Need Chart for btu output versus gas pressure
We are constantly finding oversized steam boilers and we reduce the firing rate whenever possible to proper levels. However, I need a chart showing the btu capacity versus gas pressure for standard orifices. If 3.5 inches is 100% ( like on most atmospheric boilers), what percentage input can I expect at lower pressures. I know 0.8 inches is about 50% and 1.2 is about 60% ( from LGB boilers), but a full chart would be very useful. Thanks!
There was an error rendering this rich post.
Comments
-
Does this help?"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
I would be interested in hearing about your results…I was not a fan of down firing…For several reasons….0
-
I am looking for a chart that goes below 3.5 inch, probably down to about 0.8.
We have had excellent results with down firing on steam systems (steam is about the only systems we work on). Often times, noise disappears or is greatly reduced, the effect of incorrect near boiler piping are reduced, heat is more even and fuel usage drops. I suspect is also greatly reduces stress on the equipment and system by reducing thermal cycling. On power burners, we usually pick up firing efficiency, with atmospheric we usually lose a few points. It also often allows the use of smaller gas meters, so monthly charges can be reduced greatly. Our down firing typically is simply getting the input to the proper rate that should have been installed in the first place. have to watch the chimney, though. I may be seeing some condensing going on in a 2000mbh input atmospheric WM LGB that is now allowed to operate hi / low as needed.There was an error rendering this rich post.
0 -
Where do you find various sized replacement orfices for the LGBs? Or do you just drill your own?I am looking for a chart that goes below 3.5 inch, probably down to about 0.8.
We have had excellent results with down firing on steam systems (steam is about the only systems we work on). Often times, noise disappears or is greatly reduced, the effect of incorrect near boiler piping are reduced, heat is more even and fuel usage drops. I suspect is also greatly reduces stress on the equipment and system by reducing thermal cycling. On power burners, we usually pick up firing efficiency, with atmospheric we usually lose a few points. It also often allows the use of smaller gas meters, so monthly charges can be reduced greatly. Our down firing typically is simply getting the input to the proper rate that should have been installed in the first place. have to watch the chimney, though. I may be seeing some condensing going on in a 2000mbh input atmospheric WM LGB that is now allowed to operate hi / low as needed.0 -
Dave - I have a calculator that will do all that for you. I am very busy but when I have time I will send you the info so you can order it.0
-
Dave, by the way we are going to get a chance to look at the new conversion burner I have been consulting on. We will be firing it tomorrow at my training center. I wish you could have been with us to see it .0
-
Tim, when will this new conversion burner be unveiled to us?
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Thanks, Tim.
Been too busy to take on anything else. I expect to be installing a LNB 1000 soon with full outdoor reset for steam on a Peerless LC-07 in a system that I orificed and runs with a vacuum pump.
I don't resize the orifices, just decrease the manifold pressure. The LGB can be set up 2 stage with just the factory gas train ( except the 2 smallest models). High fire is 3.5 inches, low is 0.8 (older models) 1.2 (newer models)There was an error rendering this rich post.
0 -
New burner possibly in limited numbers in the late spring or early summer.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements