Loud banging pipes or radiators
anthony1
Member Posts: 2
How can I solve this problem, my radiators do not have bleeder valves ( cast iron) I changed the air valves ,but no help ,radiators are tilted back towards turn off valve and it's a single pipe system
0
Comments
-
Help0
-
Everything needs pitched to keep the condensate flowing back to the boiler. The radiator needs pitch to the inlet. The pipe feeding the radiator needs pitch towards the main in the basement. The mains need pitch towards the end (parallel flow) or towards the feed or boiler end (counterflow). Also all pipes need to be straight, if anything is sagging it can cause banging from holding water. Do you have good piping at the boiler? Bad piping can throw excess water into the system and contribute to the problem. I would start by going through all the piping with a level and make sure it's all pitched the correct direction. Post some pictures of the boiler piping and system piping if you need help identifying which type of system as well as which way the pitch should be.0
-
Post some pictures of your boiler, and the piping above it.
Bad piping and excessive pressure above 1.5 psi. can throw lots of water up into the pipes, which can cause water hammer, especially if there are pitch issues..--NBC0 -
Also make sure that your "turn off valves" are fully open. If you need to turn off a radiator, do it by closing the vent -- not by closing the valve.
As has been said, pipe pitch is critical. Go through it, every single foot.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements