Boiler size for indirect water heater
wklopf
Member Posts: 44
I'm looking to replace my boiler and water heater. My heating needs can be satisfied by a boiler of 75,000 to 80,000 BTUs. The 45 gallon indirect heater which I'm looking at lists a boiler requirement of 155,000 BTUs. My guess is that hat size boiler would provide the maximum hot water from this system, and a smaller boiler would result in a slower recovery. But, shouldn't a 45 gallon indirect with an 80,000 BTU boiler still deliver a lot more hot water than a 40 gallon water heater with 34,000 BTU input? Thanks.
0
Comments
-
Yes. It would. I'd match those two pieces with confidence.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
Do you have mixing valve installed on your tank? if yes, than 45 gallons of 140F will produce 45/1.25x140/125= 40 gallons 125F water. As example, 2.5 gallons per minute shower, 40/2.5 x125/100 = 20 minutes of shower. To re-heat tank from 45F cold water back to 140F, you will need (140-45)x 8.33x40=31,654 btu. boiler with input 80.000 btu hr, will output 80.000x.8=64,000 btu hr. so it will take about 30 minutes to reheat the tank. If you need to cut recovery time you will need higher output boiler. 155.000 btuhr boiler will recover tank in 15 minutes, if tank will allow it. In simple terms, that's my 2 cents.Gennady Tsakh
Absolute Mechanical Co. Inc.1 -
Recovery time with 80k boiler and 45 gallon indirect will be fine, just a little slower than the larger boiler specs they give.
Our 40 gal indirect w/ 110k boiler set at 150 degrees when making DHW recovers in 12-15 minutes after a large demand like two showers and breakfast cleanup.0 -
Another option and money savings is go with a 30 gallon indirect and store high and mix down. it will give you more hot water then a 40 standard tank all day long. What is your hot water demands?LANGAN'S PLUMBING & HEATING LLC
Considerate People, Considerate Service, Consider It Done!
732-751-1560
email: langansph@yahoo.com
www.langansplumbing.com0 -
The only concern I would have with this is if the boiler is non condensing and you have no control over the flow from the boiler, you could cause the boiler to condense."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Higher tank temperatures, around 150F will also assure no bacteria can grow. Higher operating temperatures does shorten the tank life however. More mineral precipitation as temperatures increase and thermal expansion and contraction of the tank at higher ∆ operation.
Public buildings, and possibly residential will require above 140F recirculated once a day to protect against legionella growth. I think the VA recently added that requirement in their buildings.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Little late here, but something I found increased my indirect recovery time dramatically was to use a full port zone valve. I was thinking I had to replumb the whole manifold to 1", but the valve did it. My supplier had sold me a priority controller that cut off the other zones when the tank was calling, but it took so long the house was getting cold! I also use a programmable thermostat with a 15 degree spread so in summer the passive loss is low enough the boiler stays off all day when no one's using hot water.1
-
My little 50,000 BTU Munchkin takes about 20 minutes to recharge our Viessmann 50 gallon indirect. But there are only two of us in the house with one bathroom. That calculus changes when there are more bathrooms and more people.
If everyone wants to shower at close intervals, you have to get a larger indirect. Or just get an on-demand water heater that can handle peak flow.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Too bad doubling up on showers does not double your hot water.Combat Veteran owned, Final Salute LLC on FaceBook & Twitter.
www.afinalsalute.com0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements