Minimum distance between 2 boiler vent?

Options
Jacob777
Jacob777 Member Posts: 1
I'm installing two Burnham Alpine condensing boilers in multifamily. I know that distance between air intake and exhaust must be more than 12 inches. I wonder if there's a minimum distance between two boiler's intake and exhaust? I'm in the state of MA,Thank you!

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 23,345
    Options
    Check your local codes. There may be something in there. Otherwise, so far as I know, the two intakes can be close together, and likewise the two exhausts -- so long as the exhaust to intake spacing is adequate.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Zman
    Zman Member Posts: 7,569
    Options
    Not sure about MA as the laws of physics are slightly different there ;) . In most areas the manufactures installation instructions take precedence. It is a good idea to separate the intakes and exhaust as far as you reasonably can. Cross contamination will destroy your boilers.