I recently wanted to add some more main venting capacity to my system and I came across the discussions of the Barnes & Jones big mouth vents up here, so I ordered 4 of them to add to the end of my mains. There are plenty of discussions already regarding their specs so no need for me to touch on that again.

What I will attest to is the build quality and execution of the design. These vents are awesome.....AWESOME!

Now not that a steam vent is anything to necessarily geek out over, but wow!!!! pick up one of these and look it over and you feel like you are actually holding something! The fit and finish are second to none, the unit is easily opened up if ever needed any type of servicing (Not that it should its simple as pie) the machining inside and the o-ring seals are gorgeously executed. The solid brass castings for the bodies are heavy and TIGHT, not some crater filled rough casting, I was truly impressed. So much so.....and feel free to call me a dork.....that I took the liberty of spending some time with a buffing wheel putting a high polish on them.

In my building the main vents dont live in the basement, they are mounted at the end of my mains which run along the ceiling in the ground floor which is usable living space. So they can be seen if you know where to look. So I figured why not do these justice and make then look even more impressive. So now when the system fires and shortly after you hear my system start exhaling with a soft whooooooosh coming from above you head and you look up, youll see four of these bad boys gleaming back at you.

I was really impressed upon seeing them, Peter Owens was kind enough to help with answering some questions I had, and these were a breeze to install and for something as mundane as an air vent, they just look bad ****......

oh and yeah.....my building heats up a bit faster now. So most importantly yes....THEY WORK. If you need a vent or vents, definitely take a look at these!












Weil McLain EGH 95 400,000 BTU single pipe steam
ChrisJIronmanSailahkcoppTinmanSWEIb_bzBrianT1077GregWeiss

Comments

  • Christian Garibaldi
    Christian Garibaldi Member Posts: 57
    edited December 2016
    Oh thank goodness!!! we must unite my brother!!! hahaha. Did you find that with as much time as it takes to get them nicely polished, its worth the time and effort and you find yourself peeking at them more? its like the vents smile back at you and say "Hi!"

    Im thinking some nice mood lighting aiming may be a nice touch too ;-)
    Weil McLain EGH 95 400,000 BTU single pipe steam
  • KC_Jones
    KC_Jones Member Posts: 5,796
    BobC said:

    If they weren't so heavy I'd hang them on the Christmas tree as ornaments.

    Bob

    My wife gave me permission to do just that, but I am thinking perhaps the Gorton vent they replaced might be a better (lighter) choice.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • Christian Garibaldi
    Christian Garibaldi Member Posts: 57
    edited December 2016
    Ok, I see where this is going so......
    If you really wanted to be hardcore and use the big mouth vents as Christmas tree ornaments, but are having issues with their weight causing the limbs to sag, you could just build a big tree from black iron pipe fittings and nipples and have antler branches with the vents on them. See how the wife and kids like that in the living room hahahaha!
    Weil McLain EGH 95 400,000 BTU single pipe steam
    RomanGK_26986764589bcoyle
  • gerry gill
    gerry gill Member Posts: 3,078
    I LOVE IT!
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • ChrisJ
    ChrisJ Member Posts: 16,231
    Ok,

    All of you have problems, you know that right?

    :)
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    kcoppAbracadabraJohnNY
  • Sailah
    Sailah Member Posts: 826
    Lol you guys are too funny. Those polished vents look awesome. Now I need to do one myself for my desk.
    Peter Owens
    SteamIQ
    TinmanNew England SteamWorks
  • Mad Dog_2
    Mad Dog_2 Member Posts: 7,446
    Now now boys....admit it...."gonna havta face it were addicted to STEAM..." They reeeeel purdy, though.... Mad Dog
  • KC_Jones
    KC_Jones Member Posts: 5,796
    My wife actually suggested I make a small tree out of spare fittings to decorate the boiler. I love my wife!
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • Abracadabra
    Abracadabra Member Posts: 1,948
    ChrisJ said:

    Ok,

    All of you have problems, you know that right?

    :)

    erhm... this coming from the guy that is obsessed with running his steam boiler at sub-atmospheric pressures? :p
    Neild5Paul S_3
  • ChrisJ
    ChrisJ Member Posts: 16,231

    ChrisJ said:

    Ok,

    All of you have problems, you know that right?

    :)

    erhm... this coming from the guy that is obsessed with running his steam boiler at sub-atmospheric pressures? :p
    That's why it's funny. :)
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • zackwatt
    zackwatt Member Posts: 81
    Looks awesome! I'll have to do mine at some point too!
  • BurntFingers
    BurntFingers Member Posts: 38
    Yes. They are looking really good..

    Has anyone done some testing for what approx. temperature the Big Mouths are opening between steam cycles? IF memory serves well, and it usually doesn't, the Gorton #2 opens at about 130F and the Hoffman 75 opens around 180F.

    Any data yet on the BMV's..?
  • Sailah
    Sailah Member Posts: 826
    Ours will operate with a 12-15 degree subcooling effect. If we assume the steam temp is 213 for most low pressure systems you're looking right at 200.

    I remember trying a test of this using a compressed air piece of pipe and a gauge but didn't have any luck getting repeatable results mostly due to setup and I was influencing the temperature with the air.

    We know from making traps for 100 years that our diaphragms are calibrated to that design subcooling temp and the Big Mouth is essentially a radiator trap with an o ring seal.

    If anyone has any good ideas about how to test for that opening temp I'm all ears. I suppose I could just close with steam, shut it off and them poke at the plug until I detect movement all while monitoring temps but that doesn't seem very scientific. Also the plug only needs to lift a fraction for it to open
    Peter Owens
    SteamIQ
  • Paul48
    Paul48 Member Posts: 4,469
    A drop in pressure, instead of poking.
  • scott22nyc
    scott22nyc Member Posts: 7
    The open pipe venting capacity and air vent charts attached on this wall are very helpful. But i dont see anything with information on the venting capacity of an open 1 1/4 inch or larger open tap. This is for a 1920's NYC 90 unit apt building with large diameter and very long overhead steam mains with 1 1/4 tap from Tee at end of each run.
    thanks
  • scott22nyc
    scott22nyc Member Posts: 7
    I ask on this discussion because i dont know how many Barnes and Jones big mouths to use at each location to maximize venting.
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    edited May 2017
    You should measure the length of the piping in various diameters, which feed all the radiators, and post it here. This is the volume of air which must be allowed to escape without any resistance so the steam may rise into all the radiators. I have the equivalent of 12 Big Mouth vents for 55 radiators on a 1,050,000 BTU boiler, so you may need a few more. The air should vent at a couple of ounces pressure as shown on a low pressure gauge, (Valworx 0-3 psi.).
    How many stories are in the building? What is your location?--NBC
  • Fred
    Fred Member Posts: 8,542

    You should measure the length of the piping in various diameters, which feed all the radiators, and post it here. This is the volume of air which must be allowed to escape without any resistance so the steam may rise into all the radiators. I have the equivalent of 12 Big Mouth vents for 55 radiators on a 105000 BTU boiler, so you may need a few more. The air should vent at a couple of ounces pressure as shown on a low pressure gauge, (Valworx 0-3 psi.).
    How many stories are in the building? What is your location?--NBC

    @nicholas bonham-carter , I'm assuming you left a 0 off of your boiler BTU number. 55 rads a 105K boiler probably won't work.
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    Thanks Fred! Quite right it's one million, fifty thousand.
    Now i don't see my Edit button-has it moved?
    Once again, I will say that the price tag of main vents is an investment, and not an expense. The yield in reduced fuel consumption can be as high as 30%!--NBC
  • Fred
    Fred Member Posts: 8,542

    Thanks Fred! Quite right it's one million, fifty thousand.
    Now i don't see my Edit button-has it moved?
    Once again, I will say that the price tag of main vents is an investment, and not an expense. The yield in reduced fuel consumption can be as high as 30%!--NBC

    My edit button is in the same location (little cog in the upper right corner, directly across from your name at the top of your post).
  • scott22nyc
    scott22nyc Member Posts: 7
    But if i can put 3 big mouths (10.8 cfm total potential) on a 3/4 tap and have more venting that the tap can actually produce and i can have a 1 inch tap with 3 big mouths which cannot keep up with the potential venting of a wide open 1 inch tap (but not worth installing a 4th), then how much venting can i get from a wide open 1 1/4 inch tap? i just need the next size up from 1 inch tap venting capacity so i know how many big mouths to install on the 1 1/4 inch taps. BTW; i have a 75,000 sq ft apt building with 250+ huge free standing radiators.
  • Fred
    Fred Member Posts: 8,542
    There are any number of guys here that can tell you the formula to calculate the air flow capacity of a pipe. The formula is on here somewhere but I can't find it. @Jamie Hall can tell you.
  • scott22nyc
    scott22nyc Member Posts: 7
    Would anyone else know this information? I havent received a response. How many bigmouth vents for a 1 1/4 inch tap location? how many CFM can pass in a 1 1/4.
    thanks
  • ChrisJ
    ChrisJ Member Posts: 16,231

    Would anyone else know this information? I havent received a response. How many bigmouth vents for a 1 1/4 inch tap location? how many CFM can pass in a 1 1/4.
    thanks

    I don't think anyone has tested it, but I'd say there's a good chance 1 1/4" handles 2.5 to 3 times what a 3/4" tap will. I can't remember the CFM rating of a 3/4" tap but I know it's out there.

    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Fred
    Fred Member Posts: 8,542
    I believe a 1 1/4" pipe will vent at about 14 CFM at 3 ounces of pressure so it would take about 4 Bigmouths (3.6CFM ea @ 3 Ounces of pressure). The real issue, however is how long and what diameter main are you trying to vent? It's the amount of air in the main that needs to be vented. If it's a small main, adding all that venting isn't buying you anything. A big main may be a different story.
  • Koan
    Koan Member Posts: 439
    A 3/4 pipe will vent 9.5 CFM @ 3 oz (citing Gerry Gill). The internal area is 0.53 sq in. A 1&1/4 pipe has an area of 1.50 sq in. I would assume a 1&1/4 open pipe would vent 9.5 CFM x 1.50/0.53 = 26.9 CFM at 3 oz.
    ChrisJ
  • Koan
    Koan Member Posts: 439
    This would correlate to 8 big mouths (7.5 rounding up) at 3.6 CFM ea.
    ChrisJ
  • ChrisJ
    ChrisJ Member Posts: 16,231
    Koan said:

    A 3/4 pipe will vent 9.5 CFM @ 3 oz (citing Gerry Gill). The internal area is 0.53 sq in. A 1&1/4 pipe has an area of 1.50 sq in. I would assume a 1&1/4 open pipe would vent 9.5 CFM x 1.50/0.53 = 26.9 CFM at 3 oz.

    It's amazing how much volume goes up as pipes get bigger isn't it?

    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    It's all to do with the square of the radius.--NBC
    Canucker
  • Fred
    Fred Member Posts: 8,542
    Koan said:

    A 3/4 pipe will vent 9.5 CFM @ 3 oz (citing Gerry Gill). The internal area is 0.53 sq in. A 1&1/4 pipe has an area of 1.50 sq in. I would assume a 1&1/4 open pipe would vent 9.5 CFM x 1.50/0.53 = 26.9 CFM at 3 oz.

    @Koan , according to Gerry Gill, a 1" pipe will vent 11CFM at 3 oz of pressure. I don't thint another 1/4" will add an additional 16 CFM ??? I still think 4 Bigmouths, maybe 5 would be the limit.
  • ChrisJ
    ChrisJ Member Posts: 16,231
    Fred said:

    Koan said:

    A 3/4 pipe will vent 9.5 CFM @ 3 oz (citing Gerry Gill). The internal area is 0.53 sq in. A 1&1/4 pipe has an area of 1.50 sq in. I would assume a 1&1/4 open pipe would vent 9.5 CFM x 1.50/0.53 = 26.9 CFM at 3 oz.

    @Koan , according to Gerry Gill, a 1" pipe will vent 11CFM at 3 oz of pressure. I don't thint another 1/4" will add an additional 16 CFM ??? I still think 4 Bigmouths, maybe 5 would be the limit.

    a 1.25" pipe will vent 56% more than a 1".

    What's odd is this suggests a 1" pipe can pass 78% more than a 3/4" pipe, but Gerry Gill's chart shows little increase between the two, 9.5 vs 11? A 1" should pass 17 CFM according to the math.

    Maybe real world just doesn't work that way?
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Koan
    Koan Member Posts: 439
    I agree that my math and the real world must differ. One would think, as I did, that increasing with area as the square of the radius would apply, but Mr. Gill's reasearch shows different results. I was increasing solely on the area. I defer to Gerry Gill's empirical evidence. I assume the friction of the air flow against the larger surface area may be a factor. Using a linear extrapolation, adding a quarter inch in diameter adds 1.5 CFM. This would indicate a 1&1/4 open pipe would vent at a minimum 12.5 CFM @ 3oz. This would indicate at least 4 big mouth vents. That would cover up to 3.6 x4 or 14.4 CFM. I would say this is our starting point. Ironically this is what @Fred originally suggested. The math using area says 8 vents, the reasearch extrapolates linearly to 4 vents. It is actually 7.5 and 3.5. The average is 5.5. I would start at 5 or 6 vents. 5 vents would be 18CFM and cover the increase from 1" at 11 CFM. My best guess is 5, I would use 6.