They were far from air tight. Having one damper shaft just flopping in the wind in a wide open hole and the other with a lever and a wing nut. How is this considered acceptable!?
I did some thinking, and came up with this. All I need now is a bead of silicone on the seams and rivets. The abrasion resistant rubber washers fit very tight and needed to be threaded onto the shafts.
They also operate a bit nicer with the wing nuts loose as I have steel washers on the inside as well.
Thoughts?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Comments
-
No 6" damper plate here.Hatterasguy said:Observe the leakage around the 6" diameter damper plate and compare that to the effort you are making to limit airflow through a .18" hole in the side.
You'll have your answer.
8" is the smallest there, the bigger one is 14".
So you're saying at 0.02" there will be very little leakage via those holes? If so, why bother sealing all of the joints that fit fairly tight?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Maybe use Ny-locks instead of the wingnuts. I don't think you have enough thread to double nut the shaft.0
-
-
-
-
I know where you're coming from, but I don't think it's an issue only because I plan on loosening the nuts before moving the damper. Tightening them locks it in place nice.Paul48 said:Maybe use Ny-locks instead of the wingnuts. I don't think you have enough thread to double nut the shaft.
I'm really hoping once they're set, they're set. Knowing me, probably not, but I can hope.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
ChrisJ, You might like this club! http://ring4club.com/ They are over the top duct leak sealers. I know a few of them
Yours, Larry1 -
Duct leakage. Not only do you lose cold air to the attic but every 1 cfm lost to the attic is made up by 1 cfm of outdoor air infiltration leaking into the conditioned space.
I learned this the hard way. I once went on a call on a temperature and humidity controlled room (a lab) which was built inside of an unconditioned factory.
They complained about high humidity. The air conditioner worked fine couldn't find anything wrong with it..spent a few hours checking it out.
Finally crawled up on top of the lab and one of the flex ducts had pulled off a supply diffuser. Didn't think much about it just reconnected it. Then after thinking about it that air lost to the "factory" had to be replaced by air infiltration from the factory to the lab.
Almost immediately the humidity snapped back to normal0 -
Very good point, though in my case my attic isn't vented.EBEBRATT-Ed said:Duct leakage. Not only do you lose cold air to the attic but every 1 cfm lost to the attic is made up by 1 cfm of outdoor air infiltration leaking into the conditioned space.
I learned this the hard way. I once went on a call on a temperature and humidity controlled room (a lab) which was built inside of an unconditioned factory.
They complained about high humidity. The air conditioner worked fine couldn't find anything wrong with it..spent a few hours checking it out.
Finally crawled up on top of the lab and one of the flex ducts had pulled off a supply diffuser. Didn't think much about it just reconnected it. Then after thinking about it that air lost to the "factory" had to be replaced by air infiltration from the factory to the lab.
Almost immediately the humidity snapped back to normal
It's kind of an indoor space, kind of not. What I want is to insulate between the rafters in the future, if I ever get the money to do it and essentially turn it into a conditioned space.
Whatever happens, I need to be careful because I do not have any moisture issues up there in the winter currently and I'd like to keep it that way.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
It should be vented. Any good roofer will tell you without vents, roof shingles will begin to curl over time.0
-
Fred said:
It should be vented. Any good roofer will tell you without vents, roof shingles will begin to curl over time.
That's a new one on me Fred.
Roof is 10+ years old and nothing curling. Just cheap asphalt shingles.
I have no intention of venting the attic to be honest. There are plenty of properly insulated and designed unvented attics out there.
As far as I knew, the primary reason for venting an attic was to prevent condensation.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1 -
Fred said:
It should be vented. Any good roofer will tell you without vents, roof shingles will begin to curl over time.
That's BS pounded into the roofers thick skull by shingle manufacturers. Keep that thought then find a shingle manufacturer who tells you specifically what temp is to high in the attic . You won't. That's so they can say your warranty is denied because of poor venting.
If that is the case then making the attic part of the envelope, and moving the insulation detail to the roof deck like recommended will create big issues, and it doesn't.
2 -
Air tight has a whole new meaning with fa systems.......0
-
-
-
hehehehe0
-
ChrisJ said:
So I bought a bunch of "Air-Tite takeoffs with dampers" for the system I'm building.
They were far from air tight. Having one damper shaft just flopping in the wind in a wide open hole and the other with a lever and a wing nut. How is this considered acceptable!?
I did some thinking, and came up with this. All I need now is a bead of silicone on the seams and rivets. The abrasion resistant rubber washers fit very tight and needed to be threaded onto the shafts.
They also operate a bit nicer with the wing nuts loose as I have steel washers on the inside as well.
Thoughts?
For the manufacturer that's a pretty hard detail to get perfect. You have to consider deformation of the pipe from production, packing, shipping, and installation. Then be operable with out binding up. Even though it should be a balance check, and that's the last it will move in most systems.
Your method is fine. The only thing I can think of is the rubber washers dry rotting over time in a hot environment like an attic. Other than that just the tedious work to implement the fix.
Will it make much of a noticeable difference. Probably not. Will you ever stop thinking about it if you don't bring it up to your standards deffinetly not
0 -
I've always been of the thoughts that vented attics were mainly to prevent ice dams in winter.
@ChrisJ go for it, everything that helps, even if it's 1% is money saved! I tend to overthink/do most things as well.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
-
@Gordy fiber re-enforced neoprene rubber washers.
I assumed they should hold up fairly well in the attic.
But, your comment made me think about my idea of using foam tape as a gasket on the air handler. Silicone may hold up, but the typical cheap stuff likely won't.
Problem is that silicone tape is expensive, so I'll have to think about it. I liked the idea of a gasket rather than RTV or tape.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Also,
@Gordy I'm not really attacking the manufacturer in this thread. They all appear to be made this way, it's normal.
Not to mention the product they give for the price.
However, some rubber washers don't cost much.
If I followed @Solid_Fuel_Man 's way of thinking, I wouldn't even need to seal the duct work. It would just leak into a conditioned space. Zero loss.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Well the attic isn't living space. You want your conditioning in the living space. Trying to keep equipment as close to conditioned as possible with little energy.
Okay you said rubber, but fiber reinforced neoprene much better.
I would do gasket material instead of silicone. I think you will find it easier to assemble the parts, and cleaner. Once assembled you could always hit it with a little silicone here, and there in areas you may have concerns. Smell of silicone may linger in the ductwork also.0 -
I was talking about silicone gasket. The gasket I have on my monitor top is soft black silicone. Works well, but dust sticks to it like a magnet.Gordy said:Well the attic isn't living space. You want your conditioning in the living space. Trying to keep equipment as close to conditioned as possible with little energy.
Okay you said rubber, but fiber reinforced neoprene much better.
I would do gasket material instead of silicone. I think you will find it easier to assemble the parts, and cleaner. Once assembled you could always hit it with a little silicone here, and there in areas you may have concerns. Smell of silicone may linger in the ductwork also.
When I buy rubber washers, or gaskets I generally stick to silicone, Neoprene or Buna.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
@ChrisJ - If you want to seal the ductwork to most current standards, you'll need to use duct mastic and/or UL181 foil tape.Steve Minnich-1
-
I had been planning on clear silicone to seal every joint and seam. Rumor on the streets is this what is approved for use in clean rooms. That's not why I chose it, but, was nice to know.Stephen Minnich said:@ChrisJ - If you want to seal the ductwork to most current standards, you'll need to use duct mastic and/or UL181 foil tape.
But now that I'm digging into it, I may go with mastic due to cost and effort.
I'll use tape for the insulation vapor barrier of course.
Right now on the problem solving blotter is what to do with these.
They come with a "plaster flange" on them, that is a 1/2" up from the opening. This causes a big problem for me as they are going in plaster ceilings and that flange won't sit flush against the wood lath, and the 1/2" that sticks past it won't reach all the way to the finished side.
I pulled the flange off which was easy enough and I'm thinking about mounting them in just like this with the front flush with the ceiling. Next, filling around them in the attic with spray foam and then finishing the gap with something, don't know what yet though. Joint compound would work good enough and could be painted. White paintable caulk could also work.
The gap would of course be covered by the diffuser anyway, but I want it sealed and respectable looking regardless.
The seams in the box will of course be sealed before installing and the box will be insulated with R8 or better.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Duct butter, AKA mastic as mentioned above. Way better seal than foil tape for most/all uses IMHO.0
-
Do you use mesh with the mastic, or just mastic alone?ratio said:Duct butter, AKA mastic as mentioned above. Way better seal than foil tape for most/all uses IMHO.
Also, any specific brand, or formula you recommend? I've seen many out there and my only assumption was what Home Depot has is likely crap. I could be wrong there too, though.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
@ChrisJ - remember the pic I sent you of the boot "ears"? Those can be made to any size/depth very easily on a small brake or a bench type bar folder.Steve Minnich0
-
-
I've never used mesh with it, but it would probably be a good idea. As for brands, I think we just get whatever the supply house carries when we call for a stock order. If the system isn't pressurized, you can lay it on as thick as necessary to seal the gaps—it just takes longer to dry. I'm sure there's a limit to how big a void you can fix with it though.
I've actually shinnied down three stories worth of ≈ 60" x 120" medium pressure duct to seal it from the inside out. Put gallons of butter in it, but at the end I wouldn't want to be in that duct without the fan moving air.
I was not happy about having to do that, BTW. Words were said.
0 -
Hi Steve,Stephen Minnich said:@ChrisJ - remember the pic I sent you of the boot "ears"? Those can be made to any size/depth very easily on a small brake or a bench type bar folder.
Yep I remember, but for some reason I thought they were backwards?
This is what I came up with, and may be exactly what you had shown me, I can't remember.
I'll shoot you an email.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
@Stephen Minnich
Found it.
This is essentially what all of the boxes came with, but I want the ear on the finished side of the sealing. That's what makes sense in my mind. Maybe I'm being stupid? It's very possible especially on this subject.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
> @ChrisJ said:
> If I followed @Solid_Fuel_Man 's way of thinking, I wouldn't even need to seal the duct work. It would just leak into a conditioned space. Zero loss.
Well that is only if 100% of the equipment is in the conditioned space. That includes ductwork and/or piping.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!1 -
@ChrisJ - by having the metal on the finish side has no upside. Having it on the unfinished side gives you a great means of screwing in your register or grill, creating a tighter seal.Steve Minnich1
-
Square ceiling box without flange is screwed into framed opening using drywall screws. White paintable caulk is used to seal the gap around the ceiling. Aluminum diffuser is screwed into framing around box through plaster ceiling.
The screws through the box as well as all seams will be sealed using clear silicone.
Am I over thinking this, probably.
But I like having a plan.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
What's your tactic for making a nice cut through the plaster, and lathe?0
-
@ChrisJ , that's as good or better than any other method.
Not to make it more picky but you could glue 1/2" duct liner or 1/2"armaflex to the inside of the box to prevent condensation.
Just curious, is your drawing in Visio??
Plaster & lathe can be tough to cut with a sawzall can shake it loose and break some plaster. Suggest a grinder with a cutting disk and just use a jab saw on the corners if needed.0 -
-
I have a Dewalt power cut-out tool and use a Roto-Zip Dura-cut bit. That works great for smooth, straight cuts. The Dura-Cut bit is designed for Plaster and lathe cutting.0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements