Water Hammer in Rad of 2 pipe steam system
BobbyC
Member Posts: 96
Have some pretty loud water hammer coming from a radiator of a 2 pipe steam system. My old house had a one pipe system and I raised one end of the radiator to get a better pitch and they seem to work but not sure what a solution might be on a two pipe system. How do you know which pipe is feed and which is return. Both have shut off valves on them.
thanks
thanks
0
Comments
-
Generally the pipes are a different size, the bigger one is the feed the smaller one the return. Post picture of one of your rads and that will help determine what you have.0
-
Thanks KC. Will post pic ASAP.
0 -
-
Nice looking Radiator. The pipe on the right should be the return (the vent also gives this away). So you would want a slight slope towards that side. I am assuming this is a 2 pipe air vent system since I don't see a trap and those appear to be standard valves. A pro may be able to comment better.0
-
Thanks. no trap near rad. will try to raise the left side slightly.
0 -
KC just checked out your pics of your boiler install. Impressive man!
0 -
Thank you. Just a humble homeowner that owes a lot to this website.0
-
-
DanH actually talks about your system here: https://heatinghelp.com/systems-help-center/a-steam-heating-primer/
Scroll down to two-pipe steam. You're the second person who has posted with that system recently.Two-pipe Trane vaporvacuum system; 1466 edr
Twinned, staged Slantfin TR50s piped into 4" header with Riello G400 burners; 240K lead, 200K lag Btus. Controlled by Taco Relay and Honeywell RTH6580WF0 -
Jamie Hall which ones would be the runouts?0
-
The runouts to which I refer are all the pipes from the steam mains or the returns to the actual radiators themselves. Particularly in older houses, things settle and they may have not enough pitch, or they may have sags (if they are long and unsupported -- or even if they are supported!). Use a good level, and check the whole length...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Thanks Jamie.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 920 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements