You're saying the wet steam would cause the burner to operate for at least 6% longer because the steam contains less energy. Let's use 6% just because it's a number.Hatterasguy said:
You could use specific enthalpy to get an approximation.ChrisJ said:
@Hatterasguy Is any of this usable to you at this link?
http://www.engineeringtoolbox.com/wet-steam-quality-d_426.html
"Steam - produced in a boiler where the heat is supplied to the water and where the steam is in contact with the water surface of the boiler - contains approximately 5% water by mass."
I assume some of that or all of that falls out in the header, in theory?
Dry steam has an energy content of 1151 BTU/lb.
94% dry steam has an energy content of 1082 BTU/lb.
Assuming constant mass from the boiler, the energy output from the 94% steam is reduced by 6%.
I am not confident that enthalpy can be used strictly as the single variable for fuel consumption, however.
There are issues with wet steam traveling to the far ends of the system in a timely fashion and the fact that it will condense to a greater degree on the way (due to the reduced velocity). So, you may need to operate the boiler for an extended period of time independent of the enthalpy difference.
The fuel consumption delta would likely be greater than 6%.
Where did that 6% go?
My point was the boiler will just have to move 6% more wet steam. But I don't see how it can produce 6% less output? Where's that 6% going?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Show him this, courtesy of @Christian GaribaldiSeanBeans said:I talked to someone on the phone at birds all about the bigmouth, he told me it was the ugliest vent he had ever seen lololol but they got good stuff.
Peter Owens
SteamIQ2 -
-
That's enough to put @KC_Jones in his grave!Sailah said:
Show him this, courtesy of @Christian GaribaldiSeanBeans said:I talked to someone on the phone at birds all about the bigmouth, he told me it was the ugliest vent he had ever seen lololol but they got good stuff.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1 -
No no no, that's a whole other can of worms.Hatterasguy said:
If a specific amount of input only produces 94% of the output (based upon a 100% dry steam baseline), the difference can only be combustion efficiency. The 6% goes up the stack.ChrisJ said:
You're saying the wet steam would cause the burner to operate for at least 6% longer because the steam contains less energy. Let's use 6% just because it's a number.Hatterasguy said:
You could use specific enthalpy to get an approximation.ChrisJ said:
@Hatterasguy Is any of this usable to you at this link?
http://www.engineeringtoolbox.com/wet-steam-quality-d_426.html
"Steam - produced in a boiler where the heat is supplied to the water and where the steam is in contact with the water surface of the boiler - contains approximately 5% water by mass."
I assume some of that or all of that falls out in the header, in theory?
Dry steam has an energy content of 1151 BTU/lb.
94% dry steam has an energy content of 1082 BTU/lb.
Assuming constant mass from the boiler, the energy output from the 94% steam is reduced by 6%.
I am not confident that enthalpy can be used strictly as the single variable for fuel consumption, however.
There are issues with wet steam traveling to the far ends of the system in a timely fashion and the fact that it will condense to a greater degree on the way (due to the reduced velocity). So, you may need to operate the boiler for an extended period of time independent of the enthalpy difference.
The fuel consumption delta would likely be greater than 6%.
Where did that 6% go?
My point was the boiler will just have to move 6% more wet steam. But I don't see how it can produce 6% less output? Where's that 6% going?
You would need to know the exact procedure of how the companies actually calculate their magical 82% combustion efficiency. I think we'd be quite surprised at the outcome.
We're comparing a factory spec'ed piped boiler, or perhaps even a bit under to an overpiped boiler as far as efficiency.
If the poorly piped boiler puts out 6% less energy in it's steam, it must be producing 6% more steam, no? If so, where's the efficiency loss?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
The liquid water traveling with the steam causes some of the steam to condense too soon. That's where the loss is.Retired and loving it.0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements