POLARIS WATER HEATER
Tim Potter
Member Posts: 273
I want to be proactive, I want to have a plan for if & when the tank goes. I dont want to be scrambling late at night with my boiler guy discussing a plan.
I just purchased a 14 year old condo with the Polaris (PG1034-100-2nv) 34 gal, 100,000 BTU providing DHW & infloor radiant in GYP.
DHW & heat are separated by a flat plate heat exchanger, has a mixing valve to temper DHW, & 2nd mixing valve to limit water temps in the tubing.
600 sq ft condo, top floor, end unit, 9000' elevation FRASER, CO Design day -20*.
Havent had a chance to do a heat loss yet, (tenant occupy till april), but it can't be much.
006 pump to FPHE
007 pump for the 3 loops,
Thank You for any thoughts & input,
Tim
I just purchased a 14 year old condo with the Polaris (PG1034-100-2nv) 34 gal, 100,000 BTU providing DHW & infloor radiant in GYP.
DHW & heat are separated by a flat plate heat exchanger, has a mixing valve to temper DHW, & 2nd mixing valve to limit water temps in the tubing.
600 sq ft condo, top floor, end unit, 9000' elevation FRASER, CO Design day -20*.
Havent had a chance to do a heat loss yet, (tenant occupy till april), but it can't be much.
006 pump to FPHE
007 pump for the 3 loops,
Thank You for any thoughts & input,
Tim
Winter Park, CO & Arvada, CO
0
Comments
-
A small combi boiler like the Bosch GreenStar.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
I would use an HTP Phoenix , PH100-55 . There should only be a bit of repipe since it is similarly designed with the exception of modulation . If you are happy with how this has performed and the lifecycle of it you'll be happier knowing the Phoenix will last longer than this one has . Choice is yours , light duty may be better suited in BTU size . Less work and less BTUs than any combi without worrying about cold water sandwich , DHW priority , not enough GPM . Pretty damn close to existing with a boost in efficiency .
http://www.htproducts.com/phoenixwaterheater.html
http://www.htproducts.com/phoenixldwaterheater.html
You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
Thank You for the input guys.
What do i need to be aware of, or is there any high failure rate parts that I should have on hand for this unit?
TimWinter Park, CO & Arvada, CO0 -
This may be one of the few cases where a water heater makes sense. Your design day heat loss is probably less than 15k. The typical day would be single digits. They don't make boilers that small.
I think adding outdoor reset controls with a boiler protection feature would give you better comfort and insure that the btu hungry slab does not rob you of a hot shower one day.
You could do that with either a variable speed injection control on the domestic side or a smart mixing valve in place of the one you have."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
I agree, you already have a heat exchanger so a simple swap would be the best bet. If it's been working for fourteen years as is just leave it as is.Zman said:This may be one of the few cases where a water heater makes sense. Your design day heat loss is probably less than 15k. The typical day would be single digits. They don't make boilers that small.
I think adding outdoor reset controls with a boiler protection feature would give you better comfort and insure that the btu hungry slab does not rob you of a hot shower one day.
You could do that with either a variable speed injection control on the domestic side or a smart mixing valve in place of the one you have.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements