Main steam vent

Hi,

I am working on a steam system 100 years old in Kingston NY.
1 pipe system
20 cast iron radiators- present boiler is Burnham natural gas.
Was once coal, then oil now natural gas.
Am presently installing a used Burnham steam boiler 140,000 BTU

No sign of main steam vent, do I need a large vent like this?
Any pipe I cut seams clean, do I need to flush the system?
The valves on the radiators seem to work, is it worth upgrading?

Thank You -Dennis Connors

Comments

  • JohnNY
    JohnNY Member Posts: 3,287
    Find a plugged/capped tee, cut in a tee, or drill and tap to add a proper main vent somewhere about 12" back from the ends of the horizontal steam mains. No 1-pipe system has ever suffered from being vented properly. Air vents get the steam out of the boiler and into the heat emitters. That makes for efficient operation. Always.
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
    New England SteamWorks
  • BobC
    BobC Member Posts: 5,495
    The steam pipes don't need any flushing BUT any returns that have water in them need to be flushed or replaced. Carefully inspect any returns that have water sitting in them because they are rusting from the inside out.

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
    New England SteamWorks
  • dc07736
    dc07736 Member Posts: 15
    Bob,
    Thanks for info,
    Burners were completely clogged.
    Cleaned the burners, removed jets, they looked clean so we reinstalled.
    Original design had no main steam vent,
    do you advise one.

    Thanks
    Dennis Connors
    Kingston ny
  • BobC
    BobC Member Posts: 5,495
    Is this two pipe steam? Any signs of it being and old style vapor system? Some of those vented into the chimney. Take a look around and post pictures of anything that looks odd.

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • Jamie Hall
    Jamie Hall Member Posts: 24,525
    If this really is one pipe steam -- double check that! -- then you do indeed need main vent(s) at the end of any steam mains, more or less as @JohnNY suggested.

    However, if it is two pipe steam or particularly a vapour system (a variety of two pipe steam) then you may not need main vents on the steam mains -- or you may. Go to the ends of the steam mains and check to see if there are crossover traps to the dry returns. If there are, and they are working, you do not really even want vents there. However, what you do want is main vents where the dry return(s) end and turn down to become wet. You want those whether there are crossover traps or not.

    On the valves -- probably no point in messing with them.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • New England SteamWorks
    New England SteamWorks Member Posts: 1,525
    edited October 2016
    The only purpose vents would serve on the mains is to quickly chase the air out so the steam can get to the radiators as quickly as possible. The quicker the steam gets to the radiators the quicker the rooms warm. The quicker the rooms warm the quicker the thermostat is satisfied. The quicker the thermostat is satisfied the shorter the boiler cycle. The shorter the boiler cycle the smaller the fuel bill.

    Other than that...

    Yes. You need them. Big ones. Call @JohnNY. Maybe he'd like a weekend Upstate. Watch the leaves turn...

    New England SteamWorks
    Service, Installation, & Restoration of Steam Heating Systems
    newenglandsteamworks.com
  • gerry gill
    gerry gill Member Posts: 3,078
    I like that description RI
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • dc07736
    dc07736 Member Posts: 15
    System is 1 pipe
    20 cast iron radiators
    All steam vents are missing from radiators -probably taken for junk value.
    Have to buy new ones
    Should I use adjustable or plain vents o the radiators?
    DC - Kingston NY
  • BobC
    BobC Member Posts: 5,495
    If your starting from scratch, guessing what size vents to use on which radiator can get pricey. Adjustable vents let you experiment, DO NOT BUY the Durst brand at Home Depot - they don't adjust anything.

    That leaves you to choose between Hoffman 1A's that can be tricky to adjust and a bit pricey or Maid O Mist 5L's which is a kit with one air vent and 5 different size screw on orifices.

    https://www.amazon.com/s/ref=nb_sb_noss_1?url=search-alias=aps&field-keywords=hoffman+1a

    https://www.amazon.com/OMIST-0220-5L-Angle-Steam-Valve/dp/B003DV3AGE/ref=sr_1_2?ie=UTF8&qid=1476618544&sr=8-2&keywords=maid+o+mist+5l

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • Pumpguy
    Pumpguy Member Posts: 691
    Tunstall also offers adjustable radiator vents. PM me for details.
    Dennis Pataki. Former Service Manager and Heating Pump Product Manager for Nash Engineering Company. Phone: 1-888 853 9963
    Website: www.nashjenningspumps.com

    The first step in solving any problem is TO IDENTIFY THE PROBLEM.
  • Steamhead
    Steamhead Member Posts: 17,314
    20 radiators and only140,000 BTUH? Sure that's enough?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • PMJ
    PMJ Member Posts: 1,266
    The thing about vents is that while they let air out quickly they also let it back in - quickly. The original system didn't let any air back in when it was heating because the fire never went out. This breathing in and out every cycle is an unfortunate consequence of the on/off fire control. Two pipe systems are easy to control not letting the air back in and will run much more quietly and efficiently that way - I have done it for years now.

    On the first cycle air does not have to be vented out quickly because you can't heat the pipes up that quickly - there is plenty of time on that cycle with a small vent. After that most of you need fast venting, but only to get the air back out that you let back in. Seems (is) quite a waste of effort.

    Someone needs to figure out something for you one pipers. You are buying a vent for every rad anyway. There must be way. Air is the enemy. Need to keep it out.







    1926 1000EDR Mouat 2 pipe vapor system,1957 Bryant Boiler 463,000 BTU input, Natural vacuum operation with single solenoid vent, Custom PLC control
    CLamb
  • SWEI
    SWEI Member Posts: 7,356
    Would Hoffman #3's work?
  • dennis53
    dennis53 Member Posts: 58
    Very good luck with Swan Vent-Rite #1. Tool free adjustment, scale tracks well, wide range, tough to plug.
    Dennis