MIL-T-FBP in the manual.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
You lost me Bob with the MIL-T-FBP reference, but I did forget to add that we had our Mascot Ilka on the job, who is present for every MST job:New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
It's an old military engineering acronym -
Make it Like The Flippin Blue Print
Great mascot!
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
No takers?! Long day, -off to bed. More pictures tomorrow when we finish up. For now, there's this:New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
Looks nice, is that the piping kit?
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Looks like you're doing it!RI_SteamWorks said:What would you do?
0 -
I will say it will work fine, but you have way too many parts and fittings. Look up Weil McLain's piping diagram for the next one. It is so simple you won't believe it works.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating2 -
Thanks Charlie. We had quite a debate about which way to go with the piping. Because of the poor performance of the system we replaced, we opted for the header despite it's complexity. More tonight.New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
By using a 3" drop header where you supply the system you eliminate the need for the drips. You would still use both risers from the boiler, just put them into the over sized header.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
Came out real nice. Hammer is all gone now, everything quiet, she purrs like a kitten. Nicely balanced all around (radiators/rooms to each other & and the boiler to the radiation). Wind chill in the teens today. Brought the house up to temp this morning and it only cycled a few times on pressure. Thereafter we never saw more than an ounce or two and she cycled on the thermostat. Owner's thrilled of course after 15 years of aggravation. Back tomorrow to insulate the fittings and do some more skimming and that should be it!New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
Good job! Always amazing how well it works when it's done right.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Is there anything more fun that solving a problem and piping steam at the same time?! Always a little sad when the job is over...New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements