Steam heat and hot water

Options
whiteke12
whiteke12 Member Posts: 13
Steam system seems to be cycling like every ten minutes for like 3-5 seconds. I have steam heat off so only steam that would be used is for hot water. Any ideas why?

System is straight steam with no boiler.

Comments

  • whiteke12
    whiteke12 Member Posts: 13
    Options
    And hot water isn't being used as its 300 in the morning...
  • Jamie Hall
    Jamie Hall Member Posts: 23,324
    Options
    Is there an aquastat which is supposed to keep the boiler hot enough to supply the hot water? Oh... you say no boiler? How are you getting any steam without a boiler? District steam?

    If there is an aquastat, check its settings.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • whiteke12
    whiteke12 Member Posts: 13
    Options
    City steam
  • whiteke12
    whiteke12 Member Posts: 13
    Options
    These are two things around the coil...
  • ratio
    ratio Member Posts: 3,627
    Options
    Where do the wires go that come out of the valve, the first picture? Take pictures of where the wires end up at & post them.