Kick toe heater

347
347 Member Posts: 143
Hello all,
How do you guys normally install a kick toe heater to a 3/4" loop system with piping below the floor.
Monflow tees? . I'd hate to reduce the pipe size to 1/2".
Thanks

Comments

  • kcopp
    kcopp Member Posts: 4,472
    Typical fashion is to install a set of tees in the 3/4" run of the loop.
    You can do this 2 ways.
    Simplest way it to in stall 2- 3/4x 1/2x1/2 tees separated by 12" of 1/2" copper. The branches of these run out to the Kickspace heater.
    The other way is to use a diverter/ mono flow tee on the return and a simple 3/4 x 1/2 tee on the supply.
    It is important to keep the run out to the kickspace heater as short as possible. Don't have 20' of run-out to the heater.
  • ratio
    ratio Member Posts: 3,788
    Is it supplemental heat? It could be piped primary/secondary with a small pump & closely spaced tees, either as an independent zone or a second stage. It would require constant flow though, & adding what is basically a micro zone might need some thought about how it'll impact the system as a whole.
  • Bob Bona_4
    Bob Bona_4 Member Posts: 2,083
    edited June 2016
    3/4 x 1/2 T and 3/4x x1/2 monoflo T. Keep the branch at least pitched up, space them at least the width of the TK. Don't forget a 1/2 baseboard ell with a coin vent, if the TK doesn't have a bleeder installed.
    ZmanGreenGene
  • 347
    347 Member Posts: 143
    Thanks for the replies. That's what I was going to do, just wondering if any one did it different.