Pressuretrol Calibration

dabrakeman
dabrakeman Member Posts: 722
Had a question on an earlier thread posted by Fred. Relative to the instructions below what is meant by a 1/32" turn. Is 1/32 of a rotation meant?

Reason: On recoveries my system had been reaching ~3.5psi even though the differential dial was set on one and the cut in at lowest setting (0.5). I made based upon the advise a small adjustment of about a little less than a quarter turn and it seemed to bring the displayed max pressure on recoveries down to just under 3psi. I had an "annual inspection" from my installation company this Wednesday and mentioned the fact that it seems when set as it is it should cutout closer to 1.5psi or 2psi. After cleaning the pigtail the technician ran a cycle and as the pressure was rising past 2psi he adjusted the screw until it shut the burners off. I guess he turned it a good 1-1.5 rotations clockwise (I figured he knewe what he was doing). I didn't witness any issues the next and the house heated fine. Friday evening the house starts getting cold and I go down and see the boiler off even though the stat is calling for heat and everything is getting power. Why the issue didn't arise immediately the morning after the adjustment I don't know but bottom line it appears the screw was way over adjusted. I think I have it adjusted back better now but given the delay in the issue last time I will wait a few days to make judgment. The reason for this post is simply to get a clarification on the 1/32" instructions in case others try to make this adjustment. So, should be short thread.

From Fred's previous post:

Most of us use a 3PSI gauge from WIKI. The supply link is below. I would first check the Pigtail (looped pipe) the Pressuretrol is mounted to. They often get clogged andd the Pressuretrol can't sense the actual presure. Take it off and clean it out good. If that doesn't bring the Pressuretrol into a reasonable range, following is the procedure to recalibrate it:
Inside the Pressuretrol, right below the micro switch, there is a pivot arm. At the end of that arm you will see a screw pin that is activated by the diaphragm at the bottom of the Pressuretrol. If you look very carefully at that screw pin, you will see it actually has a tiny (I mean tiny) hex head on it. It takes a .050 hex wrench and you can turn it clockwise (Towards the bottom of the Pressuretrol to decrease the Cut-out pressure or counter clockwise to increase the cut-out pressure (which none of us want to do but who knows, your Pressuretrol may be really screwed up!). Turn the power to the unit off first. You may find the first attempt to turn that screw a little bit stubborn (relatively speaking) because it has some Locktite on it but it does turn. Don't turn too much, a fraction of a turn goes a long way towards getting it adjusted where you want it (maybe 1/32 inch turn to start with). You may need to play with it to get it exactly where you want cut out to be.

Comments

  • Fred
    Fred Member Posts: 8,542
    @dabrakeman Yes, turn that screw in very very small increments and test the cut-out each time. A very small amount of turn goes a long, long way, as you have learned. fortunately, the fix is simple. Start turning it back until you get the calibration right.
  • Tezak
    Tezak Member Posts: 26

    @dabrakeman @Fred I’m trying this now and the screw pin is really stuck. I’ve used a soldering iron attempting to melt off the loctite but I can only reach the one side. I’m afraid I’m going to strip it. Any advice?

  • EdTheHeaterMan
    EdTheHeaterMan Member Posts: 10,141
    edited December 2024

    Purchase a new pressure control. Since this thread is from 2015, perhaps you can get lower prices from 2015 from the supply house. Just tell then the Ed the Heater Man said it's OK!

    These prices are way to high!

    Edward Young Retired

    After you make that expensive repair and you still have the same problem, What will you check next?

    Long Beach EdTezak
  • Tezak
    Tezak Member Posts: 26

    That’s plan B. I might hit it with a solvent and some more heat after I put the kids to bed though. Not ready to throw in the towel.

  • dabrakeman
    dabrakeman Member Posts: 722

    @Tezak Sorry didn't see this. Were you successful? Hopefully you have a good fitting jeweler's screwdriver. I didn't have much problem breaking mine loose. If you are resigned already to getting a new pressuretrol I guess you have little to lose giving it a good twist with some local heat. If you do get it loose do some test runs after each incremental change to verify not only cutout but also cut in. I got mine stabilized just over 1.5psi cutout. Right at 1.5psi cutout it wouldn't cut back in with the dial right at 1.

  • Tezak
    Tezak Member Posts: 26

    @dabrakeman i was not able to break it loose with the hex key but I cleaned the pigtail which was ridiculously clogged. Should have been my first step, I know. The pressuretrol works now but I don’t think it’s accurate. I’m installing a new brass pigtail with a low pressure gage soon so I can see exactly what’s happening and then I will reassess. Thanks for the reply!

  • 109A_5
    109A_5 Member Posts: 2,137

    I've seen a post or a video somewhere that someone just bent the tab on the actuator linkage that pushes on the microswitches actuator very slightly. I'd find out what it is actually doing first, now that the pigtail is clear.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
    Tezak
  • Tezak
    Tezak Member Posts: 26

    @109A_5 i know the exact video you’re referring to. I’ve also seen someone turn the tab on the cut-in spring inside the body of the pressuretrol so it could go lower than the slot allows.

    For now though I’m going to do as @Jamie Hall is suggesting. I have the new pigtail assembly and low pressure gauge in. I haven’t seen the gauge move at all and we’re at 10F. The only time I’ve seen pressure build and start blowing from air vents and causing drips at radiator unions is when we get temps around 0F or recovering from a deep setback (which I don’t do anymore).

    I’d test it out but I try not to subject my tenants to my experiments more than I have to. Subzero temps in the forecast so I should know soon enough.

  • 109A_5
    109A_5 Member Posts: 2,137

    I've never seen my system go over 2 Inches of Water column (1.16 Oz), you would have to look very closely to see that on your gauge. Pressuretrols are notoriously dysfunctional, I'd want to know it's at least close to working correctly that is is not at a Cut-Out of 4 PSI or more, especially since mine never trips, but I can take it off and blow into it to trip the switch. How many PSI are Human lungs good for ?

    Your radiator unions should not be dripping with pressure.

    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Tezak
    Tezak Member Posts: 26

    Your radiator unions should not be dripping with pressure.

    it’s on my to do list for sure. 99% of the time they’re fine, fortunately.

    I blew as hard as I could into this 5psi gauge and I got 1.5psi.

  • anjgc
    anjgc Member Posts: 11

    I think mine must have a bit more loctite than what you all encountered, eh?

  • dabrakeman
    dabrakeman Member Posts: 722

    Geez! I was always taught Loctite goes on the threads… Do you need to try to adjust? Maybe if you had a mini torch or even a soldering iron you could soften the Loctite enough to get a hex wrench in there or maybe it would even peel off. Would have to be careful.

  • Dan_NJ
    Dan_NJ Member Posts: 267

    That's pretty big blob alright. I think mine just kind of peeled off / gently chipped away with little effort. Way less of it in my case though

  • Long Beach Ed
    Long Beach Ed Member Posts: 1,620
    edited February 22

    Mexico.

    I know we're all grown up men here, but I'll mention this since no one else has: The pressure control is a life saving safety device. Meddling with it, adjusting it or molesting it can cause its failure and a dangerous condition. Boilers can and do explode. Make sure there is a proper pressure relief valve or redundant pressure safety control on any boiler. There, it's said.

    CLamb