Can I Convert a Slant Fin GXH-190 DPZ Boiler to a Hot Water Producing Boiler?

TheRyanKing
TheRyanKing Member Posts: 8
Currently, I have a one-pipe steam system with a Slant Fin GXH-190 DPZ boiler. The way the piping was installed there is water hammer and banging constantly and I would like to convert over to hot water hydronic system. I currently have cast iron radiators that I believe will be compatible with hot water. I would like to run pex on the long runs and copper wherever needed on shorter runs. Please let me know, I'm really looking for help, I have my basement completely unfinished right now and I want to get all of the piping done before going ahead and putting in the studs, sheetrock, etc.

Comments

  • SeanBeans
    SeanBeans Member Posts: 520
    I think many people here would rather try to convince you to stay with steam.. and i dont blame them!
    RomanGK_26986764589
  • Jamie Hall
    Jamie Hall Member Posts: 24,857
    as @SeanBeans says... and I'm one of them. The first thing to do, since you have a one pipe steam system, is to look around and find out why there is water hammer and banging. A steam system in good shape simply won't do that -- it's almost completely silent.

    To help you get started:

    cutout pressure on the boiler. Should not be over 1.5 psi. Cost to adjust, zero. Time, two minutes.

    All piping. Check to be sure that it has adequate and continuous slope in the right direction. Use a level for this -- don't depend on your eye. It's not just end to end; you need to check for sags on longer runs. And make sure to check all near level sections. Rehang what needs to be rehung. Cost to fix, minimal (usually). Time -- an afternoon in your unfinished basement with the level, some pipe hanging material, a screwdriver or hammer and a good level.

    Evenness of heat. If some rooms are warmer than they need to be, or colder, you may need to adjust or change some of the radiator vents. You also need to install main vents on the steam mains, if you don't have them. This isn't hard -- do it yourself -- but there is the cost of good vents.

    Now. That should get your steam system running quietly and evenly.

    However, if you really do want to change to hot water heat, you will need all new piping. You also must change all the valves on the radiators and get rid of the vents and add return lines. You must pressure test the radiators; odds are pretty good that some of them will leak and need to be replaced (30 psi for hot water heat puts a lot more stress on them than 1.5 psi for steam!). Your Slant/Fin can be reconfigured for hot water, with all new piping and controls. However, it is a relatively low efficiency boiler, and I would recommend going to a new, higher efficiency unit.

    You will gain nothing in terms of fuel use from the change, unless you go to a new high efficiency boiler -- and even then the change will be relatively small, and the return on your investment will be negative.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Steamhead
    Steamhead Member Posts: 17,384
    Agreed. It doesn't need an exorcism, it just needs the right people to fix it. Keep the steam.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • KC_Jones
    KC_Jones Member Posts: 5,840

    Currently, I have a one-pipe steam system with a Slant Fin GXH-190 DPZ boiler. The way the piping was installed there is water hammer and banging constantly and I would like to convert over to hot water hydronic system. I currently have cast iron radiators that I believe will be compatible with hot water. I would like to run pex on the long runs and copper wherever needed on shorter runs. Please let me know, I'm really looking for help, I have my basement completely unfinished right now and I want to get all of the piping done before going ahead and putting in the studs, sheetrock, etc.

    It would have never been installed like that originally. Either the house has settled and things have moved or someone that doesn't know what they are doing moved pipes around.

    As has been said steam is silent when operating correctly. It's very likely to be much cheaper to fix what you have than to rip it out and start over which is what you are proposing.

    Sometimes banging or water hammer can be fixed almost for free by adding pipe support and correcting pitch or just fixing the pitch on the rads.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • TheRyanKing
    TheRyanKing Member Posts: 8
    The piping was never pitched correctly and the way that the pipe was put in, it is above the window and below the floor joists, so it is sandwiched in between, thus i can not move the pipe up or down to adjust the pitch unless i cut the pipes and redo them
  • Steamhead
    Steamhead Member Posts: 17,384
    How about posting some pictures?

    Also, where are you located? We may know someone near you who can help.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    KC_Jones
  • JUGHNE
    JUGHNE Member Posts: 11,276
    There are piping systems know as counterflow that slope in what seems to be the "wrong" direction. That reverse flow is compensated for at the boiler originally. It is possible that there was a boiler changeout that ignored the main drips and things got cobbled at that time.
    Pictures of boiler, piping near boiler, system pipes and a couple rads. Completely free advice available if we can just look!
  • TheRyanKing
    TheRyanKing Member Posts: 8









  • TheRyanKing
    TheRyanKing Member Posts: 8
    Image 1: Beginning of Return After Last Radiator (It should not be straight down and I believe that was done in order to not cross in front of the door)

    Image 2: Main Line Feeding Radiator with 1-1/4'' pipe

    Image 3: Boiler Name Plate

    Image 4: Radiator 1

    Image 5: Main Steam Line Directly Out of Boiler, Branched out Left and Right which I believe is wrong, shouldn't it be going in one direction? Also, notice how the pipe is pointed down immediately forcing steam down straight out of the boiler, don't think that is a good idea.

    Image 6: Main Line going above a beam, there is no way water is making it over that beam.

    Image 7: Radiator 2

    Image 8: Side of Boiler & Hartford Loop

    Image 9: Return (since the steam line is branched out both left and right, the return come together and meet before going back into the boiler, i dont know if that is correct either.
  • TheRyanKing
    TheRyanKing Member Posts: 8
    Also, I live in Queens New York @Steamhead
  • Steamhead
    Steamhead Member Posts: 17,384
    edited April 2017
    Doesn't look too bad from here- at least they used the full size of the boiler steam outlet. But the vents are in the wrong place on those two radiators. And the pipe going over the beam should have a smaller pipe going under the beam to deal with the water. I'll bet that's what is causing the banging. If I find a diagram of this I'll post it.

    And to find a Steam Man in the NYC area, go here:

    https://heatinghelp.com/find-a-contractor/SearchForm?Zip=10019&Radius=30&SecurityID=9868408bc8591d955dfcdb1aed6291d8d9934355&action_doSearch=Search
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • ChrisJ
    ChrisJ Member Posts: 16,316
    @Paul S Is near you.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    Paul S_3
  • TheRyanKing
    TheRyanKing Member Posts: 8
    Is it still less work to fix this as opposed to converting to hot water?
  • SeanBeans
    SeanBeans Member Posts: 520
    @TheRyanKing definately.
  • TheRyanKing
    TheRyanKing Member Posts: 8
    How much would something like this cost me to be fixed? I could do it myself but I don't have the time honestly
  • Jamie Hall
    Jamie Hall Member Posts: 24,857
    I'm sorry, @TheRyanKing ; we don't talk pricing because it varies so much depending on exactly where you are. None of the fixes are likely to be that difficult, though.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,563
    The horizontal nipple on Hartford loop is too long, should be a close nipple. Is the header 2.5"?
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • Danny Scully
    Danny Scully Member Posts: 1,440
    edited April 2017
    Picture is worth a thousand works right @Steamhead? @EzzyT and I did this. I would send him a private message @TheRyanKing, he services your area.
  • Steamhead
    Steamhead Member Posts: 17,384
    Bingo!

    @Erin Holohan Haskell , that needs to go in the Steam Piping section of the main site.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,600
    Nice job, Danny. Looks just like the pic on page 95 of "Lost Art." Old-school stuff!
    Retired and loving it.
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    I would love to be a fly on the wall when an uniformed person sees that in the basement and declares "...A-Ha! There's your problem..."

    There was an error rendering this rich post.

  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,600
    Me, too, Steve. ;-)
    Retired and loving it.
  • Canucker
    Canucker Member Posts: 722

    I would love to be a fly on the wall when an uniformed person sees that in the basement and declares "...A-Ha! There's your problem..."

    Maybe a copy of pg. 95 should be attached to it?
    You can have it good, fast or cheap. Pick two
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,600
    Erin's on it.
    Retired and loving it.
  • ChrisJ
    ChrisJ Member Posts: 16,316
    A laminated sign that says "If you don't know what this is you have no business working on a steam heat system"

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    CanuckerjumperPaul S_3
  • Erin Holohan Haskell
    Erin Holohan Haskell Member, Moderator, Administrator Posts: 2,354
    Steamhead said:

    Bingo!

    @Erin Holohan Haskell , that needs to go in the Steam Piping section of the main site.

    Here you go: https://heatinghelp.com/systems-help-center/piping-past-obstructions-in-one-pipe-steam-heating-systems/ Nice work, @Danny Scully and @EzzyT

    President
    HeatingHelp.com

  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,600
    And nice work Erin!
    Retired and loving it.
    Erin Holohan Haskell
  • JUGHNE
    JUGHNE Member Posts: 11,276
    Looking at the beam jump picture.....are we certain the steam is coming from the left?? Just a dumb question probably with a "Duh" answer.
    SeanBeans
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,600
    Yes, from the left.
    Retired and loving it.
    JUGHNE
  • JUGHNE
    JUGHNE Member Posts: 11,276
    edited April 2017
    This is another take for over and under. It is a dry return from the F&T of a hanging unit. The air venting would have been done in the basement thru the cond pump. I don't know why it wasn't just all run over the door as the heater was much higher. This area has been demoed. No pictures. From a print of a 1955 school house..the original Kewanee is still firing. Shows that ME's put these details on a print. FWIW

    Note: feel free to use the example.....it was drawn and installed by Dead Men....though they might have put CO on the lower wet return tees?
  • jumper
    jumper Member Posts: 2,385
    ChrisJ said:

    A laminated sign that says "If you don't know what this is you have no business working on a steam heat system"

    I've tried that. Put sign on stuff stating not to modify without calling me. I've also added notes to plans stating that the detail supersedes code. That can get one into trouble. Even if a code is written years after the project a proscription is meat for lawyers.
  • Paul S_3
    Paul S_3 Member Posts: 1,280
    edited April 2017
    This is a over under piping I recently did....i repiped a steam main and had to go around a window.... thanks @ChrisJ ..... @TheRyanKing you can private message me, I service the 5 boroughs of Nyc....
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.