2 month old circulator not silent anymore
Comments
-
What's your system pressure? How's the pump mounted? With the motor horizontal or vertical?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Agree with ironman, check the pressure, also If you have a flow or sweat check installed in the loop, they can make a chattering noise sometimes when the circ is running. Check the pressure and make sure the motor of the circ is horizontal and not vertical. Hope this helps you. Stevie G.0
-
-
15 psi, pump mounted correctly with motor horizontal.Ironman said:What's your system pressure? How's the pump mounted? With the motor horizontal or vertical?
Thanks, that's exactly what it is, the IFC that came in the circ. I watched a youtube video this morning that took one apart and the noise is coming from the exact location of the check valve. I also noticed that it's worse when only one zone is calling for heat but if both zones are open the chatter is significantly reduced. What I'm not sure of is why it didn't chatter/rattle right from the beginning. Going to call the installer and see if they can/will do anything after the holidays since it's really annoying when the house is quiet and you're trying to read a book.stevieg said:Agree with ironman, check the pressure, also If you have a flow or sweat check installed in the loop, they can make a chattering noise sometimes when the circ is running.
I did find an online homeowner review of the same pump reporting the same issue after about 3 months in service although their fix was to change it out with a Taco.0 -
Do you have zone valves or multiple circulators for zoning? If zone valves, then the check valve should have been removed at installation. If multiple circs, then the check valve or a flow check for each circ is required.
There are two recent threads that deal with this issue. Search for "banging noise" for more info.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.1 -
Over the weekend I replaced the IFC in my Grundfos 15-58 (used for the DHW indirect tank since July of this year) because of chatter noise too. I replaced it with the 1" inline flow-check from Caleffi (NA51069)... it's silent once again.
Also replaced the IFC in the CH ALpha with a 1" Webstone Isolator Double Flange Check Valve as well to prevent future problems with it's IFC.
0 -
If your t-stats operate the zone valves directly vs. using a zone control panel... you may still need a flow-check in the CH loop.
If you don't have an indirect DHW tank then disregard the above0 -
Two zone valves and one circulator. I wasn't there for the install but from the rattling noise coming from exactly where the IFC comes pre-installed @ the outlet I'd guess it's still in there.Ironman said:Do you have zone valves or multiple circulators for zoning? If zone valves, then the check valve should have been removed at installation.
There are two recent threads that deal with this issue. Search for "banging noise" for more info.
I didn't see anything in the search results for "banging noise" sorry.0 -
Thanks, I'm guessing you were hearing the same thing I am but it's so hard to describe because it's not loud like banging or gurgling just this constant rattle/chatter that the pipes transmit. I have a zone control panel. We'll see what the installer offers to do about it. I miss my Tacos, they were so silent I used to have to touch them to feel if they were running. Not impressed so far with Grundfos I have to say.NY_Rob said:Over the weekend I replaced the IFC in my Grundfos 15-58 (used for the DHW indirect tank since July of this year) because of chatter noise too.
0 -
I was hearing a "chattering/rattling" sound from the pump- it had been fine for a few months. This 15-58 pump was for the indirect DHW tank... so it only came on for maybe 10 min a couple of times per day vs. your much heavier use as a spaceheating loop pump.
An easy way to see if you need the IFC or an inline IFC in the spaceheating loop would be to turn up one of your T-stats to produce call for heat, at the same time run a shower, load of wash, etc... or whatever it takes to produce a call for the DHW circulator circuit activate. Once the DHW circulator is running- see if your zone valve is still powered open- if it is- you need a IFC or inline flow-check in the spaceheating loop. If the zone valve(s) power off on a DHW circulator cycle- you don't need a IFC or inline flow-check.
If it turns out you do still need a flow check in ths CH loop- both of the ones I linked in my previous post will give you silent operation again. The Grundfos pumps are really quiet- but their IFC's seem problematic.0 -
Here ya go:gschallert said:
Two zone valves and one circulator. I wasn't there for the install but from the rattling noise coming from exactly where the IFC comes pre-installed @ the outlet I'd guess it's still in there.Ironman said:Do you have zone valves or multiple circulators for zoning? If zone valves, then the check valve should have been removed at installation.
There are two recent threads that deal with this issue. Search for "banging noise" for more info.
I didn't see anything in the search results for "banging noise" sorry.
https://forum.heatinghelp.com/discussion/160208/loud-whoosh-and-bang-when-zone-valve-opens-not-closes#latest
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
With the 2 zone valves, you can remove the IFC from the circ completely, make sure you get it all out of there, it can be tricky. It use to say not to mount the circ with the IFC installed pumping down, I have seen them plug up over time because boiler water can be some of the most disgusting stuff in the world. Yikes0
-
Thanks. Will double check this later today but I assume the zone control would close any open heating zone when my 40 gallon indirect calls since it's zoned priority on the Taco ZVC404. Cheers for the links to the external flow checks, hopefully I won't need one.NY_Rob said:I was hearing a "chattering/rattling" sound from the pump- it had been fine for a few months. This 15-58 pump was for the indirect DHW tank... so it only came on for maybe 10 min a couple of times per day vs. your much heavier use as a spaceheating loop pump.
An easy way to see if you need the IFC or an inline IFC in the spaceheating loop would be to turn up one of your T-stats to produce call for heat, at the same time run a shower, load of wash, etc... or whatever it takes to produce a call for the DHW circulator circuit activate. Once the DHW circulator is running- see if your zone valve is still powered open- if it is- you need a IFC or inline flow-check in the spaceheating loop. If the zone valve(s) power off on a DHW circulator cycle- you don't need a IFC or inline flow-check.
If it turns out you do still need a flow check in ths CH loop- both of the ones I linked in my previous post will give you silent operation again. The Grundfos pumps are really quiet- but their IFC's seem problematic.0 -
"Cheers for the links to the external flow checks, hopefully I won't need one."
That's the point: not only do you not need one, you don't want one with zone valves. If it's still there (they come pre-installed), then it MUST be removed.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
As long as your Taco ZVC404 is wired and configured properly- you don't need the IFC's or any flow checks- but it's good to verify it's working as intended by having a DHW call interrupt a spacheating call and observe that the open zone valve(s) close.
In a very simple layout (w/o zone control panel) where the t-stats operate the zone valves directly and their end switches go to the TT terminals on the boiler- you need the flow checks in both circuits as the t-stats will hold the zone valves open during a call for the DHW circulator.0 -
I watched as a DHW call closed the open CH zone so I called the installer and he is coming next week to pull out the IFC. He "didn't remember" if he pulled it out at time of install, but I told him about the rattling noise where it comes preinstalled in the pump outlet and he thinks maybe he forgot.
What's the downside of having left it in? Other than the annoying rattle. Does it actually damage anything? It's just a flow check so I'm still a little fuzzy on why it MUST be removed.0 -
"What's the downside of having left it in? Other than the annoying rattle. Does it actually damage anything? It's just a flow check so I'm still a little fuzzy on why it MUST be removed."
Read the posts by Harvey Ramer and myself in the attached threads.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
The homeowner is so upset he posted on a public forum. " The noise is transmitting to all the baseboard piping and we're having to use white noise to drown it out." It MUST be removed to eliminate the noise. I don't know if that helps with the fuzz.
Happy Holidays.There was an error rendering this rich post.
0 -
Perhaps you missed my qualifier "other than the annoying rattle" or perhaps you weren't being condescending as **** on purpose.bob said:The homeowner is so upset he posted on a public forum. " The noise is transmitting to all the baseboard piping and we're having to use white noise to drown it out." It MUST be removed to eliminate the noise. I don't know if that helps with the fuzz.
Happy Holidays.
Anyway, my sincere thanks to NY_Rob & stevieg for using clear layman's language to explain. Happy holidays!0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements