Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Co ppm limit for combustion tes
Hvac tech_2
Member Posts: 21
What is the max co ppm limit up the flue and we're is it documented. I always go for 0 to 150 ppm in both residential and commercial but looking for a documented code limit.
0
Comments
-
400 ppm as per the EPA, but I wouldn't want to go that high. There's also ambient maximum levels/hours exposure. You'll have to google it, but it is on their site.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
The ANSI Standard is 400 PPM allowable in a flue sample. We however strive to get 100 PPM or less. A lot of new Mod/Cons give a number they want for their equipment. Contact me at gastc@cox.net and I will share some information with you.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 912 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements