Pilot lights okay, but burner won't turn on
Edwinjcb
Member Posts: 2
in Gas Heating
I just installed a gas valve on a wall heater. Robert Shaw 710 502. I can get the pilot to light just fine, but can't get the main burner to fire up. It was working on the old valve, unit it wore out on me. The Robert Shaw is a used valve which I'm told was working when it was removed. Wiring appears correct. The fact the pilot light works leads me to believe the thermopile is okay. Any ideas from anyone? Otherwise, I'm going to conclude the gas valve is bad.
0
Comments
-
-
check your millivolts prior to condemning the valve.0
-
there is no tiny switch on the gas valve. I'm jumping the two screws at the thermostat, which eliminates a possibly bad thermostat. where do I check the millivolts? on the thermopile? Is it possible the thermopile is bad so it's preventing the gas valve from sending gas to the burners?0
-
Is this a 750 millivolt system? If it is then you need to do a complete diagnosis.0
-
Go to before you ask and click the second "here" and look for my ugly face the procedure for checking millivolts is there.0
-
Is the knob on the gas valve turned to "ON" position and not the "Pilot" position?0
-
Used gas valve? Not a real good idea....jmo....0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements