Lock out
Comments
-
-
Paul
I didn't see your comment with the analyzer until after I cut the 90.
where is the best place to put the probe on the analyzer?
I can do it anytime i get an answer0 -
Carl
!st, i don't feel bad, I'm human, I make mistakes. Hopefully the mistakes I make, don't cost me alot of money to fix.
if you can give me an idea on where I should be checking around, I'd appreciate that
I'll get the analyzer out, and read over the instructions again.
To be honest, I am so happy I did the job, and I'm proud of it.
No way would I have done it, without finding this site
again
Thanks all
Mark0 -
Mark....Follow the instructions in the manual. Look in the "Start Up" section.0
-
I just did a basic CO/combustion test
co2 - 9.0
co - 6.0
02 - 5.0
x - 31.4
no - n/f
p - 0
tf - o0 -
here are the numbers i got for that test. are any other test suggested?
differential?
high resolution
high co
heat exchange test?
aux test?
0 -
I have the numbers from the test I did, but I don't know what they mean.
how do the numbers look?
should i be doing something, if the numbers are not normal. and what inspection should i do?
thanks
Mark0 -
Your combustion numbers are within range.
If everything looks and sounds normal I would not take it apart.
If you want to you could visually inspect the fan and venturi. You would have to disassemble a few things..."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
I did the test over again
o2 - 5.1
co - 720 -
p - .01
tf - oc
co2 9.0
no n/f
efc -0
x - 32.2
should i do any other test?
I f like you say the numbers are within range, you feel I did no harm at this point in time?
if you feel the need for me to check out the fan, I will.
but my eyes do not know what to look for
the boiler seems to sound great and I changed the perameters before the test, no problem getting up to the new numbers, now my DHW does go down in flame, before it reaches target. It was always 100% or nothing
Let it be?
or other suggestion, inspection? or tests0 -
Let it be...."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
again
i want to thank all of you, get thru my 1st service call on my boiler.
Carl, thank you, I'll let it be
Mark0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements