Another repipe and stage firing set up
The boiler is way over sized so the stage firing is a must. We also installed a Fan in Can for combustion make up air. Upgraded the main venting too. Just have to go back to do combustion analysis after the new chimney liner is installed.
Before and after pictures.
Comments
-
niceeee work @EzzyT as always....by the way thanks for all your help.... and how are those vaporstats working out for you .....i had one so far this year out of 8 installations this year faulty ...supplyhouse.com sent me a new one right away......whats that
EG-55?ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Awesome as usual. Why the #67?0
-
0
-
Ahh didn't realize it was commercial.0
-
It's not commercial plus I prefer float type lwco rather then the probe0
-
Judging from the draft hood I'll say EG-50
Very nice job Ezz.......DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
Where is that code? I'd prefer it if I was the one testing it0
-
Correct @Dave0176 and thanks.
Code in NYC0 -
code in nyc requires 2 lwco's .....he is correct.....one electronic....one float type.....one must be manual reset.....we dont see them much in resi jobs because nothing is filed in nyc or its a self cert.......if its an apartment building building department is coming and looks for that right awayASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
I'm in Nassau County, where in residential applications it's one or the other. Now I know a little NYC code! , most importantly, good work as always @EzzyT.0
-
-
Nice job as usual. NYC has got to be the king of whacked out code. How many home owners are flushing their 67's ,particularly when they have an electronic probe. Think that you should have water sensors every 12" along the wet returns and at least 2 or 3 under each boiler section. Also two for each radiator shutoff valve and one for each air vent. We do need to be protected from dry firin, you know.0
-
I guess that's the motivation for mandating redundancy.STEAM DOCTOR said:Nice job as usual. NYC has got to be the king of whacked out code. How many home owners are flushing their 67's...
Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
The probe I understand. What's the point of the 67? What would cause a prob not to detect a low water condition? Only thing that I could think of is wet sludge hanging from the probe. Any boiler so unmaintained will almost certainly have a plugged 67. I know anything is possible but common sense regulations are great. Only time that I have seen (That I can remember) a probe not pick up a low water condition is one that was not screwed into boiler block. Boiler was tilted and probe was in a nipple and coupling. Nipples always had water in it ,regardless of boiler water situation. Has anyone ever had a probe not detect low water and have a 67 detect the low water? I could be totally off. I am all ears. Been dealing with some ridiculous regulations recently so forgive me for being cranky. Btw, sorry to hijack the thread0
-
Probe type is electronic, has far more that could go wrong than a properly maintained #67 which is nothing more than an X rated looking brass float connected to a simple switch in a cast iron housing.STEAM DOCTOR said:The probe I understand. What's the point of the 67? What would cause a prob not to detect a low water condition? Only thing that I could think of is wet sludge hanging from the probe. Any boiler so unmaintained will almost certainly have a plugged 67. I know anything is possible but common sense regulations are great. Only time that I have seen (That I can remember) a probe not pick up a low water condition is one that was not screwed into boiler block. Boiler was tilted and probe was in a nipple and coupling. Nipples always had water in it ,regardless of boiler water situation. Has anyone ever had a probe not detect low water and have a 67 detect the low water? I could be totally off. I am all ears. Been dealing with some ridiculous regulations recently so forgive me for being cranky. Btw, sorry to hijack the thread
#67 float
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
I am all ears. Don't really know much about electronics. What is reasonably likely to go wrong? Some sort of short circuit in the electronics or wiring. "Well maintained 67"? Don't see many of thouse (in particular if homeowner knows that the 67 is only a backup).Even well maintained 67's build up crud. I am all for extra safety. However, mandated safeties =extra cost and should have some reasonable expectancy of making a difference. Calling all pro's. How many times have you seen a probe lwco not pick up a low water condition?0
-
@STEAM DOCTOR on an average heating season I tend to see about at least a dozen probe type lwco not pick up low water conditions all due to lack of maintenance.1
-
How does a probe type lwco fail wet due to lack of maint? The only one I've ever fooled with stopped sensing water due to mineral deposits from running on roughly 100% makeup water. It was not a pretty sight.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements