Rate my install!
No drip leg (sediment trap) required at the appliances?
Also, shouldn't the venting on the right rheem heater come in underneath where it joins, instead on on the side?0 -
It appears as though you are marrying old and new. How are you balancing the two? This is nit-picking, but I don't care for the T&P piping. Picture and un-manned firehose. I know... it's an exageration...but.0
I couldn't get my rise coming in under it. This is typical here.Abracadabra said:No drip leg (sediment trap) required at the appliances?
The 1" gas line reduced to 3/4" then down the wall out of view to a manifold and drip leg. Test gauge there.Just a guy running some pipes.0 -
Ball valve on each return at connection to iron pipe. If one side is favored I can reduce that side. Wasn't before.Paul48 said:It appears as though you are marrying old and new. How are you balancing the two? This is nit-picking, but I don't care for the T&P piping. Picture and un-manned firehose. I know... it's an exageration...but.
No floor drain. I agree. But, we don't use a CW fill, just reserves in expansion tank so limited flood.Just a guy running some pipes.0 -
If you look at the tag on the boiler relief valve it shows that it must be in a vertical position, not on its side. Can be a liability problem if it went off, and or didn't go off. I see this a lot around here. Otherwise, looks great for a cramped work space.
Rick0 -
If that's an old gravity conversion, it can be a challenge balancing the system, all by itself. Generally they require over-pumping to meet the flow requirements of the most remote emitters. Throttling is going to add more of a challenge.0
Oops! I'll read that tag when I get back there. I see them horizontal all the time. Often right in the side of a boiler. Easy to add a 90 if I have space. Or cut it in on top of that first run.rick in Alaska said:If you look at the tag on the boiler relief valve it shows that it must be in a vertical position, not on its side. Can be a liability problem if it went off, and or didn't go off. I see this a lot around here. Otherwise, looks great for a cramped work space.
RickJust a guy running some pipes.0 -
That 26-99 did great before. Hope it pumps the same. I did demo the 3" bull head tee it used to feed. I put the BVs on each side of the returns just to have some control since there's a 2.5" S&R heading off on each direction.Paul48 said:If that's an old gravity conversion, it can be a challenge balancing the system, all by itself. Generally they require over-pumping to meet the flow requirements of the most remote emitters. Throttling is going to add more of a challenge.
What are those capped connections on the top of the boiler? Surely those are air vent or relief valve connections, no?
Are those water heaters in series?
Does your local code allow bushings on gas piping? Mine do not. Not for many years.
You need a check valve on that mixing valve. What you've got there is a cross connection now. A temperature gauge would be nice too. I'll not mention the heat trap.
Expansion tank on its side?
Looks nice and neat.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
Wow. Your codes are way different. The X tank is fine like that here and that's how I've piped every 3-way mix valve. A gauge would be nice. I'll add that. Bushings are totally fine here.JohnNY said:What are those capped connections on the top of the boiler? Surely those are air vent or relief valve connections, no?
That boiler has supply & return connections on top and bottom. Gas too. There's a vent up there factory supplied.Just a guy running some pipes.0 -
We aren't allowed bushings or close nipples or street ells on gas either.
Tidy looking install. Sure it'll work great.0 -
there should be unions between the water heater controls and the shutoff valves. The way it is now if you have to swap out one of the heaters how will you disconnect the gas?0
I prefer parallel piping as apposed to series piping for water heaters. I've seen one heater becoming the lead and it seems to burn out before the secondary. Also flashield CSST should have the metal embedded coating into the termination ends. As was mentioned it becomes a task to swap one out without having to shut down the gas main due to the gas cock location.LANGAN'S PLUMBING & HEATING LLC
Considerate People, Considerate Service, Consider It Done!
732-751-1560
email: langansph@yahoo.com
www.langansplumbing.com1 -
Doh!! First time just using CSST to whip those in. Didn't even catch that!L Thiesen said:there should be unions between the water heater controls and the shutoff valves. The way it is now if you have to swap out one of the heaters how will you disconnect the gas?
Thanks for all the notes fellas. It's all very good to know and even if not code here it all sounds like good practice. Can't believe I missed the gas shut off on WH thing. Oops! I'll bet my inspector would never have said a word. I'll change that on my next trip.Just a guy running some pipes.0
Thanks for posting as this is how we all get better.I really like @4Johnpipe idea of water heating piping.Again different areas different codes so dont beat yourself up to muck.MA and NY are very strict but I would love to see a statewide code held to these standards and also world peace,,,,,,,,,0
- 87K THE MAIN WALL
- 57 Biomass
- 115 Chimneys & Flues
- 5.7K Gas Heating
- 106 Geothermal
- 70 Pipe Deterioration
- 982 Plumbing
- 6.3K Radiant Heating
- 388 Solar
- 15.4K Strictly Steam
- 44 Industry Classes
- 48 Job Opportunities