How not to do a Hartford Loop

Got a call from a friend who asked me to come look at some work his landlord had a local plumber do to repair on a rusted out mud leg on the loop,this is how he did it,think you want him to come do your work?

Comments

  • Randy-LeeBraman
    Randy-LeeBraman Member Posts: 46
    trying to post pictures but it just sits there and says uploading what am i doing wrong?
  • Randy-LeeBraman
    Randy-LeeBraman Member Posts: 46
    ahh finally a pic for all to admire,don't you wish you did work like this.
  • Eric_32
    Eric_32 Member Posts: 267
    What happened to the equalizer?
    Do you have any other shots higher up at the header?

    Oh boy...
  • Randy-LeeBraman
    Randy-LeeBraman Member Posts: 46
    Eric i guess you could say he figured it wasn't needed.The smaller of the two pipes was the Equalizer but he put it back as he did.This same guy charged the landlord a very outrages amount when the low water cut off tripped to reset it takes his chair and tools and makes like its a big project to fill the boiler and push the reset button,heres another picture.
  • Paul48
    Paul48 Member Posts: 4,469
    I kinda like the union, right next to the csst.
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    There could be some water hammer in that arrangement.
    God bless those plummmmmmers!--NBC
  • SWEI
    SWEI Member Posts: 7,356
    edited October 2014
    RTFM, anyone?
    RobG
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    What is RTFM?--NBC
  • BobC
    BobC Member Posts: 5,502
    Manual, we don't need no stinkin manual!

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • icesailor
    icesailor Member Posts: 7,265
    BobC said:

    Manual, we don't need no stinkin manual!

    Bob

    Who has time to read any stinkin' manuals? I know everything there is to know, and I've never forgotten anything I ever learn'ted.

  • j a_2
    j a_2 Member Posts: 1,801
    My honest opinion, if one needs to read a manual to repair a broken,rusted pipe he/she is in the wrong business….There are lots of people out here who call themselves, plumbers…Repairing of a heating pipe does not require a lic. here in Mass…The word plumber is used very commonly by handy men/ techs…They can only wish….In Mass it requires a lic. plumber to do a complete install on any boiler….as well as a lic elect...
    icesailorjonny88RobG
  • icesailor
    icesailor Member Posts: 7,265
    edited October 2014
    In Massachusetts, the only part of a boiler install that is required to be done by a licensed Massachusetts Plumber is the protected water connection. After that, and you can hire a Great Ape to pipe it up. And some look like that is who was hired to do the install. Unless the boiler is over 400,000 BTU's in which case it is supposed to be installed by a licensed pipefitter. And licensed and inspected by the Dept. of Public Safety.

    Any fool can do heating. And some of those fools do.

    30+ years ago, they gave out grandfathered pipefitters licenses to qualified plumbers, heaters and pipefitters. If you didn't get one them, you'll be taking a test and having everything inspected.

    Plumbers aren't pipefitters, and pipefitters aren't Plumbers. Unless they have a valid Plumbing License.

    Heaters may be Plumbers also, but they aren't plumbers unless licensed. If Heater can't take out a Plumbing Permit, he isn't a Plumber.
    EBEBRATT-Ed
  • KC_Jones
    KC_Jones Member Posts: 5,840
    I know this is far from the primary concern here, but...all that pipe dope not cleaned from the joint to me is a fantastic indicator of how much this person cares about their work. I am just a homeowner and my joints look better than that.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,492
    actually I think the pipefitter license starts at 700,000 btu and up (used to be 3 million btu) so anyone can install a boiler under 700,0000, howeaver a plumber is supposed to do the water and an oil burner license (for oil) or a gas fitter/plumbers license for (gas) and don't forget the electrician unless your an oil guy doing the reconnect on oil.

    Don't forget to apply for your new process piping license in MA. new applications on their website. Grandfathered if you have a plumbing or pipefitting license now.

    ONLY IN THE GREAT STATE of MA.!!!!!!!!!
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,211
    There is nothing inherently wrong with separating the hartford loop and the equalizer. The hartford loop is there to prevent dry firing in case the wet return pops a leak. The equalizer is a combo pressure equalizer and drain for the header. In theory, the equalizer can connect anywhere between the end of the header and the low point of the A dimension.
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,211
    Obviously, if the equalizer connects to far from the boiler, there could be low water issues in the boiler. Point is that the equalizer and the Hartford loop have two distinct functions and do not need to be connected to each other
  • RobG
    RobG Member Posts: 1,850
    With todays technology if I didn't do the install I want to look at the manual, if for no other reason than to show the owner what and why I'm doing what I'm doing.
  • Jamie Hall
    Jamie Hall Member Posts: 24,876

    There is nothing inherently wrong with separating the hartford loop and the equalizer. The hartford loop is there to prevent dry firing in case the wet return pops a leak. The equalizer is a combo pressure equalizer and drain for the header. In theory, the equalizer can connect anywhere between the end of the header and the low point of the A dimension.

    Provided one thing: the Hartford loop absolutely must have some sort of venting at the top of the loop, so that it can't siphon the boiler. This is most conveniently the equalizer, but in principle it could also be a drip from a return. The arrangement shown will siphon the boiler if there is a leak in the wet return.

    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,211
    Is there a difference if the" vent" is connected directly to the Hartford loop or a few inches down
  • Jamie Hall
    Jamie Hall Member Posts: 24,876
    The siphon will function until the water level in the boiler reaches the level of the vent. If that's a few inches down, then that's the level to which the boiler will drain -- not the top of the loop. Which may or may not be OK, depending on where that level is.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • j a_2
    j a_2 Member Posts: 1,801
    As far as i know wiring of any oil boiler falls under under a Massachusetts advisory ruling Mass general laws chapter 30a sec 8…as to the type of electrical wiring which may be performed by oil burner techs certified by the dept of public safety…Its pretty interesting….It appears the oil heat council contacted the state board of examiners of electricians by letter dated dec. 3 1993….Maybe there is a update but I am not sure…I have a hard copy of the advisory ruling, that I was given some time back...
    EBEBRATT-Ed
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,492
    JA your correct. An oil burner tech can replace a boiler (in ma) and reconnect the wiring without having to call in an electrician. Limited to within 10' from the boiler or from the firomatic down I think.
  • ChrisJ
    ChrisJ Member Posts: 16,316
    Jamie is correct,

    That is not a hartford loop, it is a speed bump. The vent must be at the top of the loop to break the siphon.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • STEAM DOCTOR
    STEAM DOCTOR Member Posts: 2,211
    Good morning. My grasp of syponige is not very good. Please be so kind to explain in as much detail as possible. My limited understanding tells me that if the vent is between the boiler and the leak in the wet return, then the siphon will be broken. Thank you in advance.
  • Jamie Hall
    Jamie Hall Member Posts: 24,876
    To properly understand how a siphon works -- and to see why a vent at the top of a siphon will cause it to not work, but why a vent somewhere else won't affect it -- it is necessary to consider the energy of the liquid. That energy is composed of two parts: kinetic energy, due to its motion, and potential energy. In a situation such as this one, we can ignore the kinetic energy (although to understand a venture, one must consider it). The potential energy itself is also composed of two parts: the pressure in the fluid, and the elevation above some datum of the fluid. We must use absolute pressure, not gauge pressure. Absolute pressure is the pressure in the fluid relative to a perfect vacuum. Gauge pressure (which is what most of our gauges measure) is the pressure difference between the absolute pressure and the local atmospheric pressure. The energy due to elevation can be converted into pressure -- or vice versa -- using the density of the fluid. Thus it is possible to talk about so and so many feet of head, for example.

    Now the energy in the fluid in a siphon must remain constant. You are neither adding nor, for our purposes here, subtracting any (there are friction losses, which subtract energy -- but let's ignore them for the moment at least). As the fluid moves through the siphon, it can exchange pressure for elevation, and vice versa, so long as the total is constant. Thus suppose we start in the boiler, since we are talking about boilers, and let's also suppose that the boiler is cold, which makes life a little simpler since we don't have to worry about the boiler pressure. Let us further suppose that the reference we want to use is the basement floor, since it's handy. At the boiler water line, the total energy of a packet of water is its absolute pressure, which is equal to the atmospheric pressure, plus the elevation energy head. As we go down through the water in the boiler, that total stays the same -- there is less elevation, but the measured water pressure will increase by exactly the same amount. Now let us follow our packet of water out into the siphon. It goes along horizontally -- no change in energy. As it goes up the upward going leg of the siphon, the elevation energy increases, and the absolute pressure decreases. It can continue to rise in the upward leg until the absolute pressure drops to the point where the liquid starts to evaporate -- somewhere around 33 feet above the water line in the boiler, at sea level. It then goes over the top and, as it comes down the other side, the absolute pressure will increase by exactly the same amount that the elevation decreases.

    If we then provide an opening for the water somewhere out there, such as a leak, water will flow out of that opening, but it can continue to flow through the siphon, as the absolute pressure in the siphon can drop to offset the elevation difference.

    Now what happens if we provide a vent at the top of the siphon, what happens? Quite a different picture. Our packet of water, on encountering the vent, must have an absolute pressure equal to the atmospheric pressure at that point. If it tries to drop below that, it will simply suck the atmosphere into the pipe, and the liquid cannot continue to flow (note that if that vent is a hole in the pipe, not a vent, then water will flow out of the hole if it is below the boiler water line -- I'll get back to that). Thus a vent -- or in the case of a Hartford loop, the equalizer -- will keep water from rising in the siphon any higher than that connection, so it cannot flow over the top and down the other side.

    A Hartford loop is normally set a couple of inches below the boiler water line, and vented back to the boiler through the equalizer. In this arrangement, if there is a leak somewhere in the cold returns out beyond the Hartford loop, water will flow out of the boiler and through the Hartford loop until the water level in the boiler equals the elevation of the bottom of the loop nipple, at which point it will stop -- thus preventing the boiler from draining completely, which is the objective of the exercise.

    I hope this helps...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    ChrisJZman
  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,846
    Am I seeing things or did somebody replace the gauge glass with a piece of 1/2" copper?
    Just another DIYer | King of Prussia, PA
    1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
  • ChrisJ
    ChrisJ Member Posts: 16,316

    Am I seeing things or did somebody replace the gauge glass with a piece of 1/2" copper?

    No,
    It's just so well maintained and clean that it looks like it's metal.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

    KC_Jones