Oversized Boiler
homeowner_7
Member Posts: 6
in Gas Heating
I converted from Oil to heat last year and the plumber installed a Williamson GSA‑250 Complete 250,000 BTU Steam Boiler. It seems like it is way oversized. My was built in the 1920's and is 2,500 square feet with poor insulation. I plan on insulating my house and am wondering if this boiler is oversized and if it is worth replacing? Also being that the boiler probably runs for less time because the home heats up quicker, would I really be saving money by replacing it?
0
Comments
-
Sorry, just to clarify I converted from Oil to Gas.0
-
Have you or did he measure out the radiators?0
-
No, he did not.0
-
They are cast iron radiators.0
-
Oh boy. Wondering now what else wasn't done. It would be great if you could post pictures of the boiler and all it's piping, your main vents, and some of your radiators.homeowner said:No, he did not.
The radiators need to be measured to see where we are at. Measure the height of each radiator, then count how many columns or tubes deep each one is, then count how many sections long each one is. With the pics we'll help you figure it out.
New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
Consider the efficiency curve of a steam boiler. It is possible to define efficiency by *the amount of fuel being burned which directly results in the temperature gain of a room*.homeowner said:being that the boiler probably runs for less time because the home heats up quicker, would I really be saving money by replacing it?
That being the case, steam boilers run at 0% efficiency (by that one particular definition, don't everyone get nervous) during every start up of a heating cycle. There is a point in nearly every cycle where the burner is running but steam is not yet being produced. The next part of the cycle produces steam and then pressure and steam then starts to move toward the emitters (radiators). Then we can consider efficiency.
An oversized boiler does run shorter cycles but that means it spends more time in that flat efficiency zone every hour. I know it seems counterintuitive that a longer cycle is less efficient but the farther the cycle gets away from its start-up portion, the better it is for the whole universe.
And when the boiler reaches its operating pressure and the burner shuts off, the boiler begins to cool through the chimney and jacket. That's money lost. There is no substitute for proper sizing when it comes to residential steam boilers.
Someone needs to perform an EDR survey of your system to see what size and output your boiler ought to be.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes1 -
To the OP if I was a betting man I'd guess you are massively oversized, but we need the EDR calcs to know for sure. It's the only way it can be sized correctly. If your contractor did not do that simple step and just sized off the existing boiler they most likely got it wrong. Pictures of the installation would be good as well too see if they did anything else wrong.0
-
Same situation.I just had one of the pros on here run me a two stage gas valve which downfires my oversized boiler. If your not gonna rip and replace, I'd suggest doing that.0
-
Thanks. How much does something like that usually cost?0
-
The EDR calc is practically free,
yet the most expensive mistake to make,
your time counting, measuring, and posting back here.
Then the pros wil ask a question or 2 more and tell you what size boiler you should be at.
Somewhere else it is written that cost will not be discussed here,
The stepped burner may or may not make sense for you,
again, you need the EDR calc.
and we're all still gonna wanna to see the boiler and the connected pipingknown to beat dead horses0 -
1. Boiler piping leaves what to be desired.
2. Boiler was obviously not skimmed.
3. Backflo is on wrong side of feeder
Installer was obviously not a steam pro. You would be well advised to get a real steam Pro on board0 -
ok,
piping isn't right as above,
now a pic of each radiator and its height, width, depth,
we'll count columns in the picsknown to beat dead horses0 -
I would need the pros to comment, but it sorta looks like you have dual stage setup already, unless I'm looking at an aquastat and a pressuretrol. Not sure why you would have an aquastat for a steam boiler without a hot water loop.
Also not sure why you would have two "pressuretrol" if you didn't have a dual stage setup. Normally in a dual stage one would be a vaporstat. I don't see that.0 -
2nd pressurtrol is a manual reset. Extra safety0
-
Pressuretrol & manual reset limit, but no piggy tail to protect them.0
-
Wouldn't take too much to fix the piping by dropping that tee'd main into the header and add a skim port (in the lkocation where that fiberglass insulation is showing, next to your sight glass). We do need to understand the total EDR of all the attached radiators to determine how much over-sized the boiler may be and if a two stage gas valve might help. Also, a picture of the vents on the Mains and/or the returns would help determine if main venting is adequate.0
-
Look at the piping again. Can't swear to it, but it looks like 3-inch or at least 2-1/2-inch coming out of the boiler and all the way to the end of the header. And the large riser going up from the header to the reducing tee will provide enough steam for both mains.
As long as the header is 24" above the boiler's highest possible waterline, if I'm right it should work OK. I've certainly seen worse!
There should be a separate pigtail for each pressure control, so if one clogs the other control will still work.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
That's a mess. What's with all the dust on every horizontal surface? I can just imagine what's happening inside those burner tubes. That boiler needs to be repiped to some degree, pigtails added, cleaned, and made to work safely. If it resides in an area where airborne dust is often present then consider creating a boiler room to enclose the unit and bring in clean combustion air from outside.
Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
It is pretty disastrous, however as @steamhead said I think the header is 3" which is the minimum spec Weil McLain recommends, but the system risers need to be separated and both come off the header separately. Also the reeeaaal looong Hartford loop is wrong, it should be on a close nipple.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements