Boiler pilot won't stay lit
debbyg
Member Posts: 7
My Burnham boiler pilot will not stay lit, even after replacing the thermocouple twice, and the gas valve. The valve was replaced 3 weeks ago, and the pilot stayed lit until yesterday. The pilot went out again yesterday and the tech replaced thermocouple again, it stayed lit for about 20 min, and has gone out 3 more times in the last 8 hours. The tech noticed that the new valve seems to have a fault, as it will not switch to "off", only "on" or "pilot" but I don't think this is the cause of the pilot not staying lit. The gas valve will be replaced again, and the tech said he hopes this will solve the issue, but honestly I don't think the valve the issue. When the pilot is lite, the flame is blue and consistent. Everything I have researched leads to changing the thermocouple and gas valve, so I am really at a loss trying to solve this.
0
Comments
-
Did the pilot burner get cleaned? The gas for the pilot passes thru a very tiny orifice in the pilot burner. It has to be removed and taken apart for cleaning. The orifice is barely a pinhole.
Did the tech check the in and out gas pressure at the boiler?
There is usually an adjustment on the valve to adjust the pilot flame.
If your gas utility company is having heavy load their delivery pressure can drop, or their outside regulator could be slow.
Any other gas appliances?-1 -
Make sure only the tip of the thermocoupler is actually in the flame. Not more than 3/8" to 1/2" and is cherry red. Also make sure the end that screws into the gas valve is straight in , screwed in hand tight plus a quarter turn with a wrench. That end is magnetic and needs to make good contact but there is no gas on that fitting so don't over tighten.-1
-
When in doubt check the millivolts, or keep guessing.
No on,offpilot??????? how did the pilot light without a button to push?-1 -
-
Thanks for the replies! Until the last month, I knew zero about boilers, but have been working to research what could be causing the issues, so that I can at least have general knowledge when I am addressing the tech. So thank you for your help and suggestions! I am just concerned that they will change the gas valve, and consider it repaired (again) and not find what the actual issue is, as two techs have stated with pilot light issues, the only two things causing it are the gas valve and thermocouple.
I have read something about a possible draft in the chimney causing the pilot to not stay lit, but I have my doubts it is anything having to do with this, as I have never had an issue with this in 16+ years of living in this house.
* I will definitely bring up your suggestions in question form to the tech when he returns to replace the gas valve* (the gas valve has the on/off/pilot, but will not turn to the off position)
*I believe the burner was cleaned when the pilot initially had this problem, but it never hurts to ask. I do not know if the gas pressure was checked, or if this applies, but I can say that our other appliances (water heater, gas stove and dryer appear to be working well)
*I know the millivolts were checked the first time the thermocouple was replaced and were within the "range".
* I am not too sure if there is a junction block, that will be something I should address with the tech?
*the placement of the thermocouple is something I can and will check
Thanks again for your help!0 -
Ahh I misread, I thought I read just on and off with no pilot position. Still seems odd, I thought all Gas Valves has a off position
Pilots getting blown out isn't normal.-1 -
-
Yes, the new valve has an on/off/pilot position, but will not turn to the off position. You would think when he replaced it, that he would have checked that it worked, but unfortunately I doubt if that has any thing to do with the pilot not staying lite, just another added complication. : /0
-
-
DebbyG, did you ever figure out why the pilot didn't stay lit? I have the exact same problem with my Burnham boiler pilot. I've had the coupler replaced, and the gas valve replaced, and yet still the pilot goes out every few hours. I've had 2 contractors work on it, and neither one has any idea where to go from here. Any more information on how you resolved your would be so helpful.0
-
Has anyone bothered to do a combustion test. When you have replaced the thermocouple and the gas valve without checking any millivolts or doing a combustion test. You are just guessing and that costs money. You really need to get hold of a pro who knows what they are doing. How about some pictures of the boiler, vent etc so maybe we can see more of what you may be dealing with.1
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements