2 Children Killed In Radiator Mishap In Bronx Apartment
mookie3333
Member Posts: 83
Sad. What could have caused this? Faulty pressuretrol? Clogged pigtail? I'm no expert, but don't buildings like these usually have multiple pressure regulators?
http://abc7ny.com/news/2-kids-killed-in-radiator-mishap-in-bronx-apartment/1644053/
http://abc7ny.com/news/2-kids-killed-in-radiator-mishap-in-bronx-apartment/1644053/
0
Comments
-
My money is on lack of maintenance.mookie3333 said:What could have caused this?
1 -
-
Really sad! I can't imagine how a valve would "Pop Off" I'm betting it was probably a radiator vent. If it was truly a valve, it had to be loose and in bad disrepair. Children have to be watched so closely. There is no way they should be that close to a steaming hot radiator. Hind sight is always 20/20.0
-
-
@Fred they don't need to be close to it to die. If the pressure was too high and the vent came off there could have been a massive release of steam. As Dan said it displaces the oxygen and suffocates people.
I'm sure I have told this story before, but here it is again. My father worked in power plants for 32 years and used to take me on tours. He pointed at the main steam feed to the turbine once and said "If that pipe bursts everyone in the plant will be dead within a few seconds". He wasn't kidding. It's a great heat source, but too many don't respect it as they should.0 -
-
To die from burns that quickly would have had to melt their skin completely off. It says the mom was trying to revive them, that makes me think suffocation. Usually death from burns takes days and typically it's from infection.
I'd bet the news doesn't know and they are guessing that since it's steam it's burns or I am completely wrong. We will probably never know for sure.1 -
The size of children that age would put them down pretty low. Inhaling steam certainly would cause internal burns, especially to the lungs and collapse them but like you said, we'll probably never know all the facts. This is just a tragedy.0
-
Oh my, tragic...0
-
Steam rooms are usually about 115 degrees with 100% humidity. We're not supposed to stay in there for more than 20 minutes. Imagine a small, closed bedroom with steam pouring out of a hole in a radiator for eight hours or more. The kids may be in cribs. It's always horrible, and we can never be too vigilant.Retired and loving it.0
-
So sad. @Dan Holohan. I think that you referenced one of these stories in we got steam heat. My mom actually knew the young woman who removed the air vent. If memory serves me right, she was babysitting her niece. Double tragedy. One is the death of the poor baby and one is the life long guilt of the poor babysitter. She probably didn't know any better and was advised by some "expert" to remove the air vent so the baby would be warm. So so sad0
-
Back in my rep days (we sold Hoffman), a child died in a steamed-up bedroom with a closed door. Eyewitness News shot a close-up of the Hoffman #40 vent on the floor near the radiator as the reporter said, "This is the valve that killed the baby."
That was difficult.Retired and loving it.0 -
Yup. That's the one. My mom knew the family. Just watch the government try to ban steam or air vents or whatever else makes for a self righteous headline0
-
I'm with KC suffocation. Tragic, what are the odds even though this type of incident has happened before.
All forms of heating has dangers more so from CO across all types.0 -
Updated now says 'A city official said a valve cap appears to have been blown off a radiator, possibly by the force of the steam'. I wonder what they mean by 'valve cap'. Would certainly make sense for it to be an air vent. There was another article which described the girls as having turned purple. Sounds like suffocation to me.....
So sad. Thoughts and prayers with that poor family.0 -
Air vent or supply valve bonnet?Retired and loving it.0
-
One more reason not to run on pressure at all. My boiler is only going to run around 40% of a given hour broken into three cycles leak or not. There would always be a lot of time for leaked steam to collapse and air to return. A significant leak in a closed bedroom with a pressure controlled system - even very low pressure - would be a much worse situation than I would have. Much more steam could potentially be released due to the pressure, and the uninterrupted run time significantly lengthened due to the pressure cutoff not being satisfied the way it usually is.
Question: Anyone have any kind of numbers to put to how often this has occurred? I'd never actually heard of it. I would think it must be quite rare.1926 1000EDR Mouat 2 pipe vapor system,1957 Bryant Boiler 463,000 BTU input, Natural vacuum operation with single solenoid vent, Custom PLC control0 -
-
Have you (or any one else here) ever heard of a valve bonnet coming off? seems like the necessary pressure for this (assuming the valve to be in decent shape) would be blowing the relief valve long before it blew the bonnet off a valve. Obviously we are speculating without any real information here, but it does sound like it was something sudden and forceful, so.....packing disintegrated small steam leak, packing nut starts to corrode, eventually bonnet corrodes until it finally gives out? Maybe? Would take quite a long time, and there would be lots of warning signs.....Not saying this is unlikley, just trying to figure out what this could have been.DanHolohan said:Air vent or supply valve bonnet?
0 -
Could have someone with a wrench.Retired and loving it.0
-
Very trueDanHolohan said:Could have someone with a wrench.
0 -
Im shocked..i don't know what to say. I would not have thought that possible..and yet as Dan says, it has happened before..there is shop safety training agenda coming out of this thread..i feel so bad for the family. Devastating.
gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.2 -
I'll bet pressure was higher than needed and accelerated a bad situation. Horrid. Mad Dog1
-
Reports first said "exploding" radiator...now they were "burned" by steam. We shall see. Mad Dog0
-
Parents probably put them down for a quiet nap..closed the door. I really can't stand when people complain about getting old. When we went to Ireland a few summers ago, I bought a refrigerator magnet:
"GETTING OLD IS A GIFT AND A PRIVILEGE DENIED MANY! Tis true. Poor babies. Mad Dog2 -
Live in Queens and saw this last night on the local news -- it's so horrific and sad. Hope the parents setup some type of gofundme , would love to help them a bit.
been wondering the same thing -- what exactly happened? they keep talking about a radiator exploding and valve popping off, that seems extreme. As Dan mentioned , someone took the air vent off completely perhaps ?
either way, this is sad
Harry0 -
also, in NYC with a building that size, there had to have been two pressuretrols. Question is, were they checked and/or actually working... This is gut-wrenching.0
-
I don't care what industry standard is, I ALWAYS take the Manual reset pressuretrol down to atleast 5 p.s.i.....No reason on a l.p. system to have it higher. Mad Dig0
-
-
What a horrible death.0
-
It seems very odd.
They didn't scream? A steam vent blew off of a radiator, I assume due to excess pressure and no one heard that?
From another related article, people complaining about the radiators.
http://nypost.com/2016/12/08/residents-complained-about-radiators-before-tots-tragic-deaths/
"“The radiator starts steaming and the walls get wet. It gets to a point where you can’t see anything,’’ Livingston said. “You hear ‘pop,’ [and] the stuff under the radiator explodes.”"
It sounds like the system was in desperate need of repair and the slumlord knew it.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
On old radiators the tappings can get kinda loose and the vent could fall off in your hand. I still say pressure was higher than 2 p.s.i. Mad Dog0
-
I wouldnt assume excess pressure yet. As a Bronx kid who grew up in an apt buiding I can confess that I used to hang from those vents all the time when radiators werent hot. And when they didnt seal, we never reported it- it reduced static electricity, they were considered humidifiers, never had a bloody nose from dry air. In fact, we held our stuffy noses over it when we had colds.
My guess is vent treads were compromised.
My brother replaced one on the top of a riser in his house. It didnt hold! by the time we got up there, it was a foggy rain forest. We couldnt get near it. we had to wait. he runs around 1psi.
0 -
Well see, but based on the reports of them dying by burning, not suffocation, I'm saying higher pressure AND some other stuff that doesn't make sense. We're they left alone too long? a two year old is able to walk or crawl away from something that's burning them..screams... Well see, but I'm betting there's more to this story. Mad Dog4
-
-
NY post showed them removing the "bad" radiator. So much for being able have several knowledgeable people in to assess what actually happened. The man that was with company removed it said to paraphrase "...sometimes they just pop off when pressure is too high." Read the article yourself. As I said above, looks like other extenuating circumstances probably lead to this terrible loss. Mad Dog0
-
Translation: I have no idea what I am talking about, but I am on the news and will spew some random garbage that the public wants to hear.Mad Dog said:"...sometimes they just pop off when pressure is too high."
Why is this country afraid of honesty? Without being there I think most if not all of us know this was a maintenance issue or a neglect issue. Why is the news or the powers that be afraid to say that? To protect other children we need honesty, blaming the rad is stupid and helps no one.
Here is he exact quote from the article:
too much pressure from the steam can cause the valves to pop off.
“When there is too much pressure, the whole thing blows,” he said.
The amount of pressure that would take with everything installed properly is way beyond the safety limits installed on the boiler. Again don't just say pressure say why there was that much pressure. The landlord is a deadbeat and doesn't take care of the property and it killed 2 children today.
It's tragic and sugar coating it will kill more children in the future.1 -
Curious what the PSI rating of an 1/8" thin brass NPT connector is.KC_Jones said:
Translation: I have no idea what I am talking about, but I am on the news and will spew some random garbage that the public wants to hear.Mad Dog said:"...sometimes they just pop off when pressure is too high."
Why is this country afraid of honesty? Without being there I think most if not all of us know this was a maintenance issue or a neglect issue. Why is the news or the powers that be afraid to say that? To protect other children we need honesty, blaming the rad is stupid and helps no one.
Here is he exact quote from the article:
too much pressure from the steam can cause the valves to pop off.
“When there is too much pressure, the whole thing blows,” he said.
The amount of pressure that would take with everything installed properly is way beyond the safety limits installed on the boiler. Again don't just say pressure say why there was that much pressure. The landlord is a deadbeat and doesn't take care of the property and it killed 2 children today.
It's tragic and sugar coating it will kill more children in the future.
It's a whole lot more than 15 PSI I bet.
Why is the country afraid of honesty?
Because a news article like this is a lot more interesting, and unique than the truth. Well, what I personally believe the truth to be based on the little bit of evidence supplied. TV and radio are controlling the people, not the other way around. People want honesty, they never get it and they are not quick to question things.
Our news is there to sell a product, not fact and not honesty. It's job is to sell, sell, sell. Not to inform.
Also let's not forget how they question people. They interview people, ask a ton of questions, often to get specific responses from people and then edit the footage to show what they want it to. Much like "reality shows" do. Remember Obama's "You didn't build that!" comment which was actually in regards to public highways and such? Same thing.
That's my opinion anyway.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment1 -
If you look up the raw rating for 1/8" NPT brass threads it's in the thousands of psi. There is a de-rate for temperature, but it isn't enough to get down to 15 PSI or less.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements