Any of our hydronic experts have a method of determining a bound or burnt out circulator by using a multimeter or amprobe?
0
Comments
-
Here's a start -
As with troubleshooting most loads, i.e. pumps or motors, check for the rated voltage at the load. If there's voltage, there should be amperage. Unless, the internal circuit of the load has been opened either through an open internal overload or an open winding.Steve Minnich0 -
If you can't turn the impeller easily it's bound up. If it turns easily set your multimeter to ohms (with the power shut off and the motor wires disconnected) and read between the two wires you should read a resistance.
Then ohm each motor wire separately to a good ground (cold water pipe) you should read 0 ohms. When it is pumping the amps should be at or below the nameplate amperage0 -
How about each motor wire showing nearly infinity ohms to ground. That is each wire should be completely insulated from ground....zero conductance to ground......I know what you mean Ed.....I have said this also.0
-
Hahaha steve....if I could understand your reply I wouldn't have had to posted to begin with....was hoping for some basic blue collar help...thanks for taking time to reply though...happy thanksgiving0
-
Two quick tests.
If you have a ball valve in the hydronic circuit, with all zones running, quickly close the ball valve. If you hear a tapering HIISSssss, you have flow. If you hear nothing, you most probably have little to no flow.
Other check is performed with the burner off, and the pump on. Hold a lit torch against the pipe for 5 seconds. Wait 5 seconds, then carefully touch the pipe. If it's hot, there is no flow. If its cool, there is flow.
When using an amprobe to check motors, one has to be careful. A locked rotor on a 007 draws the same amperage as one that is running correctly...
METhere was an error rendering this rich post.
2 -
Starting with electrical tests is not the way go. There are many mechanical issues that can mess up a pump that has good electrical readings. i.e. clogged ports, impeller issues, etc. Pull the pump visually check it, turn shaft and run it briefly.0
-
-
Typically when out on a troubleshooting mission I will touch one end a long screwdriver to various locations on the circ and other to my ear - makes a great stethoscope! If the circ is seized or the bearings are worn out you'll hear it. You can also "hear" flow. But be careful with mechanically sealed circs/pumps as there may be exposed rotating components that you do not want to get clothing, hair or neck ties caught in...
Mark's diagnostics work well too. BTW, infrared heat guns are much cheaper than in the old days if you don't want to touch the pipe.0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements