Replace wet return with dry, reroute, chop, or condensate pump?
2x_Tom
Member Posts: 12
So I have a system with a badly leaking (zero condensate gets back) wet return under a finished basement.
Option 1 is replacing it as piped. It's going to require replacement of all the tile (can't match what's there) then hopefully getting under a tub without having to remove it or damaging it.
Option 2 is, is it possible to turn the end of the mains around, pitch back towards the boiler then drop to the floor in the boiler room about 15' from the boiler? It's 6' below the steam main and a couple feet below the water level at the boiler room floor.
Option 3 is (this is one I'm leaning towards) rerouteing them along a wall in a lower part of the basement (still finished) then telling the carpenter to figure out how to hide them. The only issue here is the line won't be level, it will have a low point. At least the new return will have a way to clean it and get yearly maintenance, something the old one lacked. This will also lower the return line by about a foot. I don't think that will matter though.
Option 4 is a condensate receiver at the end of the mains. Getting power to it and a 3/4" line back to the boiler shouldn't be too big a deal.
Option 1 is replacing it as piped. It's going to require replacement of all the tile (can't match what's there) then hopefully getting under a tub without having to remove it or damaging it.
Option 2 is, is it possible to turn the end of the mains around, pitch back towards the boiler then drop to the floor in the boiler room about 15' from the boiler? It's 6' below the steam main and a couple feet below the water level at the boiler room floor.
Option 3 is (this is one I'm leaning towards) rerouteing them along a wall in a lower part of the basement (still finished) then telling the carpenter to figure out how to hide them. The only issue here is the line won't be level, it will have a low point. At least the new return will have a way to clean it and get yearly maintenance, something the old one lacked. This will also lower the return line by about a foot. I don't think that will matter though.
Option 4 is a condensate receiver at the end of the mains. Getting power to it and a 3/4" line back to the boiler shouldn't be too big a deal.
0
Comments
-
Option 3. A wet return can go up and down and corkscrew all over the place, so long as everywhere along it is below the boiler water line. It also helps at the various bends to use plugged T's rather than elbows, though, so you can clean the thing out when you need to...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
As Jamie said.
Where are your main vents now?
You could lay the wet return on the floor against the wall.
An inverted "U" shaped wood box could cover it and then a wall stood on top of it.
But provide accessible cleanouts, valves etc to flush with garden hose occasionally.0 -
Avoid pump if you can.0
-
Jamie Hall said:
Option 3. A wet return can go up and down and corkscrew all over the place, so long as everywhere along it is below the boiler water line. It also helps at the various bends to use plugged T's rather than elbows, though, so you can clean the thing out when you need to...
JUGHNE said:As Jamie said.
Where are your main vents now?
You could lay the wet return on the floor against the wall.
An inverted "U" shaped wood box could cover it and then a wall stood on top of it.
But provide accessible cleanouts, valves etc to flush with garden hose occasionally.
This.jumper said:Avoid pump if you can.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
You can use baseboard covers to conceal as well. I've done this with great success.0
-
Danny, great idea. Would you consider using actual BB htrs to heat the finished basement. Just use fillers & blanks to make it continuous. Perhaps 1" or maybe still too small? Depends on the connected EDR load for the wet return I suppose.0
-
Cleaning the pumps always helps with the pump.-3
-
Thanks for the replies.
I'm not sure where the main vents are or if their are any. The basement is finished so nothing is exposed. I'm going to cut some holes in the Sheetrock where I think they should be on Tuesday and find out.
I'll be going with the third option I think and rerouteing the line then trying to hide it. I'm going to leave basically purge setups on either end so you can always connect a hose and force water pressure from one boiler drain to the other and flush it.
I like the dummy baseboard idea, some Slant Fin 80 covers will hide just about anything.0 -
The typical boiler drain might have only a 3/8" passage way at best. I usually take them out of everything that mush be drained or flushed and replace with 3/4" full port ball valve with hose adaptor.
Often just getting the small boiler drain to drain let alone pass debris is a major part/time of the flush process. IMO0 -
Well I ended up repiping it in 1-1/4" copper through walls, channeling a poured staircase and going exposed through the boiler room. The pictures were before I sleeved it through the masonary and added support to it in the boiler room. It's been a few days and the systems running great. I was a little nervous their would be a drip into the wet return somewhere in the finished basement but I lucked out on that one.0
-
0 -
Looks Great! Be sure you don't drive a nail or screw through it when you replace the drywall. Nail guards might be wise.0
-
Agreed- nice work! And make sure you leave access for the valves and drains in the walls.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
real nice! Obviously you have some experience with a torch and a roll of solder0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements