Adding a shed to current Zone Circulator Question
miikeyd
Member Posts: 5
in Oil Heating
I am considering adding my shed to my current second floor heat Zone in my home. I have only two rooms upstairs. My circulator pump runs the first floor and the second floor zone. Of course the circulator makes the trip upstairs and back down. What I am considering doing is going from my second floor zone to the top of my shed and down to a baseboard heat and old fashioned radiator and back up to the second floor. My question is should or could the circulator be able to complete this new Loop. Should I just try it and see or is there a way to determine if this will work without a second circulator pump. Thank you for your time and assistance great site.
0
Comments
-
You need to figure out what the new head loss will be and what flow rate your existing pump will produce for that loss -- and then whether that flow rate will be adequate.
There are two ways to pipe this: either the shed and second floor zone in parallel, which will increase the flow rate for a given head, or in series, which increase the head for a given flow rate. The former will present some significant balancing problems; that latter may not provide enough heat for either the shed or the second floor, depending on which comes first, as well as likely being unbalanced.
But without the head calculations you can't determine where on the existing pump's head/flow curve you will be, and therefore whether or not it will be appropriate.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England-1 -
-
-
Ty i will try to answer photo too asap!0
-
Ty for help guys propane ??? lp nah!?0
-
-
I agree with Jamie. by the time you add zone, figure out how to run the pipe without freezing it which will involve insulation and/or glycol, you could just put in a separate heater and be done with it. The Gas line can just be buried back to your tank.Jamie Hall said:Um... if that were my situation, I'd put a nice little vented propane wall mounted hot air unit in the shed...
"If you can't explain it simply, you don't understand it well enough"
Albert Einstein1 -
Ty0
-
I actually own one of those!0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements