Mixing 1/2 PEX and 3/4 PEX in a single zone
dgkula
dgkula Member Posts: 59
Question for the pros please: I have a single zone in my basement which is plumbed off a manifold with 1/2 PEX to 15' of fin tube (based on 3/4 copper pipe). I want to add a second radiator to this zone to heat a soon to be finished area of the basement. A plumber has proposed adding 8' fin tube and running 3/4 PEX, splicing that into the return from the 1/2 PEX, creating a single loop consisting of source >1/2 PEX > 3/4 fin tube > 1/2 PEX > 3/4 PEX > 3/4 fin tube > 3/4 PEX > return. Is this going to be OK? Naively I would think that single diameter for the whole run would minimize changes in pressure throughout the zone for a constant flow rate but I don't know if it matters. Of course an option is to have him re-plumb the original 1/2 for 3/4 PEX so that all diameters are the same but I have read that PEX expands as it heats ...
Thanks!
David
    Jamie Hall Member Posts: 26,837
    It's fine. Won't change the pressure much. The additional piping -- of any size -- and fin tube will increase the pressure drop around the loop, but not by much for that length.
    Zman
  • Zman
    Zman Member Posts: 7,611
    Your 23' of baseboard will put out round 13,000 btu. You only need to move around 1.3 gpm. That should be easy with the piping you described.
    Albert Einstein