Does anyone have experience with Testing Radiator Traps with a Ultrasonic Tester? Best make and model to purchase?

Comments

  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,576
    Options
    What is an ultrasonic tester?
    The only way I know which can identify bad traps is the temperature method: if the outlet temperature is too hot, the traps is not closing as it should, and conversely, if cold, the trap is not open.
    An IR Camera could make this easier.--NBC
  • ChicagoCooperator
    ChicagoCooperator Member Posts: 354
    Options
    I'd like to know what people suggest for testing traps too, an IR thermometer or camera or...?
  • Abracadabra
    Abracadabra Member Posts: 1,948
    Options

    I'd like to know what people suggest for testing traps too, an IR thermometer or camera or...?

    I use both.
  • ChicagoCooperator
    ChicagoCooperator Member Posts: 354
    Options

    I'd like to know what people suggest for testing traps too, an IR thermometer or camera or...?

    I use both.
    Thanks, any suggestions for one or the other?
  • Abracadabra
    Abracadabra Member Posts: 1,948
    Options

    I'd like to know what people suggest for testing traps too, an IR thermometer or camera or...?

    I use both.
    Thanks, any suggestions for one or the other?
    I use a basic laser thermometer.. i think it's a Ryobi.

    For IR I use a Seek Thermal attachment for my tablet/smartphone.
  • ChicagoCooperator
    ChicagoCooperator Member Posts: 354
    Options
    Thanks, I'm going to check some out today/tomorrow.

    Since I use a brick, I mean old dumbPhone, that other stuff isn't realistic for me.
  • Ed. W.
    Ed. W. Member Posts: 26
    Options
    I have used Tempil Sticks, IR Temp. Sensor and a IR Camera. The Camera is the easiest .
  • SlamDunk
    SlamDunk Member Posts: 1,580
    Options
    We hired a service that used an ultrasonic tester specifically to find a leaking trap on a reducing station. there were 15 traps and steam was venting from condensate receiver to roof vent. They said all traps were fine.

    We isolated the station and started rebuilding all of the traps. we found four destroyed. I dont have a lot of confidence in them.
  • Sailah
    Sailah Member Posts: 826
    edited August 2018
    Options

    I have a fair amount of experience in this since it's what I do. Sorta.

    Temperature is reasonably accurate most of the time, if the discharge delta is something like 5 degrees then the trap is likely failed. But it also could be the trap upstream of it filling the return line and giving a false reading.

    But temperature with something like a FLIR is REALLY handy, especially in a plant because you can scan the room and find the hot stuff fast. Also just handy in general or to impress your kids.

    But ultrasound is the last word. It's actually a little faster than temp because you just walk up to trap and touch with probe wearing headphones. You'll know a bad trap when you hear it, they are fairly obvious like holding open an air chuck. The steam ripping through the orifice creates the ultrasonic signature around 25-35 kHz.

    So here's what I have an recommend:




    Thermal Camera:
    FLIR E8- Awesome, expensive, other cheaper options out there
    You can also buy an E4 and search online for how to make it into an E8..

    Ultrasound:
    Accutrak VPE-2000-Expensive, awesome, really one of the best
    Accutrak VPX-WR-Super expensive, awesome, THE best
    Bacharach Tru Pointe Ultra-Really good, inexpensive, works well

    And of course I do make my own ultrasonic steam trap tester...

    Of all my handhelds, the Bacharach is the one I recommend unless you are doing this all the time. I bought mine used on ebay for $125. It's made by Accutrak, and also called the Accutrak VPE. They are on ebay all the time but you NEED the metal probe. The ones with the gooseneck are for HVAC leaks. You need to physically touch the trap. Uses a 9V battery and regular headphones. The probe is sorta fragile I've already broken it once.

    You can also go to UE website and they have audio recordings of all traps so you can hear what a bad TD trap sounds like etc.
    Peter Owens
    SteamIQ
  • Mike_Sheppard
    Mike_Sheppard Member Posts: 696
    Options
    What about F&T traps that don't have much, if any, temperature drop across them?
    Never stop learning.
  • Sailah
    Sailah Member Posts: 826
    edited August 2018
    Options
    F&T traps will show a bigger delta drop than a radiator trap. If you have a FLIR it's pretty easy to see. You can usually also see the temperature gradient in the body. The water line will be half way up the trap, so top half of trap is above 212, bottom or outlet should be like 190.

    EDIT: This is for low pressure traps, which is what I assume most people are familiar with. A good F&T trap discharging to unpressurized return will be below sat steam temps. I said 190, but it could be a range of course. I'm most interested in outlet temp at threads, if that's above ~205 I start to think somethings wrong

    I like to measure with flir or laser right on the threads of the pipe, I find that gives me most accurate temp readings.

    Or just hit the easy button and you can check from your office

    Peter Owens
    SteamIQ
    ratio
  • Mike_Sheppard
    Mike_Sheppard Member Posts: 696
    Options
    I have a Flir E6 that I use for trap testing and I don't think I've ever seen that kind of temperature drop across a float trap. Don't they dump steam temperature water out of them? Now I'm confused because this is the opposite of what I've seen and read in books.
    Never stop learning.
  • Mike_Sheppard
    Mike_Sheppard Member Posts: 696
    Options
    Never stop learning.
  • Sailah
    Sailah Member Posts: 826
    Options
    I have enormous respect for @Dan Holohan but on this testing of F&T traps I am going to politely disagree.

    In my time working at Barnes & Jones I built, failed and tested a lot of steam traps.

    TEMP:

    F&T traps will certainly discharge close to saturated steam temp but the outlet piping isn't chock full of condensate or steam, maybe some flash. So your outlet piping should be less than 212. Unless you have a bad trap elsewhere and it's backfeeding the discharge line. Which is why I don't use temperature for testing. But on a functional trap there will be a difference in temp from inlet to outlet, that I can promise.

    This trap is failed, the body temp should not be that high. And I know it's failed because I put in a bad air vent.





    This is not a good pic to use (because the temps aren't accurate) but it's all I can find. This is what I see when I look at a good trap. There will be a gradient, sometimes slight, with the water lock on bottom and steam on top.



    All that said, I feel temp can be used to reasonably determine F&T condition. I aim the center point of the FLIR directly on the pipe threads at inlet. Same for outlet. Other places don't give me repeatable results.

    Here's another bad one I just found




    My FLIR has a SPOT/MAX function which I find extremely helpful as the spot will be where focus is but the MAX will hunt around and find the hottest part in the frame and then display the delta.

    ULTRASOUND:

    This statement is not my experience

    You can't check them with those sexy sonic devices either because F&T traps discharge constantly. Those sensors work well on bucket traps because they cycle full-open to full-closed, but an F&T trap (to me at least) sounds about the same all the time.

    A good trap is hard to hear, that's true. You can often hear condensate trickling out of the seat if you know where to put probe. But I don't listen to steam traps to find good ones and a failed F&T has a few modes of failure. If the air vent is bad it will be obvious with ultrasound. With even my cheapo ultrasound it sounds like a huge rushing WHOOOOOOOSH sound. My more expensive ultrasound rigs just detune the background noise. My super fancy one, hones in on that exact signal and it's crystal clear, kinda freaky.

    Anyways the other failures on an F&T could be seat has debris on it, could be wiredrawn. But if it's leaking, it will also be very easy to hear.

    These recordings are exactly what I hear when I test F&T traps

    http://www.uesystems.com/resources/the-sound-recording-library/float-and-thermostatic-steam-trap

    To me IB, F&T, TS traps are all easy to test. I enjoy IB traps the most because you get to hear the cool cycling. TD traps are the hardest for me because of the time it takes to hear a full cycle. Sometimes it's a couple minutes I'm standing there. If you poke a TD trap during its normal discharge cycle it might seem like it's failed.

    If people are in the Boston area, I'm more than happy to have a crew go to Barnes & Jones and we can test good/bad traps using my gear.






    Peter Owens
    SteamIQ
    Canuckerratio
  • Sailah
    Sailah Member Posts: 826
    Options
    I found this recording I did in 2016 when I first started making progress on our monitor. I borrowed an Accutrak and hooked up phone to record output.

    What we were doing was training our algorithm to detect the peaks in spectral frequency indicative of a steam leak. Which is what we do now. So our monitor does this every minute in 70 milliseconds.

    But you can clearly hear the jet engine sound as I turn on steam. From my writing on the trap it looks like I nicked the seat so what you are hearing is a bad seat.

    Sorry for the weird noises on the Accutrak, it was acting up.

    https://youtu.be/2yl4fZRoQIU
    Peter Owens
    SteamIQ
    CanuckerGordo
  • Mike_Sheppard
    Mike_Sheppard Member Posts: 696
    Options
    Great post @Sailah. I love the information. I am going to purchase a tester and experiment this heating season.

    I'm going to have to do some more testing with my E6 too. I haven't that experience with F&T traps that I can recall.

    I may have to take a trip up there to Boston to check that trap testing out!!
    Never stop learning.
  • Sailah
    Sailah Member Posts: 826
    Options
    My pleasure. I think the inexpensive tester will be more than adequate for you. Happy to have a testing party if you need it. I think you'll find it's pretty easy after a few.
    Peter Owens
    SteamIQ
  • JohnNY
    JohnNY Member Posts: 3,230
    edited August 2018
    Options


    I use both my Flir i7 or FlirONE for an initial look at a steam trap, then I put my ultrasonic tools to work. As Sailah said, you'll know a bad trap when you hear one. The problem I find with thermal testing is that at different points in the heating cycle, the traps behave differently and one bad one will make some others mistakenly look bad. We see a lot of thermodynamic traps here in NYC (Con Edison municipal steam) and systems that often run on 5 psi or more. Those are actually easier to identify as mal/functioning than in low-pressure applications.
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.