Temp does not respond to thermostat
docjone5
Member Posts: 44
I have 6 heat zones and 1 zone no matter what I set the thermostat to is always at 73 to 75 degrees. I have changed the thermostat batteries with no luck and have changed the actual thermostat with one from another zone with no luck either. Any ideas of why this would happen?
0
Comments
-
How about a little bit more description as to what kind of heating system you have? Is it hydronic? If so, are zones controlled by circulators or zone valves?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Check valve not fully closing.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
^
x20 -
So the check valve in the grundfos correct? Are those replaceable? I had one apart looks pretty simple0
-
Are the pipes to that zone staying hot all the time?0
-
Yes pipes are hot seems like all the time0
-
Then Doc Ironman's diagnosis is correct.5