Heating Pex Blew

redtyde
redtyde Member Posts: 5
Hello.
I have seen a couple of postings about heating PEX blowing and I just had this happen.
See pic below.

It was originally installed in 2005 and just burst today.
Any thoughts on why this would happen?

Comments

  • JUGHNE
    JUGHNE Member Posts: 11,276
    How hot was the water temp?
    How far to any support on the right side?
    Looks a little saggy.
    kcoppdelta TRLuck
  • redtyde
    redtyde Member Posts: 5
    Thanks for quick response Jughne.
    180 degrees is the water temp tos a hydro heating unit.
    Its about 18" from the brass fitting to the main wooden support beam where its attached.
  • kcopp
    kcopp Member Posts: 4,472
    What is the boiler???? Looks like 220*+ water temps to me....
    delta T
  • redtyde
    redtyde Member Posts: 5
    Its a Carrier with Weil Mclain burner. I know its 180, or at least that is what the gauge is showing me after I I closed off this zone and fired up the system again. Also gauge at 15 PSI.
  • Tinman
    Tinman Member Posts: 2,808
    Aquastats and temperature gauges that come with new boilers are inaccurate at best. Just one of the reasons I would NEVER use Pex in a high temp application.
    Steve Minnich
    Solid_Fuel_Man
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    Agree with @Stephen Minnich I've preached the same thing on wood/coal/pellet fires boilers. One overheat and the results can be catastrophic.

    Is there any way to confirm the max temp other than aquastat settings and boiler gauge?
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,858
    Yeah, no. I have literally MILES of this stuff out there, and have never seen a failure like this on my systems. I have seen this type of failure where the boiler was run away and producing steam. I can tell by the deformities of your tubing that it was well above steam. I also saw this kind of damage when I mistakenly applied heat (torch flame) to a kink trying to get the kink out of the pipe. Forgot it was under 100 PSI test pressure... Made a heck of a noise when it blew.

    You may have been seeing 180 F water temperatures when the system was running, but when you shut it down quickly, there is still a lot of heat left in the refractory, and it can create drift heat significantly hotter than 180. Probably softened the tubing and the pressure blew it. Need to see more pictures of the system to which it was connected to give a clearer idea.

    ME

    There was an error rendering this rich post.

    Solid_Fuel_Man
  • Ironman
    Ironman Member Posts: 7,550
    I have to ask: is that a piece of Qest or just discolored pex. Judging by the tear, it looks like Qest.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • kcopp
    kcopp Member Posts: 4,472
    Looks like Uponor/ Wirsbo to me. The fittings are the expansion type. The system water discolored the inside.
  • Zman
    Zman Member Posts: 7,611

    Yeah, no. I have literally MILES of this stuff out there, and have never seen a failure like this on my systems. I have seen this type of failure where the boiler was run away and producing steam. I can tell by the deformities of your tubing that it was well above steam. I also saw this kind of damage when I mistakenly applied heat (torch flame) to a kink trying to get the kink out of the pipe. Forgot it was under 100 PSI test pressure... Made a heck of a noise when it blew.

    You may have been seeing 180 F water temperatures when the system was running, but when you shut it down quickly, there is still a lot of heat left in the refractory, and it can create drift heat significantly hotter than 180. Probably softened the tubing and the pressure blew it. Need to see more pictures of the system to which it was connected to give a clearer idea.

    ME

    I agree that this one flashed to steam.
    I have seen the exact same damage where the insulation contractor applied spray foam too quickly with the system under air test. Talk about a hot mess...
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
    Bob Bona_4
  • redtyde
    redtyde Member Posts: 5
    UPDATE - So after getting the PEX repaired and heat going again, root cause is still undetermined and I have had (3) contractors give me (3) different reasons as to why they feel the PEX failed.

    The PEX that burst feeds a hydro-heating system in an unconditioned attic space. There was speculation that the coils froze. (It was cold and windy on the day it happened, it got down to 13 degrees). Although keep in mind this unit was installed in 2005 and has never had this type of issue before.

    Another contractor states that it couldn't have been freezing coils as he would expect the copper in the coils to split before the PEX bursting.
    After the PEX repaired and a pressure test was done, coils were fine with no leaks.

    My question, even if there was some type of blockage in that line, does a circulatory pump have that kind of horsepower to build that much PSI?

    Do we put in glycol to avoid the possibility of freezing coils?




  • Tinman
    Tinman Member Posts: 2,808
    3 contractors and not one of them suggested iron pipe for near boiler piping?
    Steve Minnich
  • redtyde
    redtyde Member Posts: 5
    No, As a matter of fact one of my questions was how far off the boiler can you start PEX. I thought you had to be so many feet away from the boiler but I may have been mixing up my domestic hot water PEX. ALL of them said you can go directly to the boiler.
  • Bob Bona_4
    Bob Bona_4 Member Posts: 2,083
    Logic dictates using iron or copper near the boiler for stability for the pumps/valves/service components. After that, pex away.
  • Zman
    Zman Member Posts: 7,611
    I am thinking the boiler got low on water and overheated, it then got a shot of cold water which immediately flashed to steam creating the temp and pressure needed to cause that kind of damage. Just a theory...
    Some more pictures of the boiler piping would help determine the cause. Does the boiler have automatic fill and/or low water cutoff?
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
  • Mark Eatherton
    Mark Eatherton Member Posts: 5,858
    I think you had a stuck aquastat, and it could happen again.

    As for antifreeze yes, but unless you want to go to the expense of setting a heat exchanger and related equipment, you will need to fill the whole house heating system with it.

    As I and others have said, it would be nice to see more of the near boiler piping...

    ME

    There was an error rendering this rich post.

    kcopp