Newly installed Weil Mclain CGt install with CI radiators - Part 2 (It's running!)
R2.0
Member Posts: 99
in Gas Heating
I originally posted in this forum last year when I was contemplating this install Here and the responses gave me a lot to think about. After many long delays it's in, and now I am in the "tuning" phase. Before people ask why the installer didn't do a proper startup, I purchased the boiler as "pre-owned" but still in the crate and I paid an installer to do the piping (gas and water), which was done to my satisfaction. Everything else was on me.
First question: the boiler has Weil Mclane 1107-1 controller I cannot find a separate manual for this. Does anyone know if one exists? My specific interest is being able to command the circ pump on for diagnostic/service reasons. It's still shoulder season conditions around here and the thermostat is not always demanding heat.
Second, someone in the previous thread mentioned using an old electric hot water tank as a buffer tank to prevent short cycling. Can someone point me to a diagram or plan for this? Most of the ones I've seen use a tank with 4 tappings - 2 high, 2 low - for storage and hydraulic separation. HW Heater isn't quite like that.
Thanks in advance
R2.0
First question: the boiler has Weil Mclane 1107-1 controller I cannot find a separate manual for this. Does anyone know if one exists? My specific interest is being able to command the circ pump on for diagnostic/service reasons. It's still shoulder season conditions around here and the thermostat is not always demanding heat.
Second, someone in the previous thread mentioned using an old electric hot water tank as a buffer tank to prevent short cycling. Can someone point me to a diagram or plan for this? Most of the ones I've seen use a tank with 4 tappings - 2 high, 2 low - for storage and hydraulic separation. HW Heater isn't quite like that.
Thanks in advance
R2.0
0
Comments
-
Sorry I missed this posting (I am very busy). Contact me at gastc@cox.net I have what you are looking for.0
-
No problem. I appreciate the time the professionals put into this board, especially in educating those of us who know enough to know that others know far more than we will ever know.
Email sent.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements