Almost all of the P-Traps are still there, but the all important inlet valves are all missing upper components (and certainly need a re-build), and some have this branding:
Anyone recognize?
New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
It was originally a single boiler. Now it is two, with the piping transition botched. Receiver is gone. No main venting. Most radiators now have radiator vents. There are a few 1-pipe radiators that have been added.
You'll note in the 2nd photo that the single supply main loops around and connects right back to the supply, with a single drip..New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
-
At a minimum all the inlet valves need to be replaced/rebuilt, the P-Traps cleaned, the near boiler piping needs to be fixed, the basement piping needs to be straightened out, and we need venting.
And the house isn't in the Hamptons.
What would you do?New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com2 -
Well I don't know about the one pipe rads. I wonder if valves can be replaced with TRVs? Broomell was supposed to be wonderful so if you can restore....0
-
-
@New England SteamWorks , the radiator in the first set of pics is a Whittier. These date back to the late 1800s. The Broomell equipment might have been retrofitted- IIRC at the time the Whittier was in production, the only two-pipe steam system was two-pipe air-vent. This may explain some of the radiator vents.
You'll want to vent this system first. Get the steam moving and make sure the owner sees the difference. Then you can start fixing the rest of the Beavis and Butt-head stuff.
@Erin Holohan Haskell , the Whittier EDR chart is missing from its place in the Heating Museum under Radiators. I've attached it here.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting3 -
IMO, for a budget job just to get the system heating, I would install the standard Plain Jane steam inlet valves with orifices in the unions.
The traps may or may not have to work.
I have read an article by Henry Gifford concerning inlet orifices and applied his theory for a system that is now running with 8-12 ounces.
If I understand correctly if you can orifice the rads down to 60 to 80% of their EDR then that is all the boiler will need to satisfy.
Mr. Gifford showed an example where a boiler replacement size could be reduced by one third.
I did ask Dan H. about this and he concurred.
Maybe the one newer boiler would heat the house?
The bedroom picture looks as if the windows have new inserts installed, if so that and any other envelope upgrades may have dropped the heat loss.
I assume this was a vapor system to begin with and the piping was sized large enough for ounces operation?
Less money than moving the house to the Hamptons.0 -
Detroit Lubricator Co, which became part of American Radiator Co.New England SteamWorks said:Almost all of the P-Traps are still there, but the all important inlet valves are all missing upper components (and certainly need a re-build), and some have this branding:
Anyone recognize?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting-1 -
If the system is piped in such a way that both boilers are feeding the system in parallel, then they could be staged, with a Vaporstat, so that one of them drops out at a couple of ounces of pressure.
This lower pressure coupled with orifices, or Mepco regulating valves would negate the need for traps on the return side. Main venting would have to let the air out quickly.—NBC0 -
Thanks for the heads up, @Steamhead. I'll update this.Steamhead said:
@Erin Holohan Haskell , the Whittier EDR chart is missing from its place in the Heating Museum under Radiators. I've attached it here.President
HeatingHelp.com0 -
You literally amaze me sometimes, @Steamhead. Well done.Steamhead said:
Detroit Lubricator Co, which became part of American Radiator Co.
Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes3 -
@New England SteamWorks great find.
I hope your customer let's you do everything you know needs to be done. The work will pay for it self.1 -
Well, I am back at this one. Banging, as in lots. The pig tail was blocked leaving the pressuretrol in operative. This was cleaned. Main venting added. Seemed to be much improved when we left, -but now back to same banging.
It's been so knuckle-headed over the decades that it is difficult to find a reference point on where to begin, beyond starting from scratch (and we are not in the Hamptons).
But we have to start somewhere. We need a baseline:
Almost all of the radiators have vents. Broomell literature says: no vents. Anyone with experience here? Should I ditch the radiator vents? That is the first question.
New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
First make sure you have a lot of dry return venting. You'll want to use Gorton #2 vents, since Big Mouths don't have floats and this is a "B" dimension.
Change the Pressuretrol to a Vaporstat.
This will eliminate the need for radiator vents. If any rads don't heat after doing this, clean out the Broomell return fittings.
Then see where you stand.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements