Thermostatic Radiator Valve
crawas
Member Posts: 134
in Gas Heating
I am using Gorton steam valves for my whole house. One of the rooms I cant seem to get working right. The #4 valve is too cold and the #5 valve is too hot and Gorton makes nothing in between. Should i splurge on a Danfoss Thermostatic Radiator Valve? is there something else on the market that i can buy to fix this problem?
0
Comments
-
We assume you are referring to air vents not steam valves.
You cannot put the standard TRV valve on 1 pipe steam.
There are thermostatic air vents though.0 -
yes i apologize....im not so good with the correct terminology....yes i mean the air vents....the ones that screw on to the free standing radiator. I have 1 pipe steam system.0
-
You could. On the other hand, there are several variable orifice vents available which you might try, give you an ability to set it in between somewhere. A lot cheaper...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
thanks! can you point me in the right direction of exactly what i could buy?0
-
The Gorton #4 vents at 0.025 while the #5 vents at 0.080 cfm. If you replace the vent with a VentRite # 1 you can dial anything from 0.025 to 0.083 cfm, that should do what you need.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Thank you. Now I have another question about a room that has a gorton c valve. That room is always cold. If I use a thermostatic valve will it also work to make the room hotter like it works to keep it cooler? If I set it to 75° or 80° will that help the situation?0
-
Air vent TRVs only stop the steam heat from coming.
Only bigger or faster air vents will get it there.
Maybe the line feeding that rad needs a large vent in the basement.
What do you have for main air vents in the basement?
0 -
That's out of my league lol. I wouldn't even know where to look and the line supplying that rad is likely in a ceiling or wall.0
-
Can someone tell me the range of settings on the ventrite #1? I've been looking online and in one place it says that 1 is off while in another place it says 1 is .033?0
-
The vent rate is between 0 cfm (at 1) to 0.083 cfm (at 8), this places it at the low end (in capacity) of radiator vents. It is very well made.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Ventrite #1 Setting 1 Off @1 oz
Ventrite #1 Setting 2 0.033
Ventrite #1 Setting 3 0.025
Ventrite #1 Setting 4 0.030
Ventrite #1 Setting 5 0.045
Ventrite #1 Setting 6 0.056
Ventrite #1 Setting 7 0.070
Ventrite #1 Setting 8 0.083
Based on Gerry Gill's bench testing
0 -
Thanks everyone!0
-
Hi guys. I’m back. I have a question about the vent rite #1 vent. Setting 2 is .033 and setting 3 is .025, so wouldn’t that mean that setting 3 cents slower than setting 2? I thought the higher the number then the faster the venting?0
-
I think those numbers are transposed in the rating table.0
-
Yea I thought so.
I’m helping a friend of mine balance some rad vents. His kids room gets stifling and he has a very old gorton 5 there that had the hole all taped up. Anything smaller than a gorton 4? It looks like the hole on the 5 he has was made bigger also0 -
Anything?0
-
@crawas The Gorton #4 vents at .025 CFM at 1 ounce of pressure. That is about the smallest there is. This isn't the result of some funny piping issue, is it? Like that particular radiator piped right off of the Header instead of the main? How many EDR is that radiator? It may mage sense to exchange the radiator, if it's too large.0
-
thanks fred. this is for a friend and putting the gorton 4 helped a lot.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements