Repiping a Small Columbia Steamer

Options
Steamhead
Steamhead Member Posts: 16,842
edited November 2016 in Strictly Steam
We were called in to troubleshoot this little steam system that banged constantly. It is in a 2-bedroom rowhouse that was built about 1925. All the ones we've been in on this row have the same system, where the two back radiators are fed with a very short 1-1/4" counterflow main. and the bathroom and two front radiators are fed from a longer 1-1/2" parallel-flow main.

The boiler is a Columbia CEG-075E, which is a re-branded Utica PEG. It is the smallest PEG/CEG made, at 196 square feet.

We found the typical piping mess- copper, wrongly configured, messed up Hartford Loop, etc.




All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting

Comments

  • Danny Scully
    Danny Scully Member Posts: 1,425
    Options
    It's not 3", AND there's no drop header?! How dare you! :lol: Mission accomplished as always @steamhead, good job.
  • New England SteamWorks
    Options
    Nice work! Allow me to rotate your photos if I may:




    New England SteamWorks
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com
  • Steamhead
    Steamhead Member Posts: 16,842
    Options
    Thanks, @RI_SteamWorks- still haven't figured out why the pics from my camera do that. The first set came from my phone, and they displayed correctly..............
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • ChrisJ
    ChrisJ Member Posts: 15,696
    Options
    Oh how I'd love to try two of those, or two EG30's out on my system.



    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • RomanGK_26986764589
    Options
    Nice work! What was the total EDR of the house?
  • Fred
    Fred Member Posts: 8,542
    Options
    Very nice.
  • Dan Foley
    Dan Foley Member Posts: 1,258
    Options
    Nice save, Frank.

    - DF
  • Steamhead
    Steamhead Member Posts: 16,842
    Options

    Nice work! What was the total EDR of the house?

    125 square feet EDR or so.

    Thanks, all.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • EzzyT
    EzzyT Member Posts: 1,295
    Options
    Beautiful job as always Frank
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • Dave0176
    Dave0176 Member Posts: 1,177
    Options
    Looking good, and that is one small steamer.
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......