Weird piping
Dave0176
Member Posts: 1,178
Well I came across a weird piped system. And it's dead men installed!! It was originally a coal fired system, converted to oil, then replaced by a monkee to a gas conversion with all the wrong piping, he did use steel piping however.
The problem however I see lies in the original piping, it runs to both ends of the house on a bullhead tee of course. The weird thing is the front run is only 1-1/2 main with three runouts, and they split right at the edge of the house to a first floor radiator and to a second floor radiator. So three runouts for 6 radiators. The rear run is only 1-1/4 with two runouts that split. It's the weirdest I've seen so far. There is only one No.1 main vent on the front run, that's it, and it don't look like it works too well judging from the water stains, lol. The couple just bought the house on foreclosure so there is no way to tell if works ok. The return into the boiler is leaking so it needs replacing, the boiler is unfortunately waaaay oversized so that's another issue 150k compared with about 75k btu load.
Just wondering if I should tell this couple install a new properly sized boiler and run two new mains with the proper amounts of runouts, of course I'd basically be installing a whole new system?
The problem however I see lies in the original piping, it runs to both ends of the house on a bullhead tee of course. The weird thing is the front run is only 1-1/2 main with three runouts, and they split right at the edge of the house to a first floor radiator and to a second floor radiator. So three runouts for 6 radiators. The rear run is only 1-1/4 with two runouts that split. It's the weirdest I've seen so far. There is only one No.1 main vent on the front run, that's it, and it don't look like it works too well judging from the water stains, lol. The couple just bought the house on foreclosure so there is no way to tell if works ok. The return into the boiler is leaking so it needs replacing, the boiler is unfortunately waaaay oversized so that's another issue 150k compared with about 75k btu load.
Just wondering if I should tell this couple install a new properly sized boiler and run two new mains with the proper amounts of runouts, of course I'd basically be installing a whole new system?
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......
0
Comments
-
Is this a counterflow, or a regular one-piper?New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
One pipeDL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
You would need to determine the total EDR on each main. It's possible to use piping that small with small EDR loads. Also, they should be parallel-flow (with a drip to a return at the end) rather than counter-flow.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Yes it's a parallel flow single pipe. EDR for the from run is about 150 the rear is about 50. However the runouts are then too small because both radiators on each runout equil about 50-55 EDR, the runout lengths are about 8' of 1-1/4.Steamhead said:You would need to determine the total EDR on each main. It's possible to use piping that small with small EDR loads. Also, they should be parallel-flow (with a drip to a return at the end) rather than counter-flow.
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
It may have been sized before 2 PSI became the standard. This system may need to be run on the pressuretrol setting up 1 psi with a 1-pound differentialCost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements