Steam Boiler in Church

Dan Foley
Dan Foley Member Posts: 1,268
We have serviced this 25 year-old W-M LGB-10 steam boiler at this stone church in Cleveland Park for over ten years. Over the years, we have replaced all the traps, radiator valves, F&T traps and main vents in the system. The boiler started to leak between the center sections onto the burners so it was time for replacement.

Welcome

It looks like you're new here. Sign in or register to get started.

Comments

  • Dan Foley
    Dan Foley Member Posts: 1,268
    We went back with a 7-section Crown 24-7 with a Beckett power gas burner (Lo - Hi - Lo off of a Vapor-Stat).

    Brian had the 6" "Bazooka" welded at a local pipe fab shop to make the header piping easier. I prefer the companion flanges to a welded header as the still have some "give" to them.

    We fired this one up last week.

    - DF
    ChrisJSWEI
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,633
    What can I say?
    Retired and loving it.
  • ChrisJ
    ChrisJ Member Posts: 16,612

    What can I say?

    "Awesome".
    ;)

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • ratio
    ratio Member Posts: 3,958
    Very nice! I've got a Peerless 211A-8, about the size of that, that I'm responsible for, but the piping isn't anything near that nice. At least not yet.
  • Steve Minnich
    Steve Minnich Member Posts: 2,868
    You steam heavyweights rock!

    Nice touch with the Dead Men sticker.

    I didn't know "explosible" was a word. Really, I didn't.
    Steve Minnich
  • SWEI
    SWEI Member Posts: 7,348
    Sweet -- and I'll be that two stage firing will really make the system hum.

    Welded header with flanges must have saved a boatload of time & money over screwed six inch.
  • That's a good use for a welded header.
    Any idea of the cost difference over threaded pipe and fittings.
    When I have raised funds for my funeral chapel project, I anticipate using a drop header about that size, with 4x 3 inch risers from 2 boilers, and would think the welded header would be more cost effective.--NBC
  • Jamie Hall
    Jamie Hall Member Posts: 25,950
    Welded headers are wonderful -- the drop header on Cedric is one -- but one caution: make sure that somewhere in the assembly there are enough threaded or flanged joints arranged so that differential expansion doesn't cause a problem. If this is a single riser (Cedric is) it's not a problem. Two or more risers? Problem.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Dan Foley
    Dan Foley Member Posts: 1,268
    Nicholas,

    I did not price out the 6" threaded fittings. The welded header was well less than $1k. The primary savings was in labor.

    - DF
  • Dan Foley
    Dan Foley Member Posts: 1,268
    Jamie,

    Point well taken. I have seen mis-piped headers actually spread the boiler sections apart. In this case, I believe the threaded risers and drop header create a swing joint that will relieve any stress. The companion flanges also provide a little give - more so than a welded connection.

    - DF
  • RobG
    RobG Member Posts: 1,844
    Did the boiler come with the "Dead Men's" sticker or is it an option? ;)
  • KC_Jones
    KC_Jones Member Posts: 5,883
    RobG said:

    Did the boiler come with the "Dead Men's" sticker or is it an option? ;)

    I would love one to put on my boiler....would look good with the flame job. I thought Dan said they weren't available anymore?
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • Steamhead
    Steamhead Member Posts: 17,744
    Beautiful job, Dan. I'm glad to see you posting your installs again!
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    SWEI
  • j a_2
    j a_2 Member Posts: 1,804
    Wow awesome, maybe not all the dead men stayed dead...
    jonny88vaporvac
  • Abracadabra
    Abracadabra Member Posts: 1,949
    Dan, when you install a large header like that, do you feel comfortable leaving it's weight on the risers? Typically I like to use clevis hangers.