to the top of a compression tank.
If you put an air elimination device on a system with a COMPRESSION tank, the tank will very quickly become water-logged and the relief valve will start discharging. You can NOT mix the two different technologies.
So to answer your question: no, absolutely not unless you also convert to a bladder expansion tank.
Is you're having issues with the present tank water-logging, then there's something wrong with your air management system.
If you post some pics of the tank and near boiler piping, we may be able to help ID the problem.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
Do these compression tanks have sight glasses?
The top valve can slowly leak air out, such a small leak it may never pass water.
Bubble test the top air holding portion of the tank. Pinhole could also pass air and not water.
Either repack the valve or shut them off. It worked for me.0 -
I've seen different methods for air management in bigger buildings. An automatic air valve at top of system. And yes compression tank will eventually get water logged. Some owners pressurized the tank with compressed nitrogen. I thought it was over the top,yuk yuk,at the time. But decades later maybe it paid off?0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 919 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements