Honeywell gas valve buzzing, again?
Back in 2011 I installed my WM EG-45 and the day after noticed something in the basement buzzing. I went down and found the gas valve on the boiler buzzing. The burner was going like normal but the gas valve was buzzing so I shut it off and turned it back on and the buzzing never came back.
I recall emailing WM and talking to a member on the wall and if I remember correctly both said basically the same thing. That sometimes gas valves will do this after sitting on the shelf for years and it may just need to be exercised. It only did it that one time until last night.
I was down the basement working on something and the boiler was running. I noticed a slight buzzing coming from the gas valve so I pulled the cover off and tapped on the valve with a screw driver handle but it really had no effect. The next time the boiler fired the valve was quiet again.
Should I be concerned about this and buy a spare valve to have on hand, or even to replace it immediately or does this sound like something that just happens from time to time? Should I check anything like the voltage going to the gas valve? Would a slightly low voltage cause such a thing or would the valve flat out close or not open in the first place?
The last thing I want to happen is for this valve to fail, especially if it fails open. The 2nd to last thing I want is it to fail closed on a cold night.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
Comments
-
This is the only picture I have handy of the gas valve, which of course is before I put everything together.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Measure the control voltage at the transformer when the boiler is on stand-by. Call for heat, and when the burners are on, measure it again. The voltage drop should not be more than 10%.
Also read the voltage on the gas valve with the burners on.0 -
Back in the 80's my company built a line of radar transmitter power supplies that were relay controlled for remote power on / off. The initial run was for a dozen units; while running through the acceptance data sheets I found two of them had chattering relays at low line full load, they were right on the edge of dropping out. This was going into air traffic control gear so it to be reliable. After going through some tests I found some relays were fine down to 80% of rated coil voltage while others barely made 85% and we had to work from 85% to 115% of 240 or 120v. We made our own transformers so I knew they were more than rated for the load
I ended up having to screen the relays to be sure I had relays that would work, I think 15% of them would not work reliably at low line. I suspect you might have a marginal valve solenoid coil. In any case measure the voltage when it's activated. has anything been added that might be loading down the 24v? The transformers they use are pretty skimpy so they won't look kindly at additional loads.
If the voltage seems low under load you might be able to wire up a filament transformer in the primary of the 24v transformer to boost the voltage by 5%.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge1 -
-
Using a Fluke 179 I've got 25.94V RMS pretty much everywhere including at the gas valve when the boiler is on. 27.38V RMS with the burner off.
Sounds like all is normal as far as voltage goes?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
It's not voltage, maybe something is loose near the coil? That plastic cover can be removed, be careful not to snag a wire when doing so.
Bob
Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Not sure, I may have a look later.BobC said:It's not voltage, maybe something is loose near the coil? That plastic cover can be removed, be careful not to snag a wire when doing so.
Bob
I tried pushing on the plastic while it was doing it last night and it changed tone a little but really had no effect. Same with tapping on the valve with the screw driver handle.
Now it's not doing it so I can't really, tell much. If it does it again I guess I can check voltages again and maybe get a closer look.
It sounds like the overall feeling everyone has is there is no immediate danger going by what I've described?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
You have eliminated one item that can cause the coil of the gas valve to be unhappy; voltage drop, which could be at the valve itself or another load upstream of the valve. From what you describe, it doesn't seem to be a safety issue. Perhaps it's time to balance peace of mind with the cost of a valve.1
-
Are you sure this is a 60HZ buzz? If it was substantially lower it might be valve chatter, you would need a manometer to check that.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
-
Hi Bob,BobC said:Are you sure this is a 60HZ buzz? If it was substantially lower it might be valve chatter, you would need a manometer to check that.
Bob
Sounds very 60hz ish to me.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
After 50 years of working on gas systems I would tell you to leave it alone gas valves do this some times and as long as it is working it is fine. DO NOT TAMPER WITH THAT VALVE TAKING THINGS APART AS YOU COULD END UP BLOWING YOURSELF UP. THESE VALVES ARE NO LONGER ALLOWED TO BE FIELD REPAIRED. IF IT WILL GIVE YOU PEaCE OF MIND REPLACE IT. By the way what is the Honeywell number of the valve?2
-
Hi Tim,Tim McElwain said:After 50 years of working on gas systems I would tell you to leave it alone gas valves do this some times and as long as it is working it is fine. DO NOT TAMPER WITH THAT VALVE TAKING THINGS APART AS YOU COULD END UP BLOWING YOURSELF UP. THESE VALVES ARE NO LONGER ALLOWED TO BE FIELD REPAIRED. IF IT WILL GIVE YOU PEaCE OF MIND REPLACE IT. By the way what is the Honeywell number of the valve?
If memory serves it's a VR8200 series. Something like a VR8204 but I'm going from memory. It's for use with intermittent pilot and 1/2" connections.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
I took a video of the valve buzzing tonight.
I measured just under 26V at the valve while it was doing this. Pushing against the plastic cover quieted it and even almost stopped it.
http://youtu.be/ftELPVK7x2wSingle pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
The valve may be giving a little solenoid hum as the first valve is a direct acting solenoid valve and they will sometimes hum a little. Not a problem as long as it keeps working.0
-
Hi Tim,Tim McElwain said:The valve may be giving a little solenoid hum as the first valve is a direct acting solenoid valve and they will sometimes hum a little. Not a problem as long as it keeps working.
Did you get to watch the video? If it still get's your seal of approval after that I'll feel better.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
-
Ok will do.Tim McElwain said:I watched and listened to the video . . . . change the valve that is too loud and that coil is on the way out! Look into whether it may be covered in warranty.
Can I use a slow opening valve like Burnham uses on the IN series or do I have to use this exact replacement?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
-
Ok.Tim McElwain said:Exact replacement if you can get it if not then a VR8345M Universal replacement valve from Honeywell.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Looking into ordering a new valve now.
Also noticed, look where some dope put the union! Now I have to take all of that apart just to change the gas valve. It's also stupid because I can't slide the burner out for inspection / cleaning.
I'm ordering a few nipples and a union so I can make this a little easier to work on. I'll cut my self some slack, I had never piped anything before this. I'll let it slide, this time....Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
You need to find someone better to run your gas lines! Actually I probably would have done something similar if it weren't for all those gas line I helped my grandfather run. lol I don't have my warranty in front of me, but is that valve still under warranty? It might not hurt to contact Weil and see what they might do. All you will lose is a few minutes for a phone call.0
-
KC_Jones said:
You need to find someone better to run your gas lines! Actually I probably would have done something similar if it weren't for all those gas line I helped my grandfather run. lol I don't have my warranty in front of me, but is that valve still under warranty? It might not hurt to contact Weil and see what they might do. All you will lose is a few minutes for a phone call.
1 year on all parts besides the block. It's 3 years old now.
I try to avoid calling these places because they never like talking to a homeowner.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
This would be a great opportunity go big and install a two-stage gas valve...0
-
He doesn't have any pressure to actuate it! Of course if it could be hooked into that eco steam system.....1
-
-
I'd probably start with something really simple, like an outdoor temp switch. Switch to high fire when OAT drops below say 20˚F? A two stage stat would mostly work if there were setbacks in use.0
-
Tonight I did an 8 degree recovery. 34F ambient and the most I saw was 1" WC.SWEI said:I'd probably start with something really simple, like an outdoor temp switch. Switch to high fire when OAT drops below say 20˚F? A two stage stat would mostly work if there were setbacks in use.
I don't think your idea would work.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Not sure I understand -- I'm not suggesting pressure-based control.0
-
I don't know,SWEI said:Not sure I understand -- I'm not suggesting pressure-based control.
Having a lower running burner on warmer days would certainly change things. I guess what I'm wondering is, is there any benefit to it?
I think the commonly used 2 stage valve would drop me from 150K input to 90K input.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Exactly what I was suggesting. Outdoor temp control would probably work well assuming the system runs with little or no thermostat setback. A two-stage stat would work with setbacks, and also kick the valve to high fire (eventually) if the system can't keep up on cold days. Combining the two would be another option.
If you're already replacing the valve, the incremental cost might be worth considering, even if you don't put it to full use right away.0 -
I can't find the part,SWEI said:Exactly what I was suggesting. Outdoor temp control would probably work well assuming the system runs with little or no thermostat setback. A two-stage stat would work with setbacks, and also kick the valve to high fire (eventually) if the system can't keep up on cold days. Combining the two would be another option.
If you're already replacing the valve, the incremental cost might be worth considering, even if you don't put it to full use right away.
Do you have a part number handy for the 2 stage?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Yikes,
That's 3 times the cost of the OEM one.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
FOR GET ABOUTIT0
-
Your boiler is so well matched to the system I don't see what the advantage of two stage firing would be.
In my case a two stage system would help a lot, My Smith G8-3 is almost 40% oversized. I need to come up with a scheme to stage my Carlin EZ-Gas. maybe dual valves with individual orifices that would combine for full output and shed the lower capacity feed as pressure starts to rise.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge1 -
I'm curious how often gas valves fail like this.
I'm assuming / hoping it only lasting 3 years is a fluke and not typical.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Bob C do not try to stage a Carlin EZ you will be wasting your time. I have been experiementing with a EZ burner in my training center trying to do that for two years and it will not work. On low fire you can't produce sufficient microamps to keep it running it keeps shutting down no matter what I tried.0
-
I can see where that would be a serious problem, maybe I can sell my neighbor some steam?
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 925 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements