Steam replacement with proper size

Dave0176
Dave0176 Member Posts: 1,178
edited February 2016 in Strictly Steam
A while back I showed some pics of a really poorly installed super oversized steam boiler. Well we finally replaced that boiler. Unfortunaty for the homeowner PSE&G either needs to run gas service or there may be an issue with the incoming gas from the street, they were there and confirmed but what ever the case manifold pressure is only around 2.20 so we're no were near firing at full throttle. But the job is done and I feel I did my best.
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

I cannot force people to spend money, I can only suggest how to spend it wisely.......

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,525
    Nice work! Shame about the gas pressure -- but that is one of the little problems with natural gas, isn't it? Nothing you can do about it, though.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Paul S_3
    Paul S_3 Member Posts: 1,274
    Nice job dave....how high are the risers before they turn down into header?
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • Dave0176
    Dave0176 Member Posts: 1,178

    The question that begs:

    How did the super oversized boiler ever run?

    Well I clocked the gas meter and it was only burning 178,000 btu but would run up to pressure pretty quick and short cycle then they complained of hammer spitting air vents etc.... Imagine it ran at the rated 200,000 btu...,,,.
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • Dave0176
    Dave0176 Member Posts: 1,178
    edited February 2016
    Paul S said:

    Nice job dave....how high are the risers before they turn down into header?

    I cut the 2-1/2 pipe 28" then added 6" nipples plus the unions, so probably 39" total and like 45" above the water line. I had plenty of height so I ran them high.
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • Fred
    Fred Member Posts: 8,542
    Looks great, as usual!
  • EzzyT
    EzzyT Member Posts: 1,338
    Beautiful work as always Dave.
    PSEG only guarantees 3"-4" of gas pressure this time of year in area's that are already low pressure
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • Dave0176
    Dave0176 Member Posts: 1,178
    EzzyT said:

    Beautiful work as always Dave.

    PSEG only guarantees 3"-4" of gas pressure this time of year in area's that are already low pressure

    Yep your right that's what the tech told me!!!!
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • Dave0176
    Dave0176 Member Posts: 1,178
    He's running about 3" supply and 2.50" manifold.
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • EzzyT
    EzzyT Member Posts: 1,338
    I've lost count on how many tankless water heaters I've had to rip out and install a regular water heaters or indirect tanks because the companies that installed the tankless's never noticed that gas pressure was in a low pressure area.
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • MikeJC
    MikeJC Member Posts: 8
    So if PSE&G can't get the gas pressure up, is there a solution other than upfiring the boiler?
  • Jamie Hall
    Jamie Hall Member Posts: 24,525
    convert to oil? :)
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • EzzyT
    EzzyT Member Posts: 1,338
    Or to propane
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • Dave0176
    Dave0176 Member Posts: 1,178
    Few more pics Mike sent me. He also told me PSE&G is there looking in to the low gas pressure, they think it might be the line from the street to the house.
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • JUGHNE
    JUGHNE Member Posts: 11,254
    Looks great, what is sitting by the wash tub..temp electric heater?
  • BobC
    BobC Member Posts: 5,495
    In 2014 i noticed my boiler was making a different sound and the gas hot water heater didn't sound right either. A few other houses on the street had had problems with the gas pipes coming in from the street. On a hunch I put a manometer on the gas line and found the input to the boiler was dropping by 50% and bouncing all over the place when the boiler came on.

    I called the gas company and they found the problem was with the 80 year old gas main coming into the house, it was partly blocked with corrosion. They reamed the pipe and inserted a 1-1/4" plastic pipe into the old pipe and the pressure came right up where it belonged.

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • Dave0176
    Dave0176 Member Posts: 1,178
    Update, PSE&G came dug up the street checked the connections and upped the pressure to 4" so now the boiler is running much better.
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • Chris_L
    Chris_L Member Posts: 336
    @Dave, Can you explain to this homeowner the piping of the risers from the header to the mains?

    Is there any particular reason for running the risers vertically from the header, instead of at an angle from the headers to the mains to align the top of the risers with the mains (by rotating the Tees)? You could eliminate the el and nipple at the top of each riser that way, and it doesn't look like the risers would be too far off from vertical.

    Alternatively, if you wanted to keep the risers vertical, could you have put the header directly beneath the mains? Thanks.
  • Dave0176
    Dave0176 Member Posts: 1,178
    Chris_L said:

    @Dave, Can you explain to this homeowner the piping of the risers from the header to the mains?

    Is there any particular reason for running the risers vertically from the header, instead of at an angle from the headers to the mains to align the top of the risers with the mains (by rotating the Tees)? You could eliminate the el and nipple at the top of each riser that way, and it doesn't look like the risers would be too far off from vertical.

    Alternatively, if you wanted to keep the risers vertical, could you have put the header directly beneath the mains? Thanks.

    The reason for the two elbows at the top of the main risers is to create a swing joint so I can pitch the mains away from the boiler.
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • Chris_L
    Chris_L Member Posts: 336
    Thanks Dave. I'll remember this if I ever get the bullheaded Tees on the mains of my two boilers fixed.


  • The Steam Whisperer
    The Steam Whisperer Member Posts: 1,247
    You could just upsize the capacity of the gas valve, that will give you more capacity at a lower pressure drop.