I converted from Oil to heat last year and the plumber installed a Williamson GSA‑250 Complete 250,000 BTU Steam Boiler. It seems like it is way oversized. My was built in the 1920's and is 2,500 square feet with poor insulation. I plan on insulating my house and am wondering if this boiler is oversized and if it is worth replacing? Also being that the boiler probably runs for less time because the home heats up quicker, would I really be saving money by replacing it?

Comments

  • homeowner_7homeowner_7 Posts: 6Member
    Sorry, just to clarify I converted from Oil to Gas.
  • kcoppkcopp Posts: 3,355Member
    Have you or did he measure out the radiators?
  • homeowner_7homeowner_7 Posts: 6Member
    No, he did not.
  • homeowner_7homeowner_7 Posts: 6Member
    They are cast iron radiators.
  • homeowner said:

    No, he did not.

    Oh boy. Wondering now what else wasn't done. It would be great if you could post pictures of the boiler and all it's piping, your main vents, and some of your radiators.

    The radiators need to be measured to see where we are at. Measure the height of each radiator, then count how many columns or tubes deep each one is, then count how many sections long each one is. With the pics we'll help you figure it out.


    New England SteamWorks
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com
  • JohnNYJohnNY Posts: 2,364Member
    homeowner said:

    being that the boiler probably runs for less time because the home heats up quicker, would I really be saving money by replacing it?

    Consider the efficiency curve of a steam boiler. It is possible to define efficiency by *the amount of fuel being burned which directly results in the temperature gain of a room*.
    That being the case, steam boilers run at 0% efficiency (by that one particular definition, don't everyone get nervous) during every start up of a heating cycle. There is a point in nearly every cycle where the burner is running but steam is not yet being produced. The next part of the cycle produces steam and then pressure and steam then starts to move toward the emitters (radiators). Then we can consider efficiency.
    An oversized boiler does run shorter cycles but that means it spends more time in that flat efficiency zone every hour. I know it seems counterintuitive that a longer cycle is less efficient but the farther the cycle gets away from its start-up portion, the better it is for the whole universe.
    And when the boiler reaches its operating pressure and the burner shuts off, the boiler begins to cool through the chimney and jacket. That's money lost. There is no substitute for proper sizing when it comes to residential steam boilers.
    Someone needs to perform an EDR survey of your system to see what size and output your boiler ought to be.
    For installations, troubleshooting, and private consulting services, find John "JohnNY" Cataneo here at :
    "72°F Mechanical, LLC"
    Or email John at [email protected]
    John is the Boilers and Hydronic Heating Systems Course Instructor at NYC's Mechanics Institute, a professional Master Plumber, licensed by The Department of Buildings of The City of New York, and works extensively in NYC while consulting for clients in and out of state.
    John also oversees mechanical installations and maintenance for metro-area clients with his family's company, Gateway Plumbing and Heating along with his brother/business partner.
  • KC_JonesKC_Jones Posts: 4,192Member
    To the OP if I was a betting man I'd guess you are massively oversized, but we need the EDR calcs to know for sure. It's the only way it can be sized correctly. If your contractor did not do that simple step and just sized off the existing boiler they most likely got it wrong. Pictures of the installation would be good as well too see if they did anything else wrong.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    https://www.facebook.com/media/set/?set=a.10202744301871904.1073741828.1330391881&type=1&l=c34ad6ee78
  • adambnycadambnyc Posts: 260Member
    Same situation.I just had one of the pros on here run me a two stage gas valve which downfires my oversized boiler. If your not gonna rip and replace, I'd suggest doing that.
  • homeowner_7homeowner_7 Posts: 6Member
    Thanks. How much does something like that usually cost?
  • neilcneilc Posts: 722Member
    The EDR calc is practically free,
    yet the most expensive mistake to make,
    your time counting, measuring, and posting back here.

    Then the pros wil ask a question or 2 more and tell you what size boiler you should be at.

    Somewhere else it is written that cost will not be discussed here,
    The stepped burner may or may not make sense for you,
    again, you need the EDR calc.

    and we're all still gonna wanna to see the boiler and the connected piping
  • STEAM DOCTORSTEAM DOCTOR Posts: 924Member
    edited October 2016
    1. Boiler piping leaves what to be desired.
    2. Boiler was obviously not skimmed.
    3. Backflo is on wrong side of feeder
    Installer was obviously not a steam pro. You would be well advised to get a real steam Pro on board
  • neilcneilc Posts: 722Member
    edited October 2016
    ok,
    piping isn't right as above,

    now a pic of each radiator and its height, width, depth,
    we'll count columns in the pics
  • adambnycadambnyc Posts: 260Member
    I would need the pros to comment, but it sorta looks like you have dual stage setup already, unless I'm looking at an aquastat and a pressuretrol. Not sure why you would have an aquastat for a steam boiler without a hot water loop.

    Also not sure why you would have two "pressuretrol" if you didn't have a dual stage setup. Normally in a dual stage one would be a vaporstat. I don't see that.
  • STEAM DOCTORSTEAM DOCTOR Posts: 924Member
    2nd pressurtrol is a manual reset. Extra safety
  • ratioratio Posts: 2,105Member
    Pressuretrol & manual reset limit, but no piggy tail to protect them.
  • FredFred Posts: 8,062Member
    Wouldn't take too much to fix the piping by dropping that tee'd main into the header and add a skim port (in the lkocation where that fiberglass insulation is showing, next to your sight glass). We do need to understand the total EDR of all the attached radiators to determine how much over-sized the boiler may be and if a two stage gas valve might help. Also, a picture of the vents on the Mains and/or the returns would help determine if main venting is adequate.
  • SteamheadSteamhead Posts: 13,288Member
    edited October 2016
    Look at the piping again. Can't swear to it, but it looks like 3-inch or at least 2-1/2-inch coming out of the boiler and all the way to the end of the header. And the large riser going up from the header to the reducing tee will provide enough steam for both mains.

    As long as the header is 24" above the boiler's highest possible waterline, if I'm right it should work OK. I've certainly seen worse!

    There should be a separate pigtail for each pressure control, so if one clogs the other control will still work.
    All Steamed Up, Inc.
    "Reducing our country's energy consumption, one system at a time"
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.
    https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
  • JohnNYJohnNY Posts: 2,364Member
    That's a mess. What's with all the dust on every horizontal surface? I can just imagine what's happening inside those burner tubes. That boiler needs to be repiped to some degree, pigtails added, cleaned, and made to work safely. If it resides in an area where airborne dust is often present then consider creating a boiler room to enclose the unit and bring in clean combustion air from outside.
    For installations, troubleshooting, and private consulting services, find John "JohnNY" Cataneo here at :
    "72°F Mechanical, LLC"
    Or email John at [email protected]
    John is the Boilers and Hydronic Heating Systems Course Instructor at NYC's Mechanics Institute, a professional Master Plumber, licensed by The Department of Buildings of The City of New York, and works extensively in NYC while consulting for clients in and out of state.
    John also oversees mechanical installations and maintenance for metro-area clients with his family's company, Gateway Plumbing and Heating along with his brother/business partner.
  • Dave0176Dave0176 Posts: 1,075Member
    It is pretty disastrous, however as @steamhead said I think the header is 3" which is the minimum spec Weil McLain recommends, but the system risers need to be separated and both come off the header separately. Also the reeeaaal looong Hartford loop is wrong, it should be on a close nipple.
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......