T
JPL941
Member Posts: 51
Hello
0
Comments
-
Well, for starters, the boiler is piped totally wrong. Look at the piping diagram in the instruction manual and you'll see the difference. Improper piping can cause water to leave the boiler along with the steam.
Not sure if the air trap still has a vacuum check on it- if so, remove it, since this can cause water to not drain back as it should.
You need a Steam Man. Where are you located?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Thanks
0 -
I know exactly where that is- passed through there on my way to Williamsport to play in the Liberty Classic. About a 2-2.5 hour drive from Baltimore, depending on how bad the traffic is at Shamokin Dam.
I'd have to get a closer look at the piping to answer your first question.
Yes, the vacuum check is the thing screwed into the air eliminator. Unscrew it and see if that helps.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Also you oversized it. Should have used an IN5 max.2
-
Also your cutout pressure (2 psi as I read it) is high. That's not going to help a bit. Something you can do today -- go down there and dial that cutout back down as low as it can go without falling apart.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
As has been said, that boiler is piped completely wrong. Has the boiler ever been skimmed? I don't mean drained and refilled, I mean a real (probably several) long slow skims from a skim port above the boiler water line. Oils sitting on top of the boiler water will cause water to push back into the wet returns. Also, the water level is too high. Reduce it to no more than 3/4's of the sight glass. You're not leaving much room for a steam chest in that boiler. Skim, Skim, Skim.0
-
Hello0
-
With the water line that high and the riser?? coming horizontally right of the boiler (instead of at least 24" above the water line), you basically turned it into a hot water boiler with a restricted return.
And, are my eyes deceiving me or is the water heater supporting the steam piping?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements