Steam replacement

Dave0176
Dave0176 Member Posts: 1,178
edited October 2017 in Strictly Steam
2007 installed Burnham V84 boiler, rotted on one section and starting to corrode on the others. He decided to convert to gas, we installed a Union Steam GSA 125,000 (EG40) I’m also going to put a two stage gas valve when my parts arrive. Totally finished basement so we had to snake Wardflex through the rafters to get gas to the boiler, all went well, but was back breaking job.






DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

I cannot force people to spend money, I can only suggest how to spend it wisely.......
Paul S_3LionA29StuckWithSteam

Comments

  • EzzyT
    EzzyT Member Posts: 1,338
    Beautiful install as always @Dave0176.
    I like the water seal you have on that boiler.
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
    Dave0176
  • New England SteamWorks
    New England SteamWorks Member Posts: 1,525
    Beautiful. I like the VXT nice and high against the wall, easy to see and work with. Picture perfect.
    New England SteamWorks
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com
    Dave0176
  • Dave0176
    Dave0176 Member Posts: 1,178
    EzzyT said:

    Beautiful install as always @Dave0176.

    I like the water seal you have on that boiler.

    Thank you Ez for teaching us pigtails suck.......
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
    Paul S_3
  • EzzyT
    EzzyT Member Posts: 1,338
    I can't take the credit for that.
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
    Danny ScullyPaul S_3
  • MilanD
    MilanD Member Posts: 1,160
    Beautiful, @Dave0176! Why 2 stage it? Are there zone valves or TRVs on the rads?
  • Dave0176
    Dave0176 Member Posts: 1,178
    MilanD said:

    Beautiful, @Dave0176! Why 2 stage it? Are there zone valves or TRVs on the rads?

    No, it’s to modulate the fire to maintain between 4-10 oz steam pressure. Starts on high fire as pressure rises in the system when it reaches 10 oz the Vaporstat kicks the fire to low.
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • Dale_3
    Dale_3 Member Posts: 58
    Nice install.
  • Phil53
    Phil53 Member Posts: 73
    Dave, Very nice work. Just wondering what is Wardflex?
  • MilanD
    MilanD Member Posts: 1,160
    edited October 2017
    > @Phil53 said:
    > Dave, Very nice work. Just wondering what is Wardflex?

    Csst gas line brand.
  • Dave0176
    Dave0176 Member Posts: 1,178
    Phil53 said:

    Dave, Very nice work. Just wondering what is Wardflex?

    @Phil53 Ward Flex is Wards version of flexible gas line aka CSST (corrugated stainless steel tubing).
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • MilanD
    MilanD Member Posts: 1,160
    > @Dave0176 said:
    > Beautiful, @Dave0176! Why 2 stage it? Are there zone valves or TRVs on the rads?
    >
    > No, it’s to modulate the fire to maintain between 4-10 oz steam pressure. Starts on high fire as pressure rises in the system when it reaches 10 oz the Vaporstat kicks the fire to low.

    Ahh, got it. Thanks!! I didn't think it was needed on properly sized boiler. We have it and does great with zones. When all are calling, never above 8 oz. With 1 zone closed, modulates at 8. Super nice. I suppose I never thought to modulate even with all zones calling. I'll play with that this winter.
  • Paul S_3
    Paul S_3 Member Posts: 1,274
    beautuful installation @Dave0176
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • jgach11886
    jgach11886 Member Posts: 13
    Looks great! I would love to do this one day!
  • mikeg2015
    mikeg2015 Member Posts: 1,194
    edited November 2017
    MilanD said:

    > @Dave0176 said:

    > Beautiful, @Dave0176! Why 2 stage it? Are there zone valves or TRVs on the rads?

    >

    > No, it’s to modulate the fire to maintain between 4-10 oz steam pressure. Starts on high fire as pressure rises in the system when it reaches 10 oz the Vaporstat kicks the fire to low.



    Ahh, got it. Thanks!! I didn't think it was needed on properly sized boiler. We have it and does great with zones. When all are calling, never above 8 oz. With 1 zone closed, modulates at 8. Super nice. I suppose I never thought to modulate even with all zones calling. I'll play with that this winter.

    I think there's a good argument that you size for load & a healthy 50% pickup, but then down fire just to match load only... plus you could use a few TRV's for rooms with varying heat loses or small sizes like kitchens and bathrooms.

    How much pressure you need is then just a matter of the size of your header relative to the boiler size and size of your vents.


    Beautiful install. Like the 2 supply's to the header. It's not a large boiler but I'll bet the steam is nice and dry with the extra pipe.