needing 100,000 btu 90+ boiler with 2" vent
Jim_115
Jim_115 Member Posts: 4
I'm needing to replace a Hydro Pluse boiler with 2" venting and it would be very difficult to install 3" venting.
Is there a 90+ boiler out there that uses 2" venting instead of 3"? It would have about 50ft total of intake and exhaust piping.
  • Ironman
    Ironman Member Posts: 7,903
    The Bosch Greenstar. It comes with 3" connections, but 2" can be used up to a certain length.
    Download the manual and look on page 44 for the venting tables.
    Bob Boan
    Jim_115
  • Zman
    Zman Member Posts: 7,609
    The triangle tube prestige 110 will work for short distances.
    Check the vent supplement.
    Albert Einstein
    Jim_115BobbyBoy
  • Snowmelt
    Snowmelt Member Posts: 1,454
    Utica wall hung, or the naviEn combo.
  • Jim_115
    Thanks guys! Looks like either one would work I'll have to get the exact measurement to know for sure.
    hot_rod Member Posts: 27,473
    I think there was a time when you could use both 2" as exhaust, with combustion air from inside. Didn't the HTP Munchkin offer that venting option? Had to be solid core PVC, of course.
  • RobG
    RobG Member Posts: 1,843
    Are you sure that you need a 100K boiler? Has a heatloss of the structure been done? In the early days of high efficiency the 100k pulse was one of a very few HE boilers out there. Chances are it is oversized.