Burnham IN6I or IN7I?
I wanted to use an IN7I which has DOE rating of 173k btus. I can't get one for at least a couple of weeks. A W/M is at least 3 weeks out. My distributor has an IN6I which has an output of 144k btus. Should I go for that or is it too small? Total EDR is 555, but I don't need a 1.33 pickup factor since the actual piping loss is 25k btus.
Thanks, guys.
You can choose to do what you want, but you cannot choose the consequences.
Comments
-
-
It's concerning because he calculated the actual piping losses, and he's below even that.Hatterasguy said:You're looking at an 8% pickup factor.
This can be done but you'll probably regret it. It will be difficult to balance and you'll absolutely need venting on every riser in the building.
It will operate forever on no pressure.
I might do it as an experiment. You're not in the "experiment" business.
If that building needs 100% of it's radiation he's in trouble right off the bat, even if the system is balanced.
@Ironman is all of the piping that can be, insulated?
How about a WM EG-55? That'll give you an output of 167K.
You know how much I push smaller steamers, but even I wouldn't recommend the IN6. It's below your radiation and piping losses in a fairly large building.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Or, maybe better yet.
Two IN4s?
Two IN5s seems like too much to me, but could work as well.
Not sure if you can mix and match when doing two setups. like an IN6 and an IN3.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
I think you did a new distributor! Also, I very much prefer a Weil EG over the Burnham IN.New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
Weil has 3" supply trappings, a real and usable skim port, and Safgard instead of Cyclegard, amongst others. Plus, don't trust Burnham castings except MegaSteam.New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com4 -
Peerless 63 series good too (except Cyclegard), if you can get that.New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com2 -
I also like multiple steam boilers. Once the system is hot it works really well cycling off one boiler.0
-
Sure,Hatterasguy said:A two stage gas valve with a larger boiler works even better. The twins are not valuable unless you must have the redundancy.
Except that the twins run with the proper amount of excess O2 where your big boiler on low fire does not.
Assuming an atmospheric setup of course.
I recommended the twins as something he could do.
I suspect as you said, the cost will be too much and just not worth it, but it is an option.
Redundancy is nice.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
It's common sense.Hatterasguy said:
What is the "proper amount" of excess O2?ChrisJ said:
Sure,Hatterasguy said:A two stage gas valve with a larger boiler works even better. The twins are not valuable unless you must have the redundancy.
Except that the twins run with the proper amount of excess O2 where your big boiler on low fire does not.
What does the "big boiler" produce on low fire as to amount?
Have you done any testing regarding your conclusions?
Drop the manifold pressure and excess O2 goes up.
More excess O2 means lower efficiency.
Are you going to argue that?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Only one we ever tested and messed around with was mine.Hatterasguy said:
Never tested one for excess O2.ChrisJ said:
It's common sense.Hatterasguy said:
What is the "proper amount" of excess O2?ChrisJ said:
Sure,Hatterasguy said:A two stage gas valve with a larger boiler works even better. The twins are not valuable unless you must have the redundancy.
Except that the twins run with the proper amount of excess O2 where your big boiler on low fire does not.
What does the "big boiler" produce on low fire as to amount?
Have you done any testing regarding your conclusions?
Drop the manifold pressure and excess O2 goes up.
More excess O2 means lower efficiency.
Are you going to argue that?
No idea about efficiency loss.
Wants to rely on "common sense".
OK.
You haven't even done that much.
But, just for the sake of argument.
@Tim McElwain Would you say it's fair to assume that if you reduce the manifold pressure on an atmospheric boiler, the excess O2 will increase therefore decreasing efficiency?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
It's not a factually incorrect statement, you can reduce the manifold pressure to whatever the low stage would be without another valve.Hatterasguy said:
What efficiency loss did you get when you used a two stage gas valve on yours?ChrisJ said:
Only one we ever tested and messed around with was mine.Hatterasguy said:
Never tested one for excess O2.ChrisJ said:
It's common sense.Hatterasguy said:
What is the "proper amount" of excess O2?ChrisJ said:
Sure,Hatterasguy said:A two stage gas valve with a larger boiler works even better. The twins are not valuable unless you must have the redundancy.
Except that the twins run with the proper amount of excess O2 where your big boiler on low fire does not.
What does the "big boiler" produce on low fire as to amount?
Have you done any testing regarding your conclusions?
Drop the manifold pressure and excess O2 goes up.
More excess O2 means lower efficiency.
Are you going to argue that?
No idea about efficiency loss.
Wants to rely on "common sense".
OK.
You haven't even done that much.
That would be a factually incorrect statement.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Thanks guys.
I was told at least 2 weeks on the IN7 and 3 weeks on an EG-55. A 63-05L won't fit through the three 28" wide doors that it has to go through, so that's not an option.
It certainly not my favorite, but I got a 7 section Dunkirk that will be here on Monday.
As far as distributors: REM, Noland and Hajoca on the Burnham; Southern Refrigeration for W/M. Burnham told my REM rep that it was a "custom build" for the 2 IN7's they have on order already! Seriously?
I know that being in VA we don't have as much steam as the Northeast, but we've got a good bit around here and in Richmond and D.C.. I just can't believe that there's not more steam boilers stocked - especially by a distributor that has 325+ branches.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
A 4" header for one boiler. Wow. Looks like ECR has made so that I'll spend as much on near boiler piping as I did for the boiler itself.
Thanks for the info.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
From the sales brochure:
It looks like a M/M PSE801 that's up a few inches.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
@Hatterasguy, what is pictured? Is that (2) LWCO? One remote probe? Do I remember that pic from another thread, or is that yours?0
-
There's a 3rd in the block somewhere?0
-
remember guys when tweaking load sizing, it is piping AND pick up factor, not piping pick up factor. Pick up factor is for coming out of setback, if your a police station for example, and manned 24/7 you don't really need a pick up factor as heat would usually be constant. You do however need piping factor.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements