There is no "C" terminal on that thermostat, therefore it can only operate on batteries.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
The "B" terminal is used for certain heat pumps. As Steamhead noted, that stat does not have a common terminal. Were it present, it would occupy the terminal marked "not used", & be labeled "C".0
-
Take your meter and go from the "R" terminal in the zone relay (where the red wire is landed now) to the two 24V terminals. One should show roughly 0 volts, that's the hot, the other will show roughly 24 volts (the 29 volts you mentioned above), that's the common or "C" terminal. Just to double check.0
-
I got 0 volts on the top 24v input and about 1.25v on the bottom 24v. That's checking DC voltage from "R" terminal to both 24VAC inputs. Does that sound right? The 24 volts from the "R" cancel out both 24 volts on the common?ratio said:Take your meter and go from the "R" terminal in the zone relay (where the red wire is landed now) to the two 24V terminals. One should show roughly 0 volts, that's the hot, the other will show roughly 24 volts (the 29 volts you mentioned above), that's the common or "C" terminal. Just to double check.
0 -
Uh... if you're still working with the transformer and zone switch, you should be reading AC, not DC...smithfan said:
I got 0 volts on the top 24v input and about 1.25v on the bottom 24v. That's checking DC voltage from "R" terminal to both 24VAC inputs. Does that sound right? The 24 volts from the "R" cancel out both 24 volts on the common?ratio said:Take your meter and go from the "R" terminal in the zone relay (where the red wire is landed now) to the two 24V terminals. One should show roughly 0 volts, that's the hot, the other will show roughly 24 volts (the 29 volts you mentioned above), that's the common or "C" terminal. Just to double check.
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Sorry, meant AC..I'm getting 0 volts from R to 24VAC and 1.8 volts from R to COMM..Jamie Hall said:
Uh... if you're still working with the transformer and zone switch, you should be reading AC, not DC...smithfan said:
I got 0 volts on the top 24v input and about 1.25v on the bottom 24v. That's checking DC voltage from "R" terminal to both 24VAC inputs. Does that sound right? The 24 volts from the "R" cancel out both 24 volts on the common?ratio said:Take your meter and go from the "R" terminal in the zone relay (where the red wire is landed now) to the two 24V terminals. One should show roughly 0 volts, that's the hot, the other will show roughly 24 volts (the 29 volts you mentioned above), that's the common or "C" terminal. Just to double check.
0 -
So now I checked W to the top 24VAC input and get 24volts. I get 0 volts on both 24VAC terminals testing from R.0
-
I figured it out, just had to probe it every which way. Bottom is common, got 29 volts on R. Top is 24 Volts hot. Now I just need a decent thermostat. Any recommendations? Wifi not necessary, but tired of changing batteries.0
-
Honeywell 5000 series for non programmable, 6000 series for cheap (relatively speaking) programmable. The 8000 series is last years' flagship, I like them a lot, but they're somewhere north of $150. I don't have any experience with their newest line, the T series.
Avoid the big box store models-they seem to be second-sourced. I'd try to get one from a local HVAC supply house, but be aware that some places deal ...poorly... with homeowners. If they are less than helpful, spend your money somewhere else!
-1
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements