We were called in to troubleshoot this little steam system that banged constantly. It is in a 2-bedroom rowhouse that was built about 1925. All the ones we've been in on this row have the same system, where the two back radiators are fed with a very short 1-1/4" counterflow main. and the bathroom and two front radiators are fed from a longer 1-1/2" parallel-flow main.
The boiler is a Columbia CEG-075E, which is a re-branded Utica PEG. It is the smallest PEG/CEG made, at 196 square feet.
We found the typical piping mess- copper, wrongly configured, messed up Hartford Loop, etc.
The boiler is a Columbia CEG-075E, which is a re-branded Utica PEG. It is the smallest PEG/CEG made, at 196 square feet.
We found the typical piping mess- copper, wrongly configured, messed up Hartford Loop, etc.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting
0
Comments
-
With all the spectacularly-done repipes we've seen recently, this one probably seems anticlimactic. But with such a small boiler, a 2-inch header is really all you need.
The owner wanted more clearance so we rotated the entire boiler, placing the controls and skim port where they are most accessible.
We connected the counterflow main to the header at a 45° angle, so the very small amount of returning condensate from two 25-square-foot rads would not shower the steam in the header. We also re-oriented the Hydrolevel VXT water feeder so you can actually see the display.
A Gorton #6 vent on the long main balanced the system perfectly.
When we started it up, it was eerily quiet. No banging!
We flushed and skimmed the boiler but it will probably need more. We'll be back to handle that.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting6 -
It's not 3", AND there's no drop header?! How dare you! Mission accomplished as always @steamhead, good job.0
-
Nice work! Allow me to rotate your photos if I may:
New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
Thanks, @RI_SteamWorks- still haven't figured out why the pics from my camera do that. The first set came from my phone, and they displayed correctly..............All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Oh how I'd love to try two of those, or two EG30's out on my system.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Nice work! What was the total EDR of the house?0
-
Very nice.0
-
Nice save, Frank.
- DF0 -
125 square feet EDR or so.RomanGK_26986764589 said:Nice work! What was the total EDR of the house?
Thanks, all.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
-
Looking good, and that is one small steamer.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements